Hello

I have a new AEG induction hob rated at 7.4kw max using power sharing but AEG do not specify a cable size or mcb rating nor will they answer the question I submitted to them by email. I think their position is that it is down to the electrician to decide.

The configuration is as follows:

Cooking zone 1 - 2300/3700/10
Cooking zone 2 - 1800/2800/10
Cooking zone 3 - 1400/2500/4
Cooking zone 4 - 1800/2800/10

Where the values represent Nominal power (max)/Power function/Power max duration (mins)

As the work is notifiable I have asked a local qualified electrician to quote for a new radial circuit and he has suggested that I need 10mm cable on a 40 amp mcb because he does not apply diversity and therefore the amperage will be 32.174 at 230 volts, hence the need to go to a 40 amp mcb and 10mm cable. He is prepared to install 6mm cable on a 32 amp mcb but will not be responsible for the frequent tripping out that he feels I may experience.

Having read a number of different forums I get the impression that most electricians (but not all) would apply diversity and I would appreciate the views of those of you experienced in this area as to whether I am likely to regret not going with the 10mm cable and 40 amp mcb. My personal feeling is that it won't be a problem as I am unlikely to ever be using all four zones on the 'power' function at the same time. Using all four zones on maximum (but without 'power') would require 7.3kw, so just within the limits of a 32 amp mcb but this isn't going to happen either.

The only reason for posting the question is that ideally I would like to use the existing cooker switch for the induction hob (it's right next to it) and run a new radial to the double oven which is currently on the existing cooker circuit. The existing circuit is 6mm cable on a 32 amp mcb.

The existing cable is 9.5 metres from the CU to the cooker switch and passes through the ceiling void and is then enclosed in conduit behind a tiled wall. It does not pass through any insulation.

I would very much appreciate your thoughts based on personal experience.

Thanks in advance.
 
If the electrician uses 240v, which is more likely, then a 32 mcb will be ok as max would be less than 31 amps. Ask the "electrician" to check whether it is 230 or 240v.
 
The electrician is wrong in my opinion.

Diversity on cooking appliances in domestic locations is first 10A and 30% of remainder. Has been for years and years. Following that rule has never let me down. The existing circuit will easily cope with the load.

I fairly often install single ovens and hobs such as yours on a single 32A supply. Hob is usually around 7kW and oven around 2.7kW
 
Many thanks to all for taking the time to reply. There are other local electricians and I will get another quote which will hopefully be in line with the opinions expressed here.

Thanks again.
 

Reply to Yet another induction hob question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob. The Induction hob is 7400W and by my calculations this would...
Replies
3
Views
2K
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...
Replies
10
Views
2K
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Replies
2
Views
2K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock