continuity

  1. scarlet7

    Class 1 Earth Continuity for PAT test.

    Hi guys, When performing an earth continuity test on class 1 appliances can you get away with just using a 200mA current on every piece of equipment? Having been on the 2377 course they say to use 1.5 times the fuse rating upto 26A for non IT. Need clarification as to what is right...
  2. B

    using metrel mi3000 to do ring continuity test

    Hi all Just got a metrel mi3000. Was using it today to test a new cu job. But I'm confused...when I do continuity tests on a ring I can do tests on the crossed line and neutral using the plug adaptor but I can't use the plug adapter to do test on crossed earth and line!? This means I have to...
  3. L

    Supplementary bonding required with RCD's?

    Much discussed issue this one. Appreciate any comments. I let a small one bed flat out. Electric only ie no gas. Year back I had a new CU put in with all circuits on RCD's (RCBO for lighting). Accompanied by an EICR. Registered ECA sparks did the work. The EICR documents that the mains...
  4. F

    LEVEL 3 -Assignment Help for 3 faults - FIRST FAULT RING CONTINUITY

    Hello there, I'm currently taking my Level 3 and have been given an assignment to do which I have all most finished but I was wondering if anyone could use their infinite electrical knowledge and help me out with 3 faults that I need to identify and rectify? I will lay out below what I have so...
  5. E

    75 volts on earth

    Hi all , was doing a periodic on a domestic board. First I got 75V between the main earth and bonding earth . There was a L/E fault after clearing the fault I've tested between earths and now getting 8V. Is that acceptable , or is it still a fail . Thanx in advance.
  6. S

    Main Protective Conductors - Continuity and Connection Verified - Sighting Clamp

    Are there any circumstances when it might be acceptable to tick the "Continuity and Connection Verified" box of the Electrical Installation Certificate when there is no visual or physical access to the point at which the bonding (normally a clamp in domestic) is applied. If so what checks over...
  7. M

    Ring final continuity readings.............

    Hi all had a weird one today, actually make it two, tested ringfinal continuity at the board lives were 0.00 and so were neutrals, earths were the same too, not sure why, is it a ring that has been interconnected causing a duff reading?? Secondingly tested another property's ringfinal circuit...
  8. N

    r1 r2 through conduit

    Hi guys, as the title suggest how do u test the R1 R2 value or R2 continuity if the sockets are earthed via the metal conduit? Thanks guys
  9. 1

    Continuity testing

    To do a R1+R2 test you connect the Line and Cpc together and test at the furthest point. But on the test sheet I have there is also a box for just an R2 test aswell, how do you correctly do just an R2 test?
  10. T

    Earth Continuity Test - Current Through Probe?

    I noticed some sparking coming off the probe during earth continuity tests on class 1 devices when the probe is touched to the metal casing. I placed a clamp meter over the probe and got readings of up to 10 amps. I can also feel a vibration from the probe lead during the earth c test. It's...
  11. S

    just sat the 2395(hard work!) can i still sit the 2391??

    hi guys i really need your help on this one, I just sat the 2395 inspection and testing certificate( replacing the old 2391), but it was really hard and wanted to know if i could sit the 2391? But does the 2391 still run on the same format as asking the questions , i.e, procedure for...
  12. T

    What exactly is required to calibrate a voltage continuity tester?

    My company does not allow us to use our own voltage/continuity testers. Instead we must use the ones they provide for us. They're pretty cheap but do the job well enough. I have had my testers for just over a year and the label says that I shouldn't use them after that time so I handed them...
  13. D

    Incoming cable - earth neutral continuity!

    Just spent a frustrating day fault finding and still left scratching my head, was wondering if anyone else had experienced something similar! The kitchen we had been working in had been a proper DIY job (diagonal cable chases, no earth sleeving etc etc etc) so we were testing a ring circuit to...
  14. F

    ring testing

    whilst doing ring continuity i have no end to end on cpc also on isulation test live earth im getting 9.50Meg ohmson the same ring are these two results to do with the same problem if so how can i go about finding the fault am i right in saying that if i spilt the ring at one of the sockets then...
  15. R

    continuity on ring main

    Hi. be nice for some feed back on this. I'm testing a ring main for an eicr. I know that the cpc reading should be around the 1.6 times higher than the live conductors but I'm getting 0.66 on live, 0.67 on neutral and 0.61 on cpc. I'm wondering, if the cpc are connected through the metal k.o box...
  16. M

    Continuity of ring final circuit..... can somebody help please !!!!

    Im currently studying electrical and im up to dead tests. ive reached continuity of ring final circuit on my scenario cd , in therory i understand the procedure and what to do but im a little un sure on finding the mid point on the sockets . please can sombody go threw it step by step in...
  17. W

    240v but no continuity

    Hi, Just went round to a customer who wants the ring extended in the garage, Prelim checks found no continuity on live, OK on E&N. When power is on 240V on each leg. Will go back and look further, customer said everything was unplugged but thought I would ask if anyone had come across this...
  18. kingeri

    Concealed bonding conductors

    Morning all. I'm about to set off to a cellar conversion. The gas, water and electric incomers are all in opposite corners of the cellar. In the next few days it's all going to be plasterboarded, which will conceal the bonding conductors permanently, although the actual earth clamps (i.e. the...
  19. D

    Some help for course work info needed

    Hi there, I am new on here,Great place ! Can someone explain to me how to do an earth continuity test and earth loop test on an electric cooker where the cooker point is already installed. Our college tutor has asked us to find out the info for next weeks lesson ,where we will be asked...
  20. C

    Weird continuity results on ring

    Strange test results on an old ring: L-L 0.14 ohms N-N 0.15 ohms E-E 1.12 ohms L-N (this is where it gets weird): 1st d/skt 0.07 ohms 2nd d/skt 0.08 ohms 3rd d/skt 0.21 ohms 4th d/skt 0.36 ohms 5th s/skt 48 ohms! 6th d/skt 48 ohms! 7th d/skt 48 ohms! Spur d/skt 48 ohms! WTF!? This was the...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock