sizing

  1. Rockingit

    NYY-J sizing

    Just speccing a job for tomorrow - simple 3ph immersion supply at 12kW. Supply to be constantly on, using the immersion temp stat for control (by request....) via a local isolator. (Have suggested future improvements with timers, stats, contactors etc but for now it's just this) So that's...
  2. V

    sizing neutral on a split phase 180 deg

    Hi, looking at installing a sub main down to a field to supply caravan hook up points. the supplier has stated they are installing 2 x 100 amp split phase 180 degrees apart. not worked on 460v/480v split phase - my question is how do i go about sizing the neutral. i plan to run a steel wire...
  3. G

    Cable sizing

    Hi Can somebody help me with this please Looking at the table in OSG. It states if I'm reading it right. That the ratings apply to insulation with thermal conductivity greater than (^)0.04 Wm-1K-1 So if 0.039 W/M2K = thermafloc loose 0.044 W/M2K= superglass 0.035 W/M2K= Rock...
  4. V

    Sizing csa of old cable

    Hi Looking at an old 3036 board and 2 peak and off peak immersion supplies. The cable looks like it is in between a 1.5 and 2.5. It is fused with a 15 amp fusewire. I know some old cabling is imperial but was this a regular thing for a batch of cable in the 70/80s???
  5. F

    SWA sizing for sub boards

    Hi guys, I'm working in a new role which requires me to size SWA cable to feed sub boards which in turn supply EV chargers. I noticed on the jobs that have been done already they have used 50mm 4c and 70mm 4c to feed 3ph 250A main switches on the sub boards. Going by tables and calculators this...
  6. J

    MCB sizing

    Is there any issues in having 10amp breaker if the circuit is pulling just under 6 amps? I know the breakers there to protect the cable and the cable is 2.5 3 core armour. Just curious.
  7. A

    Cable sizing for 50kW windmill ?

    Hello, I'm not an electrician. I'm looking for advice on the capacity of an existing SWA cable I have on a farm. It's a three phase cable (red,yellow,blue) and black neutral which connects an old 18kW wind turbine back to the farm electrical substation. I think each cable core is 10mm2 but it...
  8. C

    how to work out what size commando plug I need.

    Hello. It has been a long time since circuit designing for me as I am a simple maintenance person. How do I work out commando plug sizing, for example a machine rated at 32A, plus I have several machine that need moving onto one board, I have there rated current how do I work out board size...
  9. L

    Sizing 3 phase Generator

    Hi Everyone May be someone could shed some insight on the sizing and provide some suggestions: 3 phase Generators (400 V, 50 Hz) have the ability to sustain 250% kVA of its rated kVA at 30% voltage dip. Suppose a machine needs to be powered by a standby generator during a power outage. It...
  10. C

    Twin and Earth CPC

    IEC 60364-5-54 states that phase conductors 16mm2 and smaller require a CPC of the same size, over 16 to 35mm2 a 16mm2 CPC and over 35mm2 a half size CPC is required. My questions is why am I seeing catalogs with harmonized twin and earth with reduced size CPCs over 2.5mm2? And why doesn't the...
  11. Pretty Mouth

    Why are main protective bonding conductors sized as they are

    Hi all. Hope you are all well and virus-free. This question is not how to select main protective bonding conductor sizes according to the regulations. That I understand how to do. What I am asking is: Why do the regulations require such a large CSA for Main Protective Bonding conductors...
  12. M

    Cable Sizing for Oven...?? Please Help..!!

    Morning.... I was wondering if you guys could help me with this..?! I’m currently having my kitchen updated, including all new appliances... The oven, according to the manufacturers documentation has a rating of 4.2kw, which is 2.2kw or the oven and 2.2kw for the grill... The paperwork states...
  13. M

    Sizing MPCB

    Hi guys, just making sure that I'll be choosing the right size of MPCB, motor connected in star with current 3.32A, would a MPCB rated at 4A - 6.3A be good enough? Thanks!
  14. Javadali

    MPPT Solar Charge Controller Sizing for 1200 Watt solar Array

    Hey everyone! I am drafting out my first solar power off grid system for my back yard shed and came here in hope to get some good recommendations from you guys on trusted a charge controller which will support my current specs but also give me room to grow as I improve on this system. Below are...
  15. O

    Mismatched panels & MPPT sizing

    Hi there, I just purchased a sailboat and its electrical system was put together in questionable ways.. It came with an 815W array of mismatched PV panels, linked to a Xantrex C40 (40A) PWM charge controller, charging a 1030Ah 12V lithium battery bank. First question: can mismatched panels...
  16. R

    supply cable sizing

    Hi ,I have a wood cabin outside 70mtrs from house incoming supply, I was thinking of using a 35mm 2core pvc/swa, as I think a TT system would be appropriate for the cabin, owing to the distance away from house load would be allowing for diversity would be 51amps, seems a lot but it will be a...
  17. A

    Main earth sizing

    Hi guys, Just wondering if anyone can clear up an issue. On tncs earthing systems, can you calculate the size of the main earth? I thought you could but main bonding conductors have to be sized to the neutral. Just had a conversation with another electrician and he said it has to be 16mm for...
  18. dc-electrix

    New DNO Supply help sizing

    Hi all, I have become involved in getting a new supply laid into a block of flats. It was originally a house and was subdivided into flats >20yrs ago. Whoever did this used the existing 100A incomer and had 6x 80A BS1361 DNO fuses fitted which feed 4mm MICC submains. How the DNO p,ut 80A fuses...
  19. C

    Cable Sizing 2.2kw motor

    Need a bit of advice about a motor rewire i need to do. There is a 2.2kw motor which is supplied from an MCC with about a 30m ish run using a 4mm 4 core SWA. This then goes to an atex junction box located half a meter from the motor. Then the cable goes from this box to the motor itself. For...
  20. A

    A127 Alternator Indicator Light Sizing

    Hi, I'm intending to fit a standard A127 type alternator to my Chinese tractor, replacing the original with it's troublesome external regulator. I'm happy with the wiring and principles except for one thing ... can anyone put a figure to the current needed via the indicator light in order to...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock