Discuss 110v socket circuit advice in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
i’m looking for some advice about how I’d go about installing a 10kva 230-110v transformer and related sockets - would I require a consumer unit for the 110v sockets etc?
I’m wiring a new extension to an existing fabrication workshop and have made a quick drawing.
any other advice would be greatly appreciated.
Thanks
 

Attachments

  • 7E393904-E559-4BF4-899B-C0FADCBECB12.jpeg
    57.6 KB · Views: 20
Are you looking at 110V as per USA outlets, or (more likely) the 55-0-55 style of safe low voltage used on building sites, etc?

A 10kVA 110V transformer has 44A nominal on the primary, 90A nominal on the secondary, but if you are looking at a fault on 0-55V then it is 180A before your supply OCPD is exceeded in any way. The Hager catalogue suggests a 63A D breaker for a 10kVA single phase transformer, that is going to be hard to meet your Zs for fault clearing (OSG has 0.28 ohms) so you might want to consider a 50A BS88 fuse instead (OSG has 0.79 ohms).

So the short answer is yes. You will need per-socket protection against overload/faults. The simplest option might be a DB, but as above, if you are looking at 55-0-55 then you really should be looking at DP breakers to deal with faults to earth and that is not common for UK systems.

Of course RCD would do the same, but probably it is cheaper to go for DP MCBs given that 55-0-55 is generally considered safe (outside of a swimming pool, etc, which I think we can discount here) for shocks.

DP MCBs are common in the EU though, so it might be worth checking to see if the likes of Schneider, etc, can offer such a board from a UK stockist.
 
Most of those transformers incorporate fusing within however this is normally to give the secondary conductors fault/overcurrent protection. So yes a secondary board with double-pole rcd protection. Ensure is has a centre tap.
 

Reply to 110v socket circuit advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
702
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
692
Hi, I’m new to the forum and am seeking some advice please. I’ve picked up a job that another electrician has abandoned, the job is to...
Replies
17
Views
2K
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock