Discuss 110v supply issue? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
just a quick question I’ve searched online but want to be sure before deciding what to do.

I am putting in a supply for x5 110v commando sockets in a workshop.

The commando sockets each have a internal 16amp double pole MCB inside the socket.

I’ve wired from the DB a 32amp 10mm2 supply to a centre tapped transformer as per drawing.

From here I was unsure how to wire out to the x5 commandos.

So I ran a cable from the transformer in to a small 6 way DB and and fed the commando sockets from there the issue I have is that I’ve used x5 16amp single pole MCBs, then thought that they might need to be double pole MCB’s.

Would I need to change the small Db for a larger one and feed the commandos with x5 double pole MCBs?

thank you for your time and have a great day ??
 
If the transformer centre-tap is earthed then yes, all switching and protective devices must be double-pole, as both the other wires are lines and need protecting against faults to earth and both must be switched otherwise the appliance remains live.
 
Why not run it as an RFC and try and get the legs the same length the balance the load?
 
The sockets come with built in double pole mcbs, the problem I had is they are all fed from 1 transformer so I have 5 cables at the transformer that’s why I was planning to put a small db in next to the transformer?
[automerge]1585839103[/automerge]
Cheers for the replies ??
 
What rating is the output of the transformer and does it have any output protection built in?
Have you considered a single radial circuit from the output of the transformer?

If not yes the DB will need DP MCB's. Most of the bigger brands of DB have the facility to fit distributed neutral and DP MCB's.
Personally I prefer the schneider Acti 9 range for this.
[automerge]1585840255[/automerge]
Would one of these do: Legrand EN 60947-1 048-84 Modular Distribution Block 100A-40 Ui 500V ipk 20ka | eBay - https://www.ebay.co.uk/itm/Legrand-EN-60947-1-048-84-Modular-Distribution-Block-100A-40-Ui-500V-ipk-20ka-/302637580524
[automerge]1585840127[/automerge]
You will probably need Bootlace ferrules and a crimping tool if you don't have them already, you can get the Legrand distribution box in the UK.

No, it won't do, the OP needs a DB with a neutral kit and DP MCB's.
 
He's already got double pole MCB's in the socket, why does he need additional double pole MCB's in a DB? I suppose it all accords how long and vulnerable the lead are.
 
He's already got double pole MCB's in the socket, why does he need additional double pole MCB's in a DB? I suppose it all accords how long and vulnerable the lead are.

He said it is a workshop, so I guess the cable will be fixed and (hopefully) well protected physically, not like trailing leads on building sites that the folk just drive over!
 

Reply to 110v supply issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
837
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
568
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
712
Hi all, I've just installed an APC 6KVA SRT6KRMXLI. As a computer network engineer and electrician, I was a bit baffled by the 35mm gland that...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock