He's already got double pole MCB's in the socket, why does he need additional double pole MCB's in a DB? I suppose it all accords how long and vulnerable the lead are.
Double pole mcb’s as effectively you have two line conductors each needing fault protection and is required by regulation 411.8.3
 
Double pole mcb’s as effectively you have two line conductors each needing fault protection and is required by regulation 411.8.3
Having MCB at both ends is not terribly good from a discrimination point of view.

No information on the transformer rating but it might be a case of having some fuses at the transformer outlet/DB rate for full 110V load, and sufficient conductor cross-section to match, maybe a ring?
 
The transformers rated output is 3.0kva. The commandos are wired in 2.5mm swa on tray. 5 radials from 15 to 35 metre runs
 
Last edited by a moderator:
3kVA at 110V is just over 27A so you could consider having a pair of 32A fuses on its output before splitting to the sockets, that ought to be OK for protecting the 2.5mm wire against a major short. The 32A breaker on (presumably?) the primary would be equivalent to 67A on the 110V side.

Based on the (admittedly probably not that accurate) Eaton coordination tables "TD01400002U – April 2013" you should get discrimination to around 0.7kA fault currents between 16A MCB and the common 32A BS88 style fuses. I suspect you won't get that sort of PFC with your cable runs anyway!
 
Actually thinking about it, a 32A breaker feeding a 3kVA transformer sounds a lot more than is sensible, is it on the output?

If is is a DP on the output you already have you cable protection, but you really would need it to be a D-curve to have any hope of coordinating with the commando socket's 16A MCBs (assuming they are B-curve).

Also if that 32A is on the primary and you have the misfortune of a 55V-0V short it would look more like a 134A breaker on the secondary and that will not end well for 2.5mm cable!
 
Cheers lads I’m going to email the consultants that issued the drawing in morning to ask what they specifically require I’ll let you know what they come back with
 
Will be interesting to see what they have in mind. It is possible the 32A primary MCB was chosen to deal with switch on surges, but it may be better to use something like a 16A or 20A D-curve MCB instead.

Protecting the output wires to the sockets in the (hopefully unlikely) case of a short still seems to be missing but hopefully you will hear by tomorrow or Monday.
 
He's already got double pole MCB's in the socket, why does he need additional double pole MCB's in a DB? I suppose it all accords how long and vulnerable the lead are.

For the same reason we supply socket circuits from an MCB when every plug has a fuse in it.
The circuit feeding the socket needs to be correctly protected for overcurrent and fault.
 
I guess it also falls under 433.2.2 as the cables are longer than 3m and the output of the transformer could reasonably be taken as a "point where a change occurs".
 

Reply to 110v supply issue? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
843
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
714
Hi all, I've just installed an APC 6KVA SRT6KRMXLI. As a computer network engineer and electrician, I was a bit baffled by the 35mm gland that...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock