Search the forum,

Discuss 110v tranny in the Electrical Tools and Products area at ElectriciansForums.net

M

mickys86

Bosch drill stopped working Friday afternoon, one min it was fine the next it wasn't. I've noticed recently that the transformer has been getting really hot when plugged in, even when nothing is plugged into the transformer.

So I take the top off and check the voltage going in.... 240 somat and the voltage coming out was only 59v? Get the fluke thermometer on it.... 47 degrees centigrade.

Being Friday afternoon I say it's a job for another day, gets another transformer plugs in drill and still doesn't work.
So it must be the drill? But what's with the heat and only the 59v?
I'm going to take a look at it soon but at the moment this is all I have time for
 
Just out of interest, did you test between the earth and live conductor on the output as that should be in the region of 55V. Not sure about the excess heat.
 
Sounds like it's center tapped i.e. the secondary winding is center tapped to earth with 55V between each end of the winding and the center tap or 110V from one end of the winding to the other. Sounds like you're measuring the voltage between one end and the center tap.
 
Transformer iron and hysteresis losses predominate at no-load and the transformer is most inefficient, this results in an unloaded transformer often running warmer than when supplying a small load, particularly where the designer has used minimal iron to reduce cost or size. However, as the load increases beyond a certain point copper losses progressively dominate and each doubling of the load current results in the copper losses quadrupling in proportion.
 
Last edited by a moderator:

Reply to 110v tranny in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
13
Views
4K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I've done some basic wiring, but nothing beyond. I know enough to shut off the circuit. I have no basement or garage, so when I work with a...
Replies
6
Views
1K
Background is we are selling our house and moving out of state. I've been fixing big and little things and painting for several months now, as...
Replies
9
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock