Discuss 110v transformer reading 56v in the UK Electrical Forum area at ElectriciansForums.net

M

mrclox

Bit confused, have a 110v grinding machine and a Caroll and meynor 110v transformer
this one
Portable Transformer with 2 Output Sockets 3kVA | NoLinkingToThis

ive hooked the two together but the grinder is running slow. I checked the voltage reading across the two poles and it reads 56v.
Whats this all about then, faulty transformer? its rated 3KV/a and the grinder is only around 200Watts.

Any suggestions
 
you should get 55V from each pole to E. the E terminal is centre tapped so then you get 110V L-L.
 
thanks.
So I am out of my field of knowledge here.
The grinder is a normal usa plug domestic machine. How do i wire up the plug to get 110v out of the transformer.
:)
 
Your plug will have two small pins and a bigger one. My guess is that your grinder is connected to one small pin and the large (earth) pin. Connect the two grinder wires to the two small pins and you should be OK.
 
Tony's more the man for motors, but if you're trying to run a US 110V 60Hz motor from a 50Hz centre tap 230-110V TX then I can think of a few things that might go wrong!
 
wiring.jpg

Like this?

Your plug will have two small pins and a bigger one. My guess is that your grinder is connected to one small pin and the large (earth) pin. Connect the two grinder wires to the two small pins and you should be OK.
 

Attachments

  • Untitled-1.psd
    252.9 KB · Views: 14
no. the 2 flat pins on the plug are the ones that run the machine. the round one is E. however, as has been pointed out, the machine will probably be designed to run at 60Hz.
 
the 300w rating is the max. that the converter will supply, so it should be OK on your machine as long as the outlet socket matches your plug.
 
no. the 2 flat pins on the plug are the ones that run the machine. the round one is E. however, as has been pointed out, the machine will probably be designed to run at 60Hz.


correct it would run a bit slower @50 hz
the grinder being rated @60hz would run at 80 percent (approximate)
 
have to bribe the guys at the power station to pedal a bit faster. 3600rpm instead of 3000. :wheelchair:
 
grinder has to run at correct speed....too slow = problems and maybe dangerous as well due to sticking.....too fast = dangerous as well due to maximum disk spindle speed....

why do you have a USA model grinder here when there are plenty of cheap ones for sale in the UK? I'm only asking that as it's what an American would say if you took UK tools over there...


voltage converter may modify the frequency depending on model, might work ok...
 
Actually its a gemstone lapping grinder not available in uk. It will be ok if it runs slower.
grinder has to run at correct speed....too slow = problems and maybe dangerous as well due to sticking.....too fast = dangerous as well due to maximum disk spindle speed....

why do you have a USA model grinder here when there are plenty of cheap ones for sale in the UK? I'm only asking that as it's what an American would say if you took UK tools over there...


voltage converter may modify the frequency depending on model, might work ok...
 

Reply to 110v transformer reading 56v in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A friend asked me to have a look at a piece of equipment he had recently had installed. It's three phase with an internal transformer (415v to...
Replies
6
Views
994
I think I have a faulty 66kva transformer but have little to no experience with them (delta star I believe) Call out due to reported problems...
Replies
39
Views
4K
J
Hi All, I did a voltage test on the output side of a 110 transformer, the other day, due to a 110 SDS drill that kept cutting out. It turned out...
Replies
5
Views
8K
Engineer54
E
B
Hi all, I recently purchased a Chef's Choice Cone Maker 838, which is a fairly basic waffle iron. The problem is, that as it is a product from...
Replies
53
Views
16K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock