Search the forum,

Discuss 18th edition RCD max disconnection times!! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi all.

I am seeing different figures here all over the net, table3a (p363) states a 30ma RCD has a trip time of 300ms max.

So at 5x is the maximum 60ms? I seem to recall 200ms and 40ms for a 30ma and these are the figures I am seeing over the net...

Please I just want the correct figures for 1x and 5x in a 30ma standard AC rcd :p

Good morning :)
 
If your rcd is for additional protection then only the 5x reading is required on the certificate/report. This does not mean that you don’t have to carry out say the rcd auto test method if that’s what you prefer, but only the higher of the 5x test is required
 
BS4293 devices as Buzz states is an obsolete standard but you will still find them in service, ×1 200ms and ×5 40ms.
Current devices to EN61008 and 61009, ×1 300ms and ×5 40ms.
 
BS4293 devices as Buzz states is an obsolete standard but you will still find them in service, ×1 200ms and ×5 40ms.
Current devices to EN61008 and 61009, ×1 300ms and ×5 40ms.
Eh? Where's Buzz?
 
Hi, I'm just looking for some advice and this seemed the best post to find it.

I haven't got a copy of the regs in front of me so bare with me, please ?

First of all,
TN - 0.4 + 5s disconnection times
TT - 0.2 + 1s disconnection times

Is the above if you were using a BS60898 mcb for fault protection?

If you were using RCD (61008-1) for fault protection (high Ze) :
TT 300ms (0.3s)?

For both TN + TT systems, 40ms if using the RCD for additional protection?

Is this correct?

So on the test, or certainly the older test sheet what goes in the max disconnection time? Is it the max disconnection time for fault current protection and not the additional protection? Which would be 0.4 on the majority of TN systems for most circuits other than distribution circuits (with exceptions) and 0.2 for TT with low enough Ra if not 0.3?

Thanks for your patience reading this ??
 

Reply to 18th edition RCD max disconnection times!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
909
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
404
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
872
Hello all Well, been putting it off, but I need to upgrade my 17th edition to the 18th. Not been a practising sparky for over 5 years, but I have...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock