Discuss 2.5mm Radial Circuit- Rcbo Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

Mitch6278

Hi all,
Having currently finished a new install comprising of offices and an adjoining warehouse we have now been told by our QS that we need to change upto 99 breakers across 17 DBs!!!!
Basically we have installed a lot of 2.5mm T&E radial circuits serving floor boxes. The runs are a max of 50m.
The designer had put B20 RCBOs on the schedule and so we went with this. However the QS has now asked us to change these to B16 RCBOs because B20s are too big?? Am i missing something here?

Without trawling through the regs i was wondering if someone can point me in the right direction?

It seems a bit far fetched that the design would be so far out?
 
Hi all,
Having currently finished a new install comprising of offices and an adjoining warehouse we have now been told by our QS that we need to change upto 99 breakers across 17 DBs!!!!
Basically we have installed a lot of 2.5mm T&E radial circuits serving floor boxes. The runs are a max of 50m.
The designer had put B20 RCBOs on the schedule and so we went with this. However the QS has now asked us to change these to B16 RCBOs because B20s are too big?? Am i missing something here?

Without trawling through the regs i was wondering if someone can point me in the right direction?

It seems a bit far fetched that the design would be so far out?

That will depend on the actual current carrying capacity of the cable as installed. What's the installation method? Any thermal insulation? What about cable grouping?
 
Installation method is on a basket.. Cable grouping is minimal as its on a 300mm wide basket with about 8 or 9 circuits on.
Current carrying capacity?? Not sure but only supplying about 4/6 13A sockets?
 
Leesparky no he isn't...

Andy.. He has said that a 2.5mm radial should have a max breaker size of B16.. I just can't see it myself.. In my head I was always of the thinking that 2.5mm could easily take 20A?
 
Leesparky no he isn't...

Andy.. He has said that a 2.5mm radial should have a max breaker size of B16.. I just can't see it myself.. In my head I was always of the thinking that 2.5mm could easily take 20A?
Sounds odd to me as the other posts say ask his reasons, the design suggested 20A but he may have opinions which prove the design to be incorrect.
 
My first thought is if that's what the Q.S wants then do as he asks.
I assume you're employed so it wont cost you anything.

Second thought, maybe you should get the Designer to talk to the Q.S, it's their issue not yours.

What did the customers Spec, if any ask for?
 
Hi - for my trainee fun I looked at the good book. My design :
Perforated cable tray reference method E from 7.2 (p339), confirmed as Number 31 in Table 4A2 (p342). If that is the one you have installed, then 2.5mm ref E is 30A from Table 4D2A (p358) which is then derated due to multiple cables using Table 4C1 (p351) where item 3 says use 0.72 factor. So I get ... wait for it ... 21.6A . Of course this could be a load of trainee -------s :) . Cheers
 
And now for fun the max earth loop impedance from the OSG Table B6 (updated page 125) says 2.2Ohms for 16A or 1.75 for 20A. With 50m of 2.5mm I think r1+r2 is about 0.75Ohms leaving us with 1 Ohm spare for Ze, which should be easily the case. So I would have answered with 20A rcbo being ok if it was a test. Please let me know if I've made a mistake :)
 
Maybe the designer is concerned about the potential for voltage drop? 2.5mm2 will only give you almost 32 meters before you go over 5% at with a 20A Ib. At 50 meters the voltage drop will be around 18V (7.8%).

Of course, a 16A Ib would also have a voltage drop above 5% at 50m, but perhaps the actual voltage is sufficiently above 230V that the designer is happy to list this as a departure?
 

Reply to 2.5mm Radial Circuit- Rcbo Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I used to post here a fair bit many moons ago but I can't remember my old password not does the password reminder recognise my email so even...
Replies
2
Views
883
C
Right, bear with me, cos I know this might be boring for some of you, but a bit of advice from an experienced head or two would help to confirm my...
Replies
7
Views
17K
M
Hi sparkys. Just wanted some feedback on a interview I attended recently for a sparks in the maintenance social housing sector. After meeting the...
Replies
9
Views
1K
M
Hi All. I'm finally getting to start the installation that i'd asked advice on in October. However there have been some changes i've had to make...
Replies
19
Views
3K
Engineer54
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock