How would one figure out the following question?

The resistance of a 2.5mm copper cable is given as 7.41M Ohm per metre at 20 celcius and that of a 1.5mm copper cable is given as 12.1M Ohm per metre. A circuit wired with 25m of 2.5/1.5 twin with cpc sheathed cable would have an expected R1+R2 value measured at 20 celcius of ?
 
Break it down - this one isn't too hard to work out...

What does R1 stand for?
What does R2 stand for?

When taking an R1+R2 measurement you are getting the combined resistance of 2 cores of the T&E in this case, going up one core to a joint you made between them then back down the other core.

You know the length of each core and you also know the milliohm per meter of both legs.(not M Ohm as you have put which means Mega Ohms)

Have a go and post your sums and we will guide you :)
 
10^12 Terra = T
10^9 Giga = G
10^6 Mega = M
10^3 Kilo = K
Unit
10^-3 milli = m
10^-6 micro = u (It should be the greek letter MU but its a lot easier to do a u)
10^-9 nano = n
10^-12 peco = p

(R1+R2)xLength
(7.41+12.1)x25
19.51x2 5=487.75mOhms or just 0.48775 Ohms Might round it to 2dp and be 0.49Ohmx
 
remember because it says 20 Celsius you need to add correction factors x by 1.2 "20%" you are working out a calculation on a dead circuit but once it is pulling current the cable will get warmer and create more resistance

same with bs7671 you get the zs readings example 32a type b bs60898 = 1.37 ohm


80% of
1.37 ohm
1.37 ohms x 0.8 = 1.09ohms

i think gn3 and on site guide have this factor already applied

Edited misread the question as it said AT 20
Celsius
 
Last edited by a moderator:

Reply to 2394 practice question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...
Replies
7
Views
522
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
922
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
I have been going round in circles with this question. I just cant seem to get an answer remotely close to the options. Continuity of a ring...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock