if someone can show me how they worked this out

a circuit wired in 2.5mm/1.5mm twin with CPC sheathed copper cable has an r1 + r2 reading of 1.33 ohms, the value of r2 measured separately would be

1. 0.83
2.0.5
3.1.0
4.0.33

all in ohms

thanks
 
So just using the 1.67 to 2.67 ratio in the former equation multiplied by 6 and divided by 2 to give a fraction of 5 divided by 8 to use as a factor on the given value of resistance to resolve the answer.

Sorry... just being silly!
 
Because the earth is 1.5mm² and the line 2.5mm² the earth will have 1.67 times greater resistance than the line.

The total resistance is R1+R2, but because R2 will be 1.67 * R1 the total resistance will be 2.67 * R1 (1 R1 plus 1.67 R1).

So the resistance of the earth is the total resistance multiplied by (1.67 / 2.67) and this is equivalent to 5/8 (if you multiply both sides by 3).

Maths wise

R1 = R2 / 1.67
or
R2 = R1 * 1.67

Rt = R1 + R2

Substituting for R2
Rt = R1 + (1.67* R1)
Rt = 2.67 * R1

Since R1 = R2 / 1.67

Rt = 2.67 * (R2 / 1.67) = 2.67/1.67 * R2
So R2 = 1.67/2.67 * Rt
1.67 * 3 = 5
2.67 * 3 = 8

So R2 = 5/8 *Rt
 
where 5/8 expressed as a decimal is 0.625, as in a previous post.
 
Ignore my post number 5

If you cannot see where the 2.67 comes from by the use of post 8 then I am afraid I cannot assist.

total resistance is R1 + R2
R2 is 1.67 * R1 so you have

total resistance is R1 + (1.67 * R1)

therefore you have a single R1 plus 1.67 R1
1 + 1.67 = 2.67

so you have 2.67 R1
 

Reply to 2395 estimating r1 + r2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
8K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top