Was going to make the foolish suggestion that there should be 'as fitted' drawings available either on site or from the LEA but thought better of it.There is no way of knowing without further information if they are from the same source. I would suggest the main earth terminals need bonding together to a common main earth terminal along with the main protective bonding.
No it’s definitely 3 DNO supplies the old type cable with sheath earth & the other a new TNCSImagine school has its own substation so ultimately it's all the same supply, just different phases (in thr case of single phase) and same origin for 3 phase. Multiple heads but same source. Not uncommon when you think about that logistics of it.
One of the warehouses I was at earlier in thr month has 3 onsite substations, which multiple heads/intakes and not a single multi phase stickers in sight owing to suitable design keeping any case of touching multiple phases to a minimum, if at all.
Good shout i think, maybe worth noting on report, I doubt any classification codes can be give maybe FIThere is no way of knowing without further information if they are from the same source. I would suggest the main earth terminals need bonding together to a common main earth terminal along with the main protective bonding.
Not a clue on the phasing of the SP no coloured discsMaybe contact the DNO and ask if they can confirm the source for each individual supply.
It could be that the single phase supplies are tapped off the 3ph supply or all come from a cabinet / pillar onsite.
Are both single phase the same or different phases?
So all three supplies are separately meteredNo it’s definitely 3 DNO supplies the old type cable with sheath earth & the other a new TNCS
Yes all have separate metersSo all three supplies are separately metered
Given the different supply types I would be asking the DNO for their opinion on bonding the MET's togetherIf it's been like this for 50 years I'd imagine the main earth conductor sizes and main bonding conductor sizes are smaller than they would be today?
I also think that bonding the METs together seems a good solution.
At an absolute minimum I think the main bonding should be sized as though it was TNCS at the two TNS supplies, but if the METs were bonded then a lower resistance path than the water/gas pipes exists for any diverted neutral currents arising from a TNCS issue.