EICR finding 3 DNO supplies in main building.
The front end of building 3p 100 amp TNS, middle Sp 100 amp TNS, other part Sp 100 amp TNCS.
Water & Gas supplies are common to this building
This been in situ for over 50 years, any comments
 
At each main switch (for each supply) I would like to see a warning sign that says building is fed from multiple supply’s
A simple building plan showing where they are would be good too.

It is one thing the fire brigade wanted in a building I managed many years ago that had 2 supplies
 
Imagine school has its own substation so ultimately it's all the same supply, just different phases (in thr case of single phase) and same origin for 3 phase. Multiple heads but same source. Not uncommon when you think about that logistics of it.

One of the warehouses I was at earlier in thr month has 3 onsite substations, which multiple heads/intakes and not a single multi phase stickers in sight owing to suitable design keeping any case of touching multiple phases to a minimum, if at all.
 
There is no way of knowing without further information if they are from the same source. I would suggest the main earth terminals need bonding together to a common main earth terminal along with the main protective bonding.
 
There is no way of knowing without further information if they are from the same source. I would suggest the main earth terminals need bonding together to a common main earth terminal along with the main protective bonding.
Was going to make the foolish suggestion that there should be 'as fitted' drawings available either on site or from the LEA but thought better of it.
 
Imagine school has its own substation so ultimately it's all the same supply, just different phases (in thr case of single phase) and same origin for 3 phase. Multiple heads but same source. Not uncommon when you think about that logistics of it.

One of the warehouses I was at earlier in thr month has 3 onsite substations, which multiple heads/intakes and not a single multi phase stickers in sight owing to suitable design keeping any case of touching multiple phases to a minimum, if at all.
No it’s definitely 3 DNO supplies the old type cable with sheath earth & the other a new TNCS
 
If it's been like this for 50 years I'd imagine the main earth conductor sizes and main bonding conductor sizes are smaller than they would be today?

I also think that bonding the METs together seems a good solution.
At an absolute minimum I think the main bonding should be sized as though it was TNCS at the two TNS supplies, but if the METs were bonded then a lower resistance path than the water/gas pipes exists for any diverted neutral currents arising from a TNCS issue.
 
There is no way of knowing without further information if they are from the same source. I would suggest the main earth terminals need bonding together to a common main earth terminal along with the main protective bonding.
Good shout i think, maybe worth noting on report, I doubt any classification codes can be give maybe FI
 
Maybe contact the DNO and ask if they can confirm the source for each individual supply.
It could be that the single phase supplies are tapped off the 3ph supply or all come from a cabinet / pillar onsite.
Are both single phase the same or different phases?
 
Maybe contact the DNO and ask if they can confirm the source for each individual supply.
It could be that the single phase supplies are tapped off the 3ph supply or all come from a cabinet / pillar onsite.
Are both single phase the same or different phases?
Not a clue on the phasing of the SP no coloured discs
 
My first thought in this sort of situation is regarding separation of systems.
Given Lister1987's comment regarding "as installed" drawings, there's probably a real risk of multiple supplies being present in some part of the building. Apart from there being different earthing systems, there's then the risk of someone turning off one supply and being "surprised" to find something still live.
And then there's the situation with systems which intentionally cross dividing lines - e.g. fire alarms, school bell system, ...
 
If it's been like this for 50 years I'd imagine the main earth conductor sizes and main bonding conductor sizes are smaller than they would be today?

I also think that bonding the METs together seems a good solution.
At an absolute minimum I think the main bonding should be sized as though it was TNCS at the two TNS supplies, but if the METs were bonded then a lower resistance path than the water/gas pipes exists for any diverted neutral currents arising from a TNCS issue.
Given the different supply types I would be asking the DNO for their opinion on bonding the MET's together
It could get a bit messy with varying supply loop impedances and mixed earthing methods especially if the supplies are coming from different substations, there is also the consequences if the school is supplied from different subs of one substation supply losing it's earth and becomes earthed from another substation via the bonded MET's at the school
 

Reply to 3 DNO in school buildings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
843
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock