Maybe contact the DNO and ask if they can confirm the source for each individual supply.
It could be that the single phase supplies are tapped off the 3ph supply or all come from a cabinet / pillar onsite.
Are both single phase the same or different phases?
Not a clue on the phasing of the SP no coloured discs
 
My first thought in this sort of situation is regarding separation of systems.
Given Lister1987's comment regarding "as installed" drawings, there's probably a real risk of multiple supplies being present in some part of the building. Apart from there being different earthing systems, there's then the risk of someone turning off one supply and being "surprised" to find something still live.
And then there's the situation with systems which intentionally cross dividing lines - e.g. fire alarms, school bell system, ...
 
If it's been like this for 50 years I'd imagine the main earth conductor sizes and main bonding conductor sizes are smaller than they would be today?

I also think that bonding the METs together seems a good solution.
At an absolute minimum I think the main bonding should be sized as though it was TNCS at the two TNS supplies, but if the METs were bonded then a lower resistance path than the water/gas pipes exists for any diverted neutral currents arising from a TNCS issue.
Given the different supply types I would be asking the DNO for their opinion on bonding the MET's together
It could get a bit messy with varying supply loop impedances and mixed earthing methods especially if the supplies are coming from different substations, there is also the consequences if the school is supplied from different subs of one substation supply losing it's earth and becomes earthed from another substation via the bonded MET's at the school
 

Reply to 3 DNO in school buildings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
962
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock