Despite what I said above about teleswitches having delays, it is possable that as this is a block of flats that there is only one switch controling an off peak contactor in each house. That would switch on all the off peak supplies at the same time but does not explain Lucians point about why dont the fuses blow when replaced.
 
Pc1966 - I am pondering what the OP said about the trips and fuse ruptures ‘at the same time as 2kA spikes’ - see OP’s #7. You mention these spikes ought not to trouble the fuses unless perhaps the spikes occur as the fuses begin to rupture, arc and open circuit - all short term events at and after rupture not before them. BS88 gG fuses are current limiting. The inductance of each line’s circuit carrying high phase current generating a forward induced emf of high voltage attempting to maintain the phase currents at these amperages. These line currents increase briefly markedly - a spike - during the rupture phase but are limited by the fuses limiting properties as they open circuit and extinguish the arc? Could this explain the 2kA spiking?
 
Last edited:
It is all rather odd. The first issue is the fact both MCCB and fuses go, typically if well designed that means a very big fault, i.e. so the MCCB let-through is above the fuses pre-arcing I2t and so even though it trips, the fuse is already a goner.

Now we don't know the MCCB type or settings in any detail here, so that current where selectivity is lost might be as low as 0.8kA or so if bandly designed...but the time duration of the 1.9kA as 2 cycles or 0.04s is not enough to explain the fuse going unless it was already really hot.

However, the currents prior to that were only around 200A so fuses would be effectively cold then?

So did the monitoring get something wrong? Has it some upper limit where the CTs saturate and really the surge was really closer to 5-10kA for 2 cycles?

I guess there might be somewhere that has something causing a major fault current such as water getting on to terminals or similar and it going all arc-flash as typically a L-anywhere arc are migrates so you end up with bolted 3-phase style fault. But surely someone would notice the sound and/or damage? Doing that a couple of times I would expect to burn off metal and make it permanently shorted or open enough to stop.

The OP has not said what time it is tripping at, maybe that would give us more ideas?
 
My think-piece does not explain 3 fuses rupturing at the same time. Even if passing an overload current for minutes it would be surprising if they ruptured at the very same time. The OP may not have been perfectly accurate in this regard - the fuses ruptured about the same time maybe.

I am veering more toward a cabling or busbar fault which is producing a short-circuit or earth fault or both. What about treeing in feeder and sub main cables? I am no expert nor have any experience of it but seem to remember it can be made worse or a cable fault event triggered when the cable warms up and cools down regularly which is a particular problem for well loaded underground cables in winter. Even newish cables can be prone to treeing if they have manufacturing defects.

Electrical treeing - Wikipedia - https://en.wikipedia.org/wiki/Electrical_treeing
 
Last edited:
Might the 2kA spike be caused by supply transformer tap-changing in response to overnight mains voltage sag when electric heating is switched on in the neighbourhood? Perhaps tap change is not swift and clean. At night few flat dwellers would notice if it was not. Tap change causes a significant voltage and current step upwards.
 
Apartment block about 8 or 9 years old. Had a couple of issues in the past. The feed in question only serves the apartments water pumps lifts etc on a different incomer
This makes me a bit curious if the past history has a bearing on this fault
So what were the past issues you mention and for how long has the current fault been occurring
 
Thought I'd post an update on my head ache. For some reason the power stayed on from Friday until 6.00 pm tonight that is and as usual mccb tripped as well as taking out all three incoming fuses. Still cant find any reason for this so was just wondering. Is there any way that this could be a supply fault from the substance by any chance ? Or am I just clutching at straws now ?
 
What was the previous issue you mentioned? How far away is the sub-station? What business or industry is nearby? Is it electric water and space heating - I assume it is since you have not said otherwise. Do any tenants report their lighting sagging/swelling or flickering because of voltage disturbances? Has it only just started to happen or been a problem that has become worse over time? Any major water leaks, vermin infestation, flooding, ingress of rain, fires, building damage near switchgear, busbars and cabling since which this problem has occured? Might you rig up power analysis monitor again at incomer? Solar pv on the roof? Electric vehicle chargers? Are nearby premises suffering similarly? What are phase-neutral voltages during day and at night?

It sounds like the time of outage is now earlier than before but is it always in the evening and overnight?

Suggest you contact the DNO to find out if they know of any network/supply faults in the vicinity and to inform them of this problem.
 
Rats can gnaw cables:

There’s a Rat in the Switchgear, what are we going to do? | BASEC - https://www.basec.org.uk/news/2018/5/8/theres-a-rat-in-the-switchgear-what-are-we-going-to-do/#:~:text=Regular%20cable%20such%20as%20PVC,sheathing%20itself%20may%20be%20attacked.&text=Choosing%20the%20right%20cable%20can,help%20the%20rat%2Dproof%20outcome.

Rats are nocturnal and most active at dusk and dawn as they set out to forage and return. In the UK rats prefer to nest in places that are warm, secure and with easy access to food and water. Rats need regular access to a water supply, unlike mice who can, if necessary survive on just the moisture in their food. See:

https://www.rentokil.co.uk/blog/where-do-rats-nest/#:~:text=Rats are nocturnal and most,buildings in search of food.

They also need material to make nests; the sheath of swa cables for example.
 
Last edited:
It is difficult to see from the OP's profile what level of experience they have, and this is possibly one of those faults that requires a bit more on the ground in depth analysis of the issues surrounding it
I'm beginning to wonder why the OP isn't answering some of the questions being asked when they may be pertinent to identifying the problem
If a PQA has been monitoring the supply is this long term monitoring and are there any trends that can seen that may give any indications as to the timing of the fuses blowing / MCCB tripping
With all the bad weather recently especially the heavy rainfall has that had any effect on the frequency of fault occurring
 

Reply to 3 Phase power keeps on tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
686
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Recently my RCCB keeps keeps tripping intermittently. It can happen between several hours to few days when a trip will occur. During the trips, no...
Replies
35
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock