Discuss 3 Way Switch at Two Locations in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi,

I have five setups in my home (Kitchen, three hallways and back porch lights) that have two light switches (one at each end of the room or, with the back porch lights, switches in two different rooms). I am replacing all of the switches in the home to a different color. One of the hallways and the back porch lights work perfectly. However, the other two halls and the kitchen I can't get to work right for the life of me. I figured I would start with a hallway and see if anyone can help. I'm going to insert some images for reference:

Screen Shot 2021-02-28 at 4.50.19 PM.pngScreen Shot 2021-02-28 at 4.45.22 PM.pngScreen Shot 2021-02-28 at 4.47.44 PM.pngScreen Shot 2021-02-28 at 4.48.21 PM.png
 
You either have the 'hot' wire on switch 1 on the wrong terminal, or the wire to the lamp on switch 2 is on the wrong terminal.
You say there is a 'hot' wire at switch 2 when switch 1 is connected. Is that a one wire that is 'hot' when switch 1 is up, and a different one when switch 1 is down?
Do all US switches have large, unenclosed potentially 'hot' terminals on the side of them like yours, along with the bare 'ground' wires?
 
You either have the 'hot' wire on switch 1 on the wrong terminal, or the wire to the lamp on switch 2 is on the wrong terminal.
You say there is a 'hot' wire at switch 2 when switch 1 is connected. Is that a one wire that is 'hot' when switch 1 is up, and a different one when switch 1 is down?
Do all US switches have large, unenclosed potentially 'hot' terminals on the side of them like yours, along with the bare 'ground' wires?
The hot wire at switch 1 is connected to the correct screw according to everything I can find and the instructions that come with the switches.

I disconnected switch two and tested your question. When Switch 1 is Up, the red wire at switch 2 is hot. When Switch 1 is Down, one of the black wires at switch 2 is hot.

As far as I know, this is what all light switches look like in the US. I've never seen any that look different.
 
Those switches look decidedly lethal to UK eyes. The only ones with that much exposed terminal were last made in the '60s.
Sounds like switch 1 is wired correctly.
If there are two black wires at switch 2, try swapping them over.
 
I got the hallway working. The thing you said that sparked the lightbulb in my head was the thing about different wires in switch 2 being hot depending on if the toggle in switch 1 was up or down. Now, I will see if that's the same issue i the other two places. Thanks!
 

Reply to 3 Way Switch at Two Locations in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
507
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
391
Hi, I have two 3-way toggle switches by the opposite sides in my garage. Is it possible to replace both of them with motion sensors? Thank you. .grig
Replies
7
Views
391
Hi all, currently doing a job at a house where there are 3 switches In the hallway to control the hall lights. All 1 gang switches, one at...
Replies
2
Views
547
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock