Working on an empty property which has 4 RFCs. 3 of these are showing no continuity across R1 R2 and Rn. The wiring is around 30 years old and each room has 2/3 single sockets. Each of these sockets is fed by a single 2.5mm T&E. What's going on here? Is it likely the sockets are being fed from a ring under the floor with a junction and spur for each socket? This could give plausibility for their being a break in one of the junctions but it just doesn't make sense. I'm heading back tomorrow to investigate properly but keen to know if anyone has come across similar before?
 
You say 4 RFC's and 3 have no continuity on r1, rn, and r2........and there is a single 2.5 T/E at each socket. Well in that case the three are clearly not RFC's!
Assuming other tests are satisfactory if you are there to alter these circuits treat them as 20a radials, or if they need a 32a OCPD they will have to be rewired as rings.
 
If you have 2 cables at the fuse board but only 1 at the sockets then at some point someone has split the ring under the floor most likely in a JB

not a particulary big issue and most likely been like this for years
 
Can you tell with the age of the sockets themselves? Ie 30 year old, splash painted the same colour as the wall will be original on rfc... anything new, or doesn’t match might be additions.
Also listen out for squeaky floorboards.... hint that they have been lifted.... that could be where the joints are.
 
Presumably the end to end testing was done at the DB if you only have single cables feeding at the sockets? Looks like you'll have to test for continuity for each socket back to the one leg to try and make sense of the arrangement or start pulling floorboards up. Sounds like you may be right about an RFC with the sockets dropped off in spurs which I've come across a few times but you should still get an end to end reading at the DB.
 

Reply to 3 x RFC all with no continuity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
857
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
752
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
673
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top