Hi

I am planning to convert an old office building with 3Ø 100amp supply into 14 self contained student studios (approximately 20 sqm)

Each studio will only have 2 electric heaters, 2 lights, 10 double sockets. The hot water will be gas heated.

I'm hoping someone will be able to tell me if the current 3 phase, 100amp supply be enough to power 14 units?

Your help is much appreciated

Thanks
 
Possibly, probably not. Electric hobs for example would make this a definitely not.
You need to employ the services of an electrical designer to calculate you a maximum demand figure to present to the DNO, then they will tell you what is possible and for how much.
You might get lucky and the current cable may be capable of supporting 160A fuses, you may get unlucky and have to pay for a larger supply cable.
 
I am planning to convert an old office building with 3Ø 100amp supply into 14 self contained student studios (approximately 20 sqm)

Each studio will only have 2 electric heaters, 2 lights, 10 double sockets. The hot water will be gas heated.

I'm hoping someone will be able to tell me if the current 3 phase, 100amp supply be enough to power 14 units?
so whats your loading ?;)
 
Relying on "internet" advice could be an expensive mistake

My recommendation is to get a price from the DNO to upgrade the incoming supply - then you can build it into your costings .

But beware, it may take a few weeks for them to come out, then if you go ahead there will be a delay in in actually happening..

Hope this helps
 
As above, this needs to be correctly designed and planned. However just looking at the top line numbers, assuming full occupancy it looks rather light, averaging just 21A per apartment, which could seriously limit what tenants do and when. You may be supplying just two fixed electric heaters, that's not going to stop tenants adding their own. If they all put a kettle on around the same time when they get up in the afternoon (student accom, right?) this could overload the installation. Seeing what's easily available from the DNO should be your first step.
 
If it’s for students - based on your description most likely will be ok.

Wouldn’t be sticking my name to it until I had full loading specs from each unit. Ie heater sizes etc
 
Perhaps consider heating from your gas boiler? Bear in mind those kind of rentals often leave without paying energy bills which no doubt would be high if you have electric heating.
 
Hi,as already mentioned,you need someone to do an assessment,with knowledge of the build plans,and methods of mitigating peak loads.

It is not impossible,to arrange things,to achieve a reliable outcome,but is not a guess anyone will make,without full knowledge of all the factors....or you may be handing out your freshers,complimentary,travel-kettles...
 
Changing to gas heating might just shift the problem from an undersized electrical supply to an undersized gas supply.

Improving the insulation in the studios might allow smaller electrical heaters to be specified, but kitchen appliances might be a bigger problem; the students are likely to want kettles, fridges and microwaves, toasters and possibly hobs. Even allowing for the fact that not everything will be on at once, I think electric heating and the small kitchen appliances will exceed the available supply. Only a proper design and better specification of the loads to be supplied will tell you whether the current supply is adequate or what larger supply will be required.
 
You could just supply those students with a paraffin stove and wind-up LED lamp...tell them a 6 month lease can go towards their Duke of Edinburgh award...
 

Reply to 3Ø 100amp Question in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
Hello, We are converting a former office into 10 self-contained flats with kitchens, showers, heaters all electric, no gas. We have been offered a...
Replies
1
Views
723
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
2K
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
305

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock