Discuss 5 amp Radial Bs1363 Socket in the UK Electrical Forum area at ElectriciansForums.net

J

john100

Hi

I have a Radial circuit wired with 2.5mm T&E , which is protected by a 3 amp MCB due to the fact that it is switched via a home automation relay rated at 5amp.

My question is this

Given the above scenario is it ok to install/wire a BS1363 socket if I know that the load that will be plugged in will be less than 3amp or do I have to fuse down with an FCU to stop a 13amp load which may be plugged in by the home owner. If I label the socket accordingly would this be acceptable

J
 
As already mentioned , not worth any other fusing with the MCB rating that your installing , you won't get any discrimination …….
 
Thanks for the advice

Just out of interest , is there any situation where installing a BS1363 socket is not allowed on a radial circuit for circuits rated at less than 13 amp.

I.e would it be acceptable to have a 6 amp MCB 1.5mm T&E Radial protected circuit that uses BS1363 sockets without labelling them

J
 
I've got a stash of 3's and 4's as they're useful for making up heating control systems
 

Reply to 5 amp Radial Bs1363 Socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
432
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
641
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
466
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Got some amateurish questions. Please excuse me but want to set this straight in my head. Do amp ratings only matter when current is being drawn...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock