Discuss When do amp ratings matter in the UK Electrical Forum area at ElectriciansForums.net

Neptune

DIY
Reaction score
24
Got some amateurish questions. Please excuse me but want to set this straight in my head.

Do amp ratings only matter when current is being drawn i.e. an appliance plugged in, light fitting, etc.
  • To expand, if I have a 50amp MCB with a 1mm T&E cable going into a 5amp junction box, would that matter or would it have any adverse effects?
  • If in the above example, I had a socket at the end of the cable and a heater plugged in, I assume that would be problematic as the 1mm cable isn't correctly sized
  • Similarly, if I had a ring main where every point was terminated into 5amp junction boxes instead of sockets, I assume that would be fine too
  • However, if one of the points had a socket and the socket had a fridge plugged into it, the 5amp junction boxes would be an issue as you now have a higher current being drawn through the ring.

I would really appreciate your wisdom on the above scenarios. Thanks in advance.
 
Pedantically 'no', as without current flowing none of it matters.

In reality 'yes', as you also have to consider what happens if/when there is a fault, possibly in the fixed cable or accessories themselves and not in any planned load. Then the lack of correct over-current protection for the down-stream cable and accessories, etc, can lead to damage or even a fire.
 
Pedantically 'no', as without current flowing none of it matters.
That’s what I expected. Thanks

Then the lack of correct over-current protection for the down-stream cable and accessories, etc, can lead to damage or even a fire.
I don’t understand this. Can you give an example please?
How can you have a fire if nothing will be plugged in or draw current from the circuit? Clearly if there will be a current draw, the I understand that junction boxes, cables and breakers need to be sized appropriately.
 
I don’t understand this. Can you give an example please?
How can you have a fire if nothing will be plugged in or draw current from the circuit?
  • Someone nails a cable doing DIY
  • A local mouse chews a cable
  • The person installing the sockets trapped a cable against a back-box and eventually the pressure punctures the insulation
  • There is poor manufacturing control for an accessory or reel of cable
I am sure others on this forum will have examples of how you can get a fault in an installation!
 
A basic factor to consider is that the current carrying capacity of a cable determines the size of protection device to be used. Obviously I.0mm cable is nowhere near 50amp rated. Well over 50amps could be flowing with a 15amp (approx) rated cable which, as a result, could become a bit warm, to say the least.......an extreme fire hazard, of course.
This is not even taking into account the danger of short circuit fault currents possible, as could be involved with some of the examples indicated above.
 
Last edited:
Under 'fault conditions' a relatively small csa cable will survive a large fault current so long as the over current device disconnects the supply quickly

The bigger issue is a prolonged over current , this is when insulation breaks down

JW did some interesting videos on passing large current through small cables and to see how long it took before the cable got warm
 
Got some amateurish questions. Please excuse me but want to set this straight in my head.

Do amp ratings only matter when current is being drawn i.e. an appliance plugged in, light fitting, etc.
  • To expand, if I have a 50amp MCB with a 1mm T&E cable going into a 5amp junction box, would that matter or would it have any adverse effects?
  • If in the above example, I had a socket at the end of the cable and a heater plugged in, I assume that would be problematic as the 1mm cable isn't correctly sized
  • Similarly, if I had a ring main where every point was terminated into 5amp junction boxes instead of sockets, I assume that would be fine too
  • However, if one of the points had a socket and the socket had a fridge plugged into it, the 5amp junction boxes would be an issue as you now have a higher current being drawn through the ring.

I would really appreciate your wisdom on the above scenarios. Thanks in advance.
KAre you a Spark? if yes then I WOULD TRY SOMETHING EKSE TO DO AS A LIVING
 
When sizing cables and circuit breakers the much simplified rule is:

The cables maximum current carrying capacity must be greater than the current the connected equipment draws.
The fuse/circuit breaker used needs to have a higher current rating than the connected load, (so the fuse/mcb doesn't operate during normal conditions) but lower current rating than the cable used (so under fault conditions the circuit is switched off before the cable is thermally damaged. Remember, fuses and circuit breakers are mostly designed to protect the cables not the equipment connected to the electrical circuit

There are more factors to consider when selecting cable and circuit protection sizes and ratings such as:
The cables length.
How and where the cable is installed.
How many other cables your cable is bunched with.
The external earth loop impedance value.

Under 'fault conditions' a relatively small csa cable will survive a large fault current so long as the over current device disconnects the supply quickly
Even when everything is correctly sized and rated the conductors can still get surprisingly hot during heavy fault currents! Just not hot enough to cause damage to the cable.

JWs experiment is way more scientific than my attempt of just connecting bell wire across the mains:
 

Reply to When do amp ratings matter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
431
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
638
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
812
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock