Discuss 6.0mm earthing conductor to MET on TNS in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Marcus Vaughan

-
Esteemed
Reaction score
240
Hello.
I am carrying out an inspection on a domestic TN-S system. First observation is that I can see 16.0mm earthing conductor fro CU to MET - but then is steps down to 6.0mm connecting to the supply cable.
This should be 16.0mm - shouldn't it? I am going by table 54.7 in the big yellow book.
Sorry if this has been asked before.....
 
Still not saying a word but how do you use the adiabatic equation when you don't know the fuse size/type at the service head.
 
I would use the Adiabatic on the worst case scenario say 100 amp fuse and also allow for other sizes.
Thing is most of the time depending on the actual fault current you need the let through energy from the manufacturer as the time is below the 0.1 second minimum given in bs7671
Often tho the 0.1 second is just used for time if fault current is over the max given in table.

Really the only time I've used the Adiabatic is when your disconnect time is closer to 5 seconds for fuses and then it's often required to use a bigger sized conductor

If anyone's still got the red copy of the 17th edition it has the data in for bs 1361 fuses as these are now replaced in yellow book with bs88
 
Last edited:
Hello.
I am carrying out an inspection on a domestic TN-S system. First observation is that I can see 16.0mm earthing conductor fro CU to MET - but then is steps down to 6.0mm connecting to the supply cable.
This should be 16.0mm - shouldn't it? I am going by table 54.7 in the big yellow book.
Sorry if this has been asked before.....

Minimum required size of an earthing conductor is 6mm.
You can't just fail it on the basis of table 54.7 because the designer may have calculated the size using the a diabetic equation.
 
Thanks for the responses. It's always good to get the reassurances.
Everything tested just fine - I was just initially alarmed when I saw it step down from 16mm to 6mm at the MET.
Every day is a school day!
 

Reply to 6.0mm earthing conductor to MET on TNS in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
770
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
808
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
465
Has anyone seen one of these please ? I propose a little earthing tape to identify it. I am upgrading the system and will put in place a new MET...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock