Discuss 6 Amp RCBO 13 Amp load in the UK Electrical Forum area at ElectriciansForums.net

Top Cat

-
Esteemed
Arms
Reaction score
993
Doing a rewire at the moment in an empty house. I am using RCBO's mostly so when i got 1 room complete i wired the 4mm radial into the RCBO so we could get the kettle going.

After several brews i went to disconnect it only to find i had wired it into a 6 Amp RCBO!

The trip never operated once with a 3 KW kettle on it. It was a Square D RCBO.

Going to swap the breaker on Tuesday when the merchants open but surely this should not happen.
 
if it's a 3kW kettle, it should pull close on 13A, but you know what liars these manufacturers are.
 
The thing is the kettle would have only been on for a minute and breakers tend not to trip until 1.5 times there rated value...which the kettle would have only just been over that, but then would take a certain amount of time before it trips anyway, which you would have to look at the graphs in the regs book to find out how long it would take...you will probably find it takes longer than boiling a kettle!
 
MCB's and RCBO's don't trip that quickly at there operated current. Page 301 BGB has the time/current characteristics for type B MCB's/RCBO's.
 
A 6A mcb/rcbo will hold 1.67 times its rated capacity for up to an hour so if you only had a kettle on it would need to be over 10A to trip, that's if the kettle pulls 3kw.
 
The trip never operated once with a 3 KW kettle on it. It was a Square D RCBO.

Check the time/current characteristics for a 6A MCB and you will see why. 3KW Kettles are normally only drawing current for a couple of minutes, for a full kettle. Half full of water, then even less time...
 
Next time you put the kettle on, clamp your ammeter on the cable at the MCB... All will become clear :)
funnily enough, just done that. clamp in main tail, current reading 2.4A. switrched on 3kW kettle, reading up to 10.8A. so 3kW my arse!
 
Glad I'm not the only one to have put the kettle on lol.

My 2.2Kw kettle pulls 2.3Kw (Got a keypad meter here which will give your KW load, load cost etc etc), got a voltage of 244v at the moment though so its about bang on.

It's a damn site more accurate than clamp metres.
 

Reply to 6 Amp RCBO 13 Amp load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock