O
Discuss 6A RCBO for this Legrand? in the UK Electrical Forum area at ElectriciansForums.net
I queried with Legrand about fitting one of their RCBO's in a similar looking CU as yours. They said it wasn't compatible & won't fit?
The 6a MCB I was thinking of replacing with an RCBO, was a Legrand 06156. Legrand said their current RCBO was incompatible with the CU the 06156 was fitted in. Is that the same MCB as in your CU? Let us know if you find the opposite is true, make my forthcoming job a bit easier.Somebody else said something similar hence the thread!
Yep normally do that myself. However in my particular case, customer is converting existing bedroom into bathroom, and existing bathroom into bedroom, don't ask me why! So new bathroom needs RCD, and existing bathroom pull cord will need converting to normal flush switch. No room at the Inn, where CU is located, but converting mcb - rcbo would have been a good'en.Just put a fused connection unit rcd in?
Sent from my SM-G930F using Tapatalk
Just put a fused connection unit rcd in?
Sent from my SM-G930F using Tapatalk
More expensive though, when all you after is the additional RCD side, does it matter if the fuse or mcb goes first?That's a very poor design, you can't get discrimination between the fuse and the mcb. A better solution is an RCD in a separate enclosure.
More expensive though, when all you after is the additional RCD side, does it matter if the fuse or mcb goes first?
It’s not a bodge in my opinion (and that of others I think), just an acceptable method of resolving an issue. Another example, if someone hasn't an rcd protected RFC whilst using an electric lawn mower, then a socket outlet RCD or adaptor could be an acceptable answer.Depends on whether you take pride in doing a job properly, or just want to bodge it and scarper really
Hoping to save some time on this!
Need a 6A RCBO to fit this Tenby / Legrand board - anyone know if they are readily available?
View attachment 32763
Thanks
Are you trying to replace the 6A that is in the off position ? as it looks like it is on the RCD protected part of the c.u.
These gray Tenby c.units must be about 15 years old as I think that Legrand took them over and updated the c.u. and JUST rebadged the mcb/rcbo,s to Legrand.
About 3/4 years ago the mcb/rcbo's changed to new type but fit in c,u.
Tell me they are wrong, as I need to do the same replacement?I queried with Legrand about fitting one of their RCBO's in a similar looking CU as yours. They said it wasn't compatible & won't fit?
That's me stuffed, only have single module available.3. The obsolete part number is 007731 and beware its a 2 width module unit.
Reply to 6A RCBO for this Legrand? in the UK Electrical Forum area at ElectriciansForums.net