Discuss 8.5kw shower wires in 4mm, burnt terminals in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I've told llthe landlord to get other electrican to call me if he has any issues returning to sort, also when I undid the isolator Fascia the cables just fell out the back.

I checked over the board before I disconnected the supply and some of the terminals were LOOSE :/

Sounds like he had plastic wrists
 
I had a similar situation yesterday.
Reports of shower isolator getting hot. Go to check it out. 6mm installed last year supplying a 9.5kw shower. Burnt out connections.
I would always install a 10mm if wirring for a new shower.

20170728_140007.jpg
 
^^ even if I knew it was going to be a 7kw shower, I would still have fitted 6mm cable

Which is fine, and if you wish to do that then there is nothing preventing you from doing so. But if the calculations show that 4mm is suitable then you cannot criticise someone for installing 4mm, whatever your personal preference in the situation.
 
10.0 doesn't prevent loose connections and burnt conductors.
You're quite right.
I always tighten connections. Leave them a minute to settle then u can normally get another quatre turn on them.
The reason we always wire a new shower supply in 10mm, is so the customer has some flexibility when coming to choose a shower.
And like ive seen before, when the customer decides on him/her self to uprate the shower to a 10.5kw. Not realising the existing 6mm will not be adequate. (Normally a trip back to b and q for them)
I would always recommend not installing a electric shower, much better of a combi, but needs must sometimes
 
I had a similar situation yesterday.
Reports of shower isolator getting hot. Go to check it out. 6mm installed last year supplying a 9.5kw shower. Burnt out connections.
I would always install a 10mm if wirring for a new shower.

View attachment 37616
Hi - not to disagree at all with ccc etc, but this pic does look like the heat is concentrated at the termination rather than evenly along the cable. And as the neutral seems unaffected (?) it perhaps suggests in this case the cause was poor termination of the line conductor?
 
Hi - not to disagree at all with ccc etc, but this pic does look like the heat is concentrated at the termination rather than evenly along the cable. And as the neutral seems unaffected (?) it perhaps suggests in this case the cause was poor termination of the line conductor?

Hi wilko. Yes that was indeed the problem.
Only been in for 8 months, so someone with plastic wrists must of installed it.
I just think it's good practice to always install a 10mm cable for a new shower install.
 
A job I'm starting a new build bungalow has been specified 16mm twin and earth for 10.5kw shower complete with a wall mounted isolation switch outside of the ensuite, which is a stud wall!
Oh the joys.
 
A job I'm starting a new build bungalow has been specified 16mm twin and earth for 10.5kw shower complete with a wall mounted isolation switch outside of the ensuite, which is a stud wall!
Oh the joys.

Good luck.

Is that due to cable running through alot of insulation?
Never seen a 16mm at a shower before.
At least you can install a double 47mm metal box in the stud partition
 
Apparently 3 layers of insulation are going in so looking at reference method 101 even 16mm twin only pulls 46 amps reference method 101.
At 10.5kw I'm looking at a loading of 43-44 amps so the 16mm will be able to handle it.
I need to consult the builder and maybe request some boards are fixed above the insulation so a 10mm can be clipped above the insulation.
They won't budge to a lower rated shower tho.
Doubt I'd even manage to fit a 47mm box in the wall as the studs are only about 50mm deep
 
That is a narrow stud
Thankfully always 4x2 with the joiners we work with.
Would not like to terminate a 10mm in anything less than a double 47mm box.
To be honest don't like wirring showers fullstop :tearsofjoy::tearsofjoy:
 
Apparently 3 layers of insulation are going in so looking at reference method 101 even 16mm twin only pulls 46 amps reference method 101.
At 10.5kw I'm looking at a loading of 43-44 amps so the 16mm will be able to handle it.
I need to consult the builder and maybe request some boards are fixed above the insulation so a 10mm can be clipped above the insulation.
They won't budge to a lower rated shower tho.
Doubt I'd even manage to fit a 47mm box in the wall as the studs are only about 50mm deep

Don't like using them, but could u fit a 47mm faster fix box to give u that extra room.
 
That is a narrow stud
Thankfully always 4x2 with the joiners we work with.
Would not like to terminate a 10mm in anything less than a double 47mm box.
To be honest don't like wirring showers fullstop :tearsofjoy::tearsofjoy:
I'll get round it as I really don't want to be installing 16mm but it's not mine or my company's spec
4mm ring circuits as well.
 
Last edited:
If there is any kind of airing cupboard then a suggestion if re-routing the cable isn't an option would be a contactor operated by a lighting pull switch, cable size thus of no concern then. If the designer has issue with this then give then let them try terminate 2 x 16mm T&E into a standard shower switch and deep box.
 

Reply to 8.5kw shower wires in 4mm, burnt terminals in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Hi all, A few months ago we had a Triton Martinique 8.5kw shower installed. We've noticed that the temperature seemed quite low. Its what I'd...
Replies
13
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
442
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock