Errr have I said something!!!
all I was saying last week is I recommend 10mm on a 40a so no iinconvenience occurs to the user
On the contrary, there is a very important point to be made here and all electricians must understand that while the nominal volts in UK are 230V, the actual volts are anywhere from 255V to 218V as already mentioned on in this thread.
For a 9500W shower for example, the currents are:
at 218V = 35.96A
at 230V = 37.93A
at 240V = 39.58A
at 252V = 41.56A
If you are consistently getting 252V at a property, and you install a 40A breaker for a 9.5Kw shower, then you will be called back to rectify the tripping shower, although you can try to explain to the customer as much as you like that the BRB states......, the nominal voltage is supposed to be ........ etc etc.
Yes, but the point is that the regulations are written allowing for this.
230 is only used as a sop to Europe.
When n.v. was reduced from 240 to 230 all the values we use were also derated ( x230/240 )
so that the results were the same.
If the voltage never went above 240V then we would have higher CCC values which we were allowed to use.
Do you know the csa of 100A fuse wire?
I have a rule where anything over 8KW I install a 10mm cable.
There are some new grants available in Wales recently where they are installing insulation free of charge for people on benefits, they even installing between floors and in stud walls for houses with energy rating of E or below.
I will not risk installing a 6mm cable or keeping a 6mm cable for a 9KW shower when next week they could get this grant and put insulation ontop of the cable changing the max current it will take.
If they insist that they wont allow me to put a 10mm cable in then they sign an advisory form stating that the cable must be upgraded if anything happens around the cable - i.e. insulation in loft or walls.
What ever happens cover your back!
Yeah, the CSA of a 100A fuse is 3.142mm2.
So - a 3.142mm² conductor can carry 100A 'for ever'.
Even with the maximum derating of 50% for thermal insulation a 3.142mm² conductor can carry 50A 'for ever'.
So - a 3.142mm² conductor can carry 100A 'for ever'.
Even with the maximum derating of 50% for thermal insulation a 3.142mm² conductor can carry 50A 'for ever'.
Why do you think it necessary to make up your own rules rather than use the regulations?I have a rule where anything over 8KW I install a 10mm cable.
If the customer agrees that is acceptable.There are some new grants available in Wales recently where they are installing insulation free of charge for people on benefits, they even installing between floors and in stud walls for houses with energy rating of E or below.
I will not risk installing a 6mm cable or keeping a 6mm cable for a 9KW shower when next week they could get this grant and put insulation ontop of the cable changing the max current it will take.
Fair enough.If they insist that they wont allow me to put a 10mm cable in then they sign an advisory form stating that the cable must be upgraded if anything happens around the cable - i.e. insulation in loft or walls.