Convince them they have to upgarde the cable or downgrade the shower or the house will burn down. Quote them a fortune. Then tell them they need a rewire...else the house will burn down. Quote them a fortune.

Robbing people blind is fine as long as you convince yourself its for their own safety......
 
I feel that if you tell them and put it in writing then your covered - the owner said no to bigger cable and they knew if they where going to have it insulated then the cable needs upgrading. Its on their back then if the place burns down - you have noted that no insulation in place and action to be taken and they ignored your advice!

Have you ever tried running 40 amps down a 6mm T&E and then dropping a sheet of fiber glass on it? (or getting a mouse to) Does the cable catch fire when you do this?

Why dont you make them sign an advisory form stating that if someone puts a petrol bomb through their letter box and the house burns down, that you offered to weld shut their letter box but they refused. Just to cover yer back like....
 
Convince them they have to upgarde the cable or downgrade the shower or the house will burn down. Quote them a fortune. Then tell them they need a rewire...else the house will burn down. Quote them a fortune.

Robbing people blind is fine as long as you convince yourself its for their own safety......

Jesus you'll end up on rouge traders with an answer like that , not really acceptable
 
That's going to look great on open forum isn't it
People have enough trouble trusting tradesmen without nonsense like that being in public view
Come on Trev, you know I'm only messing about. Just annoys me people advising clients to fix things that arn't broken.
 
Dave you may well be messing about but put yourself in a potential customer's position. A lot of people are nervous enough about tradesmen ripping them off and we get plenty coming on here looking for advice.
 
I agree that there's an over reaction to fixing things that aint broken but you can't tell people's inflection from what they type mate.
 
Just to add my tuppence worth,
I have seen many, many 8kw and above showers wired in 2.5mm flex from the isolator to the actual shower unit in my time testing, none of which showed any signs of damage, poor terminals and terminations cause many more,
I think in an ideal world there should be a 'domestic shower diversity' added to the regs, it irritates be to give a code 6mm supplying showers in houses, in fact I often give it a code 3 rather then 2 if there is no heat damage.
 
Just to add my tuppence worth,
I have seen many, many 8kw and above showers wired in 2.5mm flex from the isolator to the actual shower unit in my time testing, none of which showed any signs of damage, poor terminals and terminations cause many more,
I think in an ideal world there should be a 'domestic shower diversity' added to the regs, it irritates be to give a code 6mm supplying showers in houses, in fact I often give it a code 3 rather then 2 if there is no heat damage.

Dont understand why you would code it at all ?
On what grounds ? for what rating of shower is 6mm unacceptable ?
 
If you design your circuits correctly you must be aware that.
As a 9.5KW shower draws 41.3A you are unable to use a 40A MCB You need to use the next size up. This would be a 45A
it is correct that the tabulated current carrying capacity of a 6mm T&E cable is 46A this is the value prior to any correction factors being taken to account. I would suggest that the there are multiple cables exiting the DB at the same place so the grouping factor will reduce the cable rating below 41.3A without taking into account any other factors.
It is not acceptable to assume that no harm will be caused to the cable as the shower will only be on for a short while or the loading is only 1A over the 40A MCB rating.
When the electrical installation certificate is issued you are sating that the installation complys with BS 7671 and is a legal document in the event of future problems.
I would suggest if this size shower is to be installed a 10mm cable minimum cable should be used. Pay now or pay later.
 
If you design your circuits correctly you must be aware that.
As a 9.5KW shower draws 41.3A you are unable to use a 40A MCB You need to use the next size up. This would be a 45A
it is correct that the tabulated current carrying capacity of a 6mm T&E cable is 46A this is the value prior to any correction factors being taken to account. I would suggest that the there are multiple cables exiting the DB at the same place so the grouping factor will reduce the cable rating below 41.3A without taking into account any other factors.
It is not acceptable to assume that no harm will be caused to the cable as the shower will only be on for a short while or the loading is only 1A over the 40A MCB rating.
When the electrical installation certificate is issued you are sating that the installation complys with BS 7671 and is a legal document in the event of future problems.
I would suggest if this size shower is to be installed a 10mm cable minimum cable should be used. Pay now or pay later.

Welcome steve
what scam do you work for
 
How do you know the calculated cable capacity and suitable MCB rating without calculations, you also need to take into account loop values prior to changing MCB's
 

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
165
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock