Discuss A 2000-watt dishwasher is running on 6 amperes, C grad MCB, how is it possible? in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
0
I have by mistake used 6amps C grad MCB on a 2000-watt dishwasher. though I was asked to put 10 amps. but it is running properly.
how it is possible and is it safe?

thanking you.
 
Last edited:
If the 2000 watt rating is what it says on the info sticker on the back of the dishwasher then it's the absolute maximum power the machine will ever run at and most of the time the actuial power consumption will be considerably less. Also a 6 A MCB will happily allow 7 or 8 Amps through it without tripping for a good period of time.

All that aside, the MCB is sized to protect the circuit wiring, not the appliance itself. Whether it's safe or not is down to the current rating of the MCB being appropriate for size of the wiring going to the socket outlets.
 

Reply to A 2000-watt dishwasher is running on 6 amperes, C grad MCB, how is it possible? in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Wiring to new dishwasher causes garbage disposal to stop working. I just installed a GE dishwasher and came across a problem with the...
Replies
1
Views
667
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
588
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
489
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
826
Hey folks Apologies if my question is too basic. I am an Electrical Engineer but do not work in the field. I am looking for feedback to ensure...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock