Discuss Acceptable readings for a NEW installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

Guest 004

OK peeps

I have just tested an 185 4 core SWA, and have got readings of 40 Megs on L2 to earth and L3 to earth. Although this is accepatable according to the regs, I feel it is unacceptable as a NEW installation, and indeed there is evidence of water on some of the switchgear, which clearly indicates water tracking between the cores. So I am refusing to pass it untill readings of >200 Meg are acheived. This equipment actually forms part of the EDF supply cable, so is in effect theirs, so I suppose its up to them to accept it.

Would like to have peoples thoughts on this?

whether to pass it or not? will EDF accept it?

Thanks
 
40 million amps have to flow or something like that to create a short. But as you say if it's new it should be higher, mYbe will dry out.
 
Come on get a grip before the thread gets trashed.185mm2 cable and water between the cores? Pull yourself together man.
 
How do you explain the readings? what's the environment, humidity, type of termination enclosures, what sort of spark did the glanding etc

How can anyone make a judgement on a forum?
 
You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!

This job has 3 risers, each with an 185mm 4 core feeding it. EDF turned up on Frfiday and QA'd the other 2 supplies and equipment. Unfortuately I was not part of the team when EDF were on site. So must be something in it.
 
How do you explain the readings? what's the environment, humidity, type of termination enclosures, what sort of spark did the glanding etc

How can anyone make a judgement on a forum?

The enviroment is the same as the other 2 185's that were tested and were fine, with readings >499 Meg tested at 1000V

- - - Updated - - -

Is there a nest of insects at the terminations

lol .......No
 
You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!
If this cable is part of the DNO supply then it is not subject to BS7671, it will be whatever the DNO decides is acceptable (EDF in this case).

If this is a lot lower than other identical cables/risers then I would be concerned too, did you try wiping the terminations riser etc. with a dry clean rag ? it is more likely the terminations or the switchgear being damp than between cores, and did you test between all of the cores (all 10 tests) ?
 

Reply to Acceptable readings for a NEW installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
hello i have been asked to install a kiosk at a farm entrance to accept 100 a 3 phase,RURAL TT ,at present there is a bungalow slap in the middle...
Replies
3
Views
777
Hi all. I'm starting a new project at work and part of it is installing SPDs onto D.B.s in telecommunication installations. All of the current...
Replies
11
Views
5K
So today i go to a job to remove 3 x dual sockets, 1 x light switch and 1 x light fitting from a bedroom that the customer is converting into a...
Replies
38
Views
6K
Hello chaps, I class myself as having good electrical knowledge and good at my job. However, heating systems is something I have little to...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock