Hi all

I've been ask to change another dual tarriff consumer unit (17 useable ways) I've changed a few of these in past but choice does seem limited and always seem to pay over the odds for what it is. I am considering adapting a dual rcd FuseBox consumer unit. I'm just checking am I missing anything in plan for this? The FuseBox consumer units come with 3 neutral bars from what I remember so no problem there. So my theory is all I need to do is purchase another main switch and consumer unit cable kit BG Consumer Unit Cable Kit - https://electrical-showroom.co.uk/catalog/product/view/id/5501/s/bg-consumer-unit-cable-kit?gclid=Cj0KCQiAmL-ABhDFARIsAKywVadon4FzxhouM62TtMtRkwj9jG-WerEUWITZY3D1xmTN1iJ3U53trHMaAsjTEALw_wcB

And I'm good to go? Or am I missing anything? Been a long day : )
 
Given it's a Fusebox board you're proposing I would use Fusebox gear only to avoid the possibility of it coming back to bite you if something did go wrong.

You should also consider adding a 4th neutral bar... you're going to have 1 for each RCD and 1 for the off-peak side which means you won't have one to use for splitting the switched neutral on the dual RCD side. You could probably get away with using the main switch terminal but again, to ensure your backside is covered I would use the cables how they are intended by adding another neutral bar.
 
Given it's a Fusebox board you're proposing I would use Fusebox gear only to avoid the possibility of it coming back to bite you if something did go wrong.

You should also consider adding a 4th neutral bar... you're going to have 1 for each RCD and 1 for the off-peak side which means you won't have one to use for splitting the switched neutral on the dual RCD side. You could probably get away with using the main switch terminal but again, to ensure your backside is covered I would use the cables how they are intended by adding another neutral bar.
Thanks SparkyChick I've actually just had to take cover off my own CU to check how would all be linked together. Does look like 3 bars would do job but your right 4th would be better. Call me a numbnut but how do you actually go about fitting a 4th bar? Cheers
 
Thanks SparkyChick I've actually just had to take cover off my own CU to check how would all be linked together. Does look like 3 bars would do job but your right 4th would be better. Call me a numbnut but how do you actually go about fitting a 4th bar? Cheers
That largely depends on the manufacturer.

Hager for example will sell you neutral bars and the clips required to mount them on the bar at the top. I've just looked on the Fusebox site and they don't appear to have anything in the way of that kind of accessory so it may be better to use another manufacturer.

My primary area of concern in suggesting this is that if you attempt to use the cables that would ordinarily be present in a split load board, one end is typically terminated in a crimp lug and the other is welded. Without the crimp lug you may struggle to properly terminate two cables in the main switch. With the lug you may find it difficult to get a good sound connection as the lugs are quite solid and cage clamps rely (to an extent) on deforming the conductors to get a solid connection. But also modifying them may also invalidate the type testing used to ensure it conforms to the required standards.

It's a tricky one and to be honest I would perhaps be inclined to use two separate boards to avoid any of this kind of nonsense.
 
That largely depends on the manufacturer.

Hager for example will sell you neutral bars and the clips required to mount them on the bar at the top. I've just looked on the Fusebox site and they don't appear to have anything in the way of that kind of accessory so it may be better to use another manufacturer.

My primary area of concern in suggesting this is that if you attempt to use the cables that would ordinarily be present in a split load board, one end is typically terminated in a crimp lug and the other is welded. Without the crimp lug you may struggle to properly terminate two cables in the main switch. With the lug you may find it difficult to get a good sound connection as the lugs are quite solid and cage clamps rely (to an extent) on deforming the conductors to get a solid connection. But also modifying them may also invalidate the type testing used to ensure it conforms to the required standards.

It's a tricky one and to be honest I would perhaps be inclined to use two separate boards to avoid any of this kind of nonsense.
Thanks SparkyChick really helpful. Going with the two boards might actually be a better bet the FuseBox ones are cheap enough. I'll have to check out the dimensions
 

Reply to Adapting CU for dual tariff, am i missing anything in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
Just had a phone call from an existing customer. He has just had solar panels put in, along with a very large battery. He has a single up front...
Replies
12
Views
2K
I've been working as a domestic electrician for 6+ years now alongside two NICEIC approved contractors and I hold my 1/2/3 City & Guilds NVQ, 18th...
Replies
7
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock