Discuss Adding a light to a circuit with no earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

robo83

-
Reaction score
40
Got to quote a job where the existing circuit does not have an earth.

It's swapping a pendant for 3 Downlights.

The board was changed about 2 yrs ago and has labels indicating no CPC on lighting.

All Fascias are plastic. Where do I stand Regards this, I understand you can accept no CPC on lighting with Fascias but not sure about modifying the circuit.
 
How hard would it be to add a 4mm earth?
 
My thought is to look in CU and see if cct starts with cpc in earth bar, then look at the cable inco to pendant, it might just be cut back ? (optimistic me)
 
Can't see that you can. If you are adding new wiring, reg 411.3.1.1 'A cpc shall be run to & terminated at each point in wiring & at each accessory except a lamp holder having no exposed conductive parts.....'.

If it was the case of just replacing luminaires, Class 2 and note etc.
A cpc will be ran in by the op I would imagine if altering installing new wiring to luminaries.
Granted it may not do anything but a class 2 luminar will have no exposed conductive parts so the wiring will be no more dangerous than previous with a relivant note on a MWC
 
That's the issue, the way I read the OP's post?
Yeah no cpc to existing circuit db is labelled as such.
However if installing class 2 there is no exposed conductive parts so a fault to the enclosure cannot give a person an electric shock by touching it.
Wiring hopefully covered for overload and short circuit protection by a adequate protective device.
I don't see a problem with it as long as it's clearly identified at the db which it is.
Also note the MWC

Obviously class 1 luminaries are a no no unless a cpc is installed from the db perhaps
 
A cpc will be ran in by the op I would imagine if altering installing new wiring to luminaries.
Granted it may not do anything but a class 2 luminar will have no exposed conductive parts so the wiring will be no more dangerous than previous with a relivant note on a MWC

The definition of a cpc is a conductor that is connected to the MET.
So I would read 411.3.1.1 as each point requires a conductor that is connected to earth.
612.2.1 requires that continuity of protective conductors is carried out during testing.
132.16 requires that all existing equipment and arrangements are suitable for safe alteration before the work is carried out.

I would personally not extend a circuit with no cpc.
 
Yeah no cpc to existing circuit db is labelled as such.
However if installing class 2 there is no exposed conductive parts so a fault to the enclosure cannot give a person an electric shock by touching it.
Wiring hopefully covered for overload and short circuit protection by a adequate protective device.
I don't see a problem with it as long as it's clearly identified at the db which it is.
Also note the MWC

Obviously class 1 luminaries are a no no unless a cpc is installed from the db perhaps

That's not the way I read the reg; new wiring, cpc to each terminated point.
 
1 Pendant to 3 downlights.. so +2 points extension to the circuit?

Balls....
I read it as 1 pendant to another fitting with 3 lights on... My fault....

I'm sure the OP will clarify all this... :tearsofjoy::tearsofjoy::tearsofjoy:
 
So let's say the circuit has a cpc
If class 2 lights are fitted what is the cpc actually doing?
Yes it's required to be terminated at each point and accessory but in the case of class 2 fittings it function is not required.
By that I don't mean you'd just snip the cpc off by the way.

Would you then not change a db if all lights are class 2 and the switches and no cpc to circuit?
Suitably labelled as required

The work covered ,the wiring is no more dangerous than the previous way it was.
 
The definition of a cpc is a conductor that is connected to the MET.
So I would read 411.3.1.1 as each point requires a conductor that is connected to earth.
612.2.1 requires that continuity of protective conductors is carried out during testing.
132.16 requires that all existing equipment and arrangements are suitable for safe alteration before the work is carried out.

I would personally not extend a circuit with no cpc.
A definition of a cpc also says connecting exposed conductive parts of equipment to the MET of which there would be no exposed parts of class 2 equipment.
Continuity of cpc would be N/A as there is no cpc to the circuit.
The wiring installed to the altered wiring would contain a cpc, granted it's doing nothing but again it's being installed in the altered works.
If someone in the future wants to fit metallic fittings then the db is labelled to advise against it.

Just my view on it.
I appreciate your view so not starting an argument Andy.
 

Reply to Adding a light to a circuit with no earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
461
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock