Discuss Adding a light to a circuit with no earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

It mightn't be more dangerous, but it would still fail to meet the minimum safety standard for electrical installation work, i.e. BS7671.
Why? It's changing a pendant to 3 down lights.
Class 2 fittings hopefully.
Same as if you change a db and reconnect the lights.
If all class 2 you wouldn't rip the place apart installing a cpc unless agreed with customer
 
Why would it fail to meet BS7671? Quite simply because it wouldn't comply with it.
By that logic a lighting circuit containing no cpc must not be re-energised when renewing a consumer unit even with class 2 fittings fitted and suitably labelled which is allowed by bs 7671

A cpc is required to connect exposed conductive parts to the MET so if a fault of negligible impedance between live and earth happens current will flow and disconnect the protective device,but tell me what exposed parts are there on a class 2 light?
 
But the point is Ian, if you are installing new wiring, i.e. alteration or addition, then whatever you do must comply with current edition BS 7671.

If you are installing a new CU and connecting a lighting circuit without a cpc, you are not adding to etc, and 'conditions' apply, otherwise the circuit should not be connected (most guidance I've read, also recommends advising customer to rewire said circuit).

I have not read, or been informed by others, that it is compliance with BS 7671, to add new wiring to an existing circuit without a cpc.
 
By that logic a lighting circuit containing no cpc must not be re-energised when renewing a consumer unit even with class 2 fittings fitted and suitably labelled which is allowed by bs 7671
Firstly replacing a distribution board is quite different as you are not altering the existing circuit (leaving aside the protective device for now). So you are only required to verify your installation work (namely the replacement distribution board) - so you would ensure that the protective devices will operate in the time required. It doesn't mean that you are taking responsibility for installation methods; core colours etc.

Secondly, you state "with Class II fittings fitted and suitably labelled which is allowed bs BS7671". Can you quote where BS7671 suggests that this is acceptable, or prescribes any label for this eventuality? I can assure you that it is not contained within BS7671.
 
Available from Niceic direct
Bs 7671 does not go into long explanations of rules and regulations.
It's a set of regulations hence why we have guides and guidance notes to break the information down in to chunks IMG_2846.PNG
Firstly replacing a distribution board is quite different as you are not altering the existing circuit (leaving aside the protective device for now). So you are only required to verify your installation work (namely the replacement distribution board) - so you would ensure that the protective devices will operate in the time required. It doesn't mean that you are taking responsibility for installation methods; core colours etc.

Secondly, you state "with Class II fittings fitted and suitably labelled which is allowed bs BS7671". Can you quote where BS7671 suggests that this is acceptable, or prescribes any label for this eventuality? I can assure you that it is not contained within BS7671.
 
Whilst researching this topic, I found reg 412.2.3.2, which I'll let you chaps read and explain, cos my heads hurting now.

On this point, would running a cable from a 12v dc transformer, to a remote luminaire require a cpc?
 
Whilst researching this topic, I found reg 412.2.3.2, which I'll let you chaps read and explain, cos my heads hurting now.

On this point, would running a cable from a 12v dc transformer, to a remote luminaire require a cpc?
Well I'd say if it's selv then the cpc is required to be not connected to the primary side of the source
 
My thought is any new cable must have a cpc, and the cpc must be tested and confirmed for connectivity to the MET. And these are new cables to the new downlight positions...
 

Reply to Adding a light to a circuit with no earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
483
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock