Discuss Adding more sockets to ring main in the UK Electrical Forum area at ElectriciansForums.net

you'd need to fit a 13A RCD FCU,as you can only spur 1 socket outlet off a ring without fusing down.
 
Most definitely not - it's only the front bit of an RCD socket that's protected, not the terminals !

Edit - reply to OP, Tel nipped in before me.
 
Keep this for just this sort of question....

IMG_0262.PNG
 
Yes Anthony, but i want to spur off with more than one socket and nothing i plug in will no where near touch 13A

You don't want to add another RCD if the existing ring is already protected. Either extend the ring or fit an FCU with 13A fuse and feed your sockets from that.
 

Reply to Adding more sockets to ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
209
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
306
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
483
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
230

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock