Discuss Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
214
Evening All,

I have an industrial install this week, installing 200A feeds to MCCB panels in workshop, with 70mm SWA

Im just working out the CPC at the DB, not done this for a while so just wanted to check it..

S= root(I2 X T) / K

The fuses are BS88-2 200A, i have another DB in exactly the same place with same sized cable, and the ZS is 0.04 PFC 5.2KA

so using those figures-

Root ((5200x5200)X0.1= 1644.38/ 115= 14.2mm

So 16mm will be adequate. does this look correct?
 
The 10.4 is, I assume, 2 x the original 5.2 he had to give him an approximation of the 3ph fault current based on the line - earth fault current.

The question is where did the 5.2 come from?
 
The 10.4 is, I assume, 2 x the original 5.2 he had to give him an approximation of the 3ph fault current based on the line - earth fault current.

The question is where did the 5.2 come from?

2 x a zs value is a very poor way to approximate a three phase fault current.

Chris
 
I don't believe there's any need to double it (*1.732 to be more precise). Don't forget... It's pefc were concerned with here, not pscc (line to neutral or line to line)
 
The actual 3phase fault current was not calculated I just typed a figure of 10.4 as 5.2 x 2=10.4
Obviously it would be 5.2x root 3
But I don't have that symbol on my phone right now
 
Thanks spark shark that's what I was getting at in first post, it's not the 3 phase fault it's the earth,hence the 5.2 figure, sintra threw me when he sAid about being 3 phase
 
I think the point I'm trying to make is... Doesn't matter how much fault current flows between line to line/line to neutral... It won't effect what size CPC u need to use
 
5750 your right. I didn't work all the figures out it was mainly the equation I wanted to clarify, I can confirm the actual pefc once on site this week
So it's only ever the single phase fault current to earth basically. Cheers
 
I'd also go as far as to check with the fuse manufacturer's instructions what it's actual disconnection time is as opposed to using the nominal figure of 0.1. You will probably find it is even lower, thus having a more favourable bearing on your final cpc size :)

You win some you lose some, but it's always worth doing if you have a roll of Xmm in the van which you think might do, but using 0.1 as your disconnection time throws up Ymm.
 
I have just had a quick check on BS88-2 and even using the I²t value I can only get down to 6.1mm￾² and as the disconnection time at 5750A is 0.025s and that gives about 7.9mm² so it looks like you are stuck with at least 10mm².
 
Evening All,

I have an industrial install this week, installing 200A feeds to MCCB panels in workshop, with 70mm SWA

Im just working out the CPC at the DB, not done this for a while so just wanted to check it..

S= root(I2 X T) / K

The fuses are BS88-2 200A, i have another DB in exactly the same place with same sized cable, and the ZS is 0.04 PFC 5.2KA

so using those figures-

Root ((5200x5200)X0.1= 1644.38/ 115= 14.2mm

So 16mm will be adequate. does this look correct?


Stick with your original CPC size of 16mm, buggered if i'd install a 10mm or less CPC for a 200A feed supplying MCCB panels!! By the way, what is/are the Max Zs values on the MCCB's??
 
Why not see if you can use the armour as the CPC?
 
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!

Very true Eng54 but the OP hasn't mentioned that additional bonding is required, so I thought that the armour should be OK for his purpose.
 
Unfortunately, most don't even consider the bonding side of things in the first place, so just because it hasn't been mentioned by the OP, doesn't mean it's not a consideration that should be taken into account....
 
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!![/QUOTE]

I am very interested as to why bonding would cause a problem.
 
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!

I am very interested as to why bonding would cause a problem.[/QUOTE]

Because it becomes very difficult to have armouring which complies with the requirements for a bonding conductor.
 
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!

I am very interested as to why bonding would cause a problem.

Because it becomes very difficult to have armouring which complies with the requirements for a bonding conductor.[/QUOTE]

Please explain more, do you mean the reason is because bonding has to be bonded from the m.e.t ?? And not from the mccb panel
 
Please explain more, do you mean the reason is because bonding has to be bonded from the m.e.t ?? And not from the mccb panel

For example if bonding was required to be 50mm copper at the intake then it would have to have a path back to the MET which is never less than 50mm copper.
Steel is 8 times less conductive than copper so to achieve this with steel armour the actual CSA of the armour would have to be 50x8 = 400sqmm of steel.

Or at least that is my understanding of it, I'd wait for the local earthing expert to share his knowledge before taking it as gospel though.
 
Zs=0.04Ω
V= 230V

230/0.04= 5750A

-----------------

I=5750A
T= 0.025s (Read this from you post, also agrees with regs)
K=115


S = ((5750²)x0.025)
-----------------
115

S= 7.906 mm²

So with a 10mm² you will be oversized by 21%.

-----------------------------------------------

If you want to use the Steel armoured of the SWA:

I=5750A
t=0.025s
K=51 (assuming thermoplastic)

S = ((5750²)x0.025)
-----------------
51

S= 17.827 mm²

If you're thinking 'Jesus Christ that seems small' remember that the cpc only has to take this fault current for 0.025 seconds. And 21% is a nice amount of headroom, only if the result was borderline would I move up too the next size.

I presume you got the result:

S= 15.811mm² ????

That's because you used 0.1 as the value of 't' instead of 0.025. t is the actual disconnection time for your PFC (not maximum allowed or anything else). The actual disconnection time can be found by looking at the disconnect time curves in the reg, or better still from the manufacturers data sheet.

Hope that helps. =)
 
Last edited:

Reply to Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
832
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock