Evening All,

I have an industrial install this week, installing 200A feeds to MCCB panels in workshop, with 70mm SWA

Im just working out the CPC at the DB, not done this for a while so just wanted to check it..

S= root(I2 X T) / K

The fuses are BS88-2 200A, i have another DB in exactly the same place with same sized cable, and the ZS is 0.04 PFC 5.2KA

so using those figures-

Root ((5200x5200)X0.1= 1644.38/ 115= 14.2mm

So 16mm will be adequate. does this look correct?
 
Is this install 3 phase. If so your PFC seems to be low.
 
The 10.4 is, I assume, 2 x the original 5.2 he had to give him an approximation of the 3ph fault current based on the line - earth fault current.

The question is where did the 5.2 come from?
 
The 10.4 is, I assume, 2 x the original 5.2 he had to give him an approximation of the 3ph fault current based on the line - earth fault current.

The question is where did the 5.2 come from?

2 x a zs value is a very poor way to approximate a three phase fault current.

Chris
 
I don't believe there's any need to double it (*1.732 to be more precise). Don't forget... It's pefc were concerned with here, not pscc (line to neutral or line to line)
 
The actual 3phase fault current was not calculated I just typed a figure of 10.4 as 5.2 x 2=10.4
Obviously it would be 5.2x root 3
But I don't have that symbol on my phone right now
 
Thanks spark shark that's what I was getting at in first post, it's not the 3 phase fault it's the earth,hence the 5.2 figure, sintra threw me when he sAid about being 3 phase
 
I think the point I'm trying to make is... Doesn't matter how much fault current flows between line to line/line to neutral... It won't effect what size CPC u need to use
 
5750 your right. I didn't work all the figures out it was mainly the equation I wanted to clarify, I can confirm the actual pefc once on site this week
So it's only ever the single phase fault current to earth basically. Cheers
 
I'd also go as far as to check with the fuse manufacturer's instructions what it's actual disconnection time is as opposed to using the nominal figure of 0.1. You will probably find it is even lower, thus having a more favourable bearing on your final cpc size :)

You win some you lose some, but it's always worth doing if you have a roll of Xmm in the van which you think might do, but using 0.1 as your disconnection time throws up Ymm.
 
I have just had a quick check on BS88-2 and even using the I²t value I can only get down to 6.1mm￾² and as the disconnection time at 5750A is 0.025s and that gives about 7.9mm² so it looks like you are stuck with at least 10mm².
 
Evening All,

I have an industrial install this week, installing 200A feeds to MCCB panels in workshop, with 70mm SWA

Im just working out the CPC at the DB, not done this for a while so just wanted to check it..

S= root(I2 X T) / K

The fuses are BS88-2 200A, i have another DB in exactly the same place with same sized cable, and the ZS is 0.04 PFC 5.2KA

so using those figures-

Root ((5200x5200)X0.1= 1644.38/ 115= 14.2mm

So 16mm will be adequate. does this look correct?


Stick with your original CPC size of 16mm, buggered if i'd install a 10mm or less CPC for a 200A feed supplying MCCB panels!! By the way, what is/are the Max Zs values on the MCCB's??
 
Why not see if you can use the armour as the CPC?
 

Reply to Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi All, I think I have confused myself somehow and feel I am spiraling into further confusion. When I am doing the equation, it is saying the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock