E
Engineer54
Why not see if you can use the armour as the CPC?
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!
Discuss Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net
Why not see if you can use the armour as the CPC?
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!
There should be no problem using the armouring as a straight CPC, the problem comes if there is any bonding involved at these MCCB panels!!
I am very interested as to why bonding would cause a problem.
Please explain more, do you mean the reason is because bonding has to be bonded from the m.e.t ?? And not from the mccb panel
Or at least that is my understanding of it, I'd wait for the local earthing expert to share his knowledge before taking it as gospel though.
Where is D.W. Cockburn when you need him?!?
Reply to Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.