Zs=0.04Ω
V= 230V

230/0.04= 5750A

-----------------

I=5750A
T= 0.025s (Read this from you post, also agrees with regs)
K=115


S = ((5750²)x0.025)
-----------------
115

S= 7.906 mm²

So with a 10mm² you will be oversized by 21%.

-----------------------------------------------

If you want to use the Steel armoured of the SWA:

I=5750A
t=0.025s
K=51 (assuming thermoplastic)

S = ((5750²)x0.025)
-----------------
51

S= 17.827 mm²

If you're thinking 'Jesus Christ that seems small' remember that the cpc only has to take this fault current for 0.025 seconds. And 21% is a nice amount of headroom, only if the result was borderline would I move up too the next size.

I presume you got the result:

S= 15.811mm² ????

That's because you used 0.1 as the value of 't' instead of 0.025. t is the actual disconnection time for your PFC (not maximum allowed or anything else). The actual disconnection time can be found by looking at the disconnect time curves in the reg, or better still from the manufacturers data sheet.

Hope that helps. =)
 
Last edited:

Reply to Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi All, I think I have confused myself somehow and feel I am spiraling into further confusion. When I am doing the equation, it is saying the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock