That was my inclination yes - I had understood from several calculators and manufacturer specs that 2.5mm 3-core clipped to external wall would be adequate for my couple of sockets to my shed?

It would likely be fine for a couple of sockets yes, it is definitely not fine for a 32A circuit though.
While my main board is new and the secondary CU is on a 40A RCBO, would you put in another rcd at the shed end for good measure or is this pointless?
No I wouldn't install another RCD as that would not comply with the wiring regulations

My secondary CU which the shed is all mcbs and given this runs my heating, would be more than inconvenient if the shed sockets were to blow.

Yes that will be inconvenient but with an RCBO at the supply end you are stuck with the risk of that happening, even if you put another RCD in the 40A RCBO will almost certainly trip first in a fault.

will endeavour to consult my electrician friend in the design as you suggest. He struggles with English a bit though.

You may need to get someone else to help with the design of the job then, understanding the wiring regulations can be difficult even for some people who don't struggle with English.
 
It would likely be fine for a couple of sockets yes, it is definitely not fine for a 32A circuit though.

No I wouldn't install another RCD as that would not comply with the wiring regulations



Yes that will be inconvenient but with an RCBO at the supply end you are stuck with the risk of that happening, even if you put another RCD in the 40A RCBO will almost certainly trip first in a fault.



You may need to get someone else to help with the design of the job then, understanding the wiring regulations can be difficult even for some people who don't struggle with English.
So helpful and sincerely appreciated. Thank you.

Rest assured, I will get this checked and notified as part of a more complex battery install i'm having done professionally next month. I am a stickler for paperwork, and this is as much about my curiosity and wanting to learn and impress my electrician friend. Where I have done similar DIY in the past, qualified electricians have told me my work is perfect and have been happy to do the final CU termination and notify - but in hindsight, this was probably more luck than judgment as admittedly I had not involved them in the design. I respect the 2.5mm is controversial and not how others may do it. I've got to get the SWA round some very tight spaces though. I just want to avoid anybody finding an obvious 'bodge' or non-compliance.

I think this is the last question —would this new design be more appropriate? Should I put a corresponding MCB at the shed end in a waterproof DIN enclosure? A full CU seems overkill now, but from other installs I've observed, there should at least be a switch over there? I've updated my design below.

Thank you again and excuse my ignorance.
Blank diagram (1).jpeg
 
Last edited:
Heating ?? - Not an Off Peak supply is it by any chance as you could be back to square one!!
Good call out thanks. This CU is actually for an Air Source Heat Pump.

The contractor (not the guys who rewired the rest of the house) put in a great big 10 way CU for 3 ASHP MCBs. It's only on a 45A RCBO but the ASHP/Immersion never draws more than 15A. Obviously, it's less than ideal if it shuts my heating down, but I guess I can isolate the non-critical shed in the event there's a fault with it. It's only running a garden vacuum/pressure hose and some cordless chargers.
 
Last edited:
. I respect the 2.5mm is controversial and not how others may do it.
It is not controversial, nor is it a situation of being 'not how others would do it'. If you had followed your original design of a 32A MCB protecting the 2.5mm cable it would have been non-compliant and potentially dangerous.
However following your new design of a 20A MCB protecting the 2.5mm it is likely to be compliant and safe subject to confirmation.

I've got to get the SWA round some very tight spaces though.
Is there any particular reason it needs to be SWA?

Sould I put a corresponding MCB at the shed end in a waterproof DIN enclosure?
No, There is no point having a 20A MCB in series with another 20A MCB.
Why waterproof? If water is getting in to the shed then you should fix that before installing the electrics.

A full CU seems overkill now, but from other installs I've observed, there should at least be a switch over there?

You'll probably want a light switch for the light but other than that no.
You will need to fuse down for the light but this could be done via a fused connection unit.
 
e similar DIY in the past, qualified electricians have told me my work is perfect and have been happy to do the final CU termination and notify - but in hindsight, this was probably more luck than judgment as admittedly I had not involved them in the design. I respect the 2.5mm is controversial and not how o
Thank you for another very helpful response. Just to assure you we are saying the same thing, I was referring to the 2.5 on 20A radial which I now understand to be technically compliant but still seems to be drawing criticism from some folks here. I respect it leaves little flexibility for future. I’m starting to think just put in 4mm

Is there any particular reason it needs to be SWA?
Actually no, come to think of it. It’s clipped to a wall/fence away from any mechanical interference. Squirrels perhaps.

Would you recommend an alternative e.g NYY-J? I’m not sure hard conduit will work and the flexible stuff would be unsightly for the neighbours
 

Reply to Advice on Shed Wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
544
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
342
Hi Everyone, hoping someone will be able to help me decipher the wiring for this hoist controller. the handset it came with has stopped working...
Replies
5
Views
494
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
301
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
868

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock