Discuss AFDD EICR - unsatisfactory report landlord in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Smem18

DIY
Reaction score
22
We are new landlords and have just got an EICR done. The building is only 5 years old so I am shocked that remedial work has been noted as necessary/mandatory. Apparently AFDDs needs to be fitted as the building is over 6 story’s high (it’s a 4th floor one bed flat) due to a regulation that came in a couple of months ago? Does this sound right to you? It’s thrown a massive curve ball as we are meant to have tenants moving in tomorrow but there is no way we can get this remedied in 24 the next hours. Please tell me we aren’t being scammed into work we don’t need? I was so surprised because I asked the electrician before he left and he said everything was fine! But the report I received a few hours later says otherwise. What am I looking at cost wise to fix this? I’m heavily pregnant and so stressed by this. I did so much research into what was required for landlords but never came across this new regulation  I had a report booked to be done sooner as well but we were let down by the electrician and had to rebook elsewhere at short notice
 

Attachments

  • DB6DA592-FF5D-4E64-9548-16BCC55D45EA.jpeg
    80.4 KB · Views: 94
Last edited by a moderator:
Regulations are not retrospective, so if your installation conformed to the regulations at the time of installation then they do not need up-dating.
 
Regulations are not retrospective, so if your installation conformed to the regulations at the time of installation then they do not need up-dating.
Thank you. Things I am reading online are saying that in order to pass an EICR we would now need AFDDs. Is that not the case? If so, why has this company provided us with an unsatisfactory report
 
EICR's are made against the latest regulations, they can not comment on an installation that was done under an unknown regulation time period.
 
My understanding is you have to have an EICR done (outcome satisfactory or unsatisfactory), with 28 days allowed for remedials - so a tenant can still move in prior to the remedial work being completed (if it is even needed). However, some letting agents don't understand it that way.
 
Hi Smem18.

An EICR will compare the electrical installation to the current edition of the regulations, and will 'code' any non compliances. C1 and C2 are immediate or potential danger, C3 improvement recommended. Any C1s or C2s will need correcting for your rental property.

The current edition of the regs came into full effect at the end of September, and now mandates AFDDs for certain properties, including yours, so this had to be coded. Whether lack of AFDDs is a C2 or C3 is for the electrician to decide, it's up to their judgement. Industry guidance hasn't been updated yet for the latest edition.

In this case (s)he has decided C2, so it will need correcting, I'm afraid.
 
You have two choices - get it inspected again and discuss the AFDD situation in advance, or get them fitted. The price of a re inspection would/should be higher than getting this work done.

The good news is that it’s a Hager board and AFFD modules are available - for some this would need a completely new consumer unit.

(I’d go ahead and move tenants in myself. AFDDs haven’t been around very long and the idea that not having them suddenly makes an installation potentially dangerous is a stretch for me personally.)

It’s a fairly quick job to fit 2 or 3 modules to a consumer unit and retest those circuits. I’d imagine you are looking at a couple of hours labour plus the price of the AFDDs (roughly £120 each)
 
You have two choices - get it inspected again and discuss the AFDD situation in advance, or get them fitted. The price of a re inspection would/should be higher than getting this work done.

The good news is that it’s a Hager board and AFFD modules are available - for some this would need a completely new consumer unit.

(I’d go ahead and move tenants in myself. AFDDs haven’t been around very long and the idea that not having them suddenly makes an installation potentially dangerous is a stretch for me personally.)

It’s a fairly quick job to fit 2 or 3 modules to a consumer unit and retest those circuits. I’d imagine you are looking at a couple of hours labour plus the price of the AFDDs (roughly £120 each)
Thank you. I am inclined to just get the work done even if it costs extra, rather than trying to wheedle out or circumvent the system as it will likely only cause problems is years to come every time we need to renew the certificate. I was reading new consumer units are £2k+ and stuff so your message is reassuring. I am not an electrician so I do not know from looking at our consumer unit what the cost is likely to be?
 
EICR's are made against the latest regulations, they can not comment on an installation that was done under an unknown regulation time period.

An EICR can and should comment on installations carried out to previous versions of the regulations where items affect safety.

One of the reasons an EICR is carried out is to identify areas of an installation where changes in regulations and technology mean that safety improvements can be made.

The outcome of an EICR doesn't change based on the age of an installation.
 
GN3 say that we test against the current regs ,however BS7671 also states the regulations are not retrospective. I think guides like best practise guide 4 (still not updated) allow for the fact the places were wired in the past. We would not code no rcd on domestic lighting as a C2 ,i discussed possible future coding of BPG4 at my last NICEIC assessment ,he said afdd in HRRB would most likely be a C3 .
having said this its up to the inspector to code and im sure its good to protect your property from cheap white goods as i suspect is the job of Arc Fault Detection Device (AFDD). I wonder if SPD’s are fitted and that attracted a C2 code ?
 
There's an interesting aspect to this....... So they've picked on AFDD's as non-compliant for a HRRB, but not use of AC type RCD's in a domestic. So much inconsistency here.
 
There's an interesting aspect to this....... So they've picked on AFDD's as non-compliant for a HRRB, but not use of AC type RCD's in a domestic. So much inconsistency here.
Interesting. I suppose one of the things I am worried about is that these new regs have come out and there will be companies eager to jump straight to labelling this issue C2 and handing out expensive quotations for fixes. It’s clear reading this thread there are differences in opinion on this matter between electricians, making it very hard to navigate.
 
For what it's worth...... if this was me, I'd be giving a C3, because......

Is it imminently or potentially dangerous = No
Is it currently compliant = No
Can it / should it be corrected in the future = Yes
 
. I wonder if SPD’s are fitted and that attracted a C2 code ?
SPDs are not fitted and it has been coded C3. (Post #2)
I too would code lack of AFDDs as C3, and lack of SPDs as C3.

Edit: any new work planned as an alteration or addition to an affected circuit could not proceed unless the AFDD was installed.
So this could add weight to your decision to just go ahead and get the AFDDs fitted anyway.
 
I wonder if SPD’s are fitted and that attracted a C2 code
They are not fitted, and got a C3!
There's an interesting aspect to this....... So they've picked on AFDD's as non-compliant for a HRRB, but not use of AC type RCD's in a domestic. So much inconsistency here.
Yes, I thought that too.
It’s clear reading this thread there are differences in opinion on this matter between electricians, making it very hard to navigate.
EICR's are primarily supposed to be about assessing safety. @davesparks sums it up very well above.
Generally C2 codes are supposed to be for where if one more thing happened you would be one step away from serious injury or fatalities being likely.
AFDD's (while now mandated for some new installations) are an additional safety feature to reduce the risk of fires due to electrical faults. Not having one would not be judged potentially dangerous for most pragmatic seasoned electricians unless there were things observed in the inspection that increased risks.

One other comment - you are not obliged to use the same firm to fix this.
You can get as many quotes as you like to fit Hager AFDDs to the socket circuits, and choose one you like. All you need according to the PRS legislation is evidence that the work is done, and an invoice clipped to the original EICR would achieve that, or even some photos.

Section 5 of the ‘Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020’ states that where remedial work is required following an EICR report a private landlord must obtain written confirmation from a qualified person that the further investigative or remedial work has been carried out and that (i)the electrical safety standards are met; or (ii)further investigative or remedial work is required.
 
Having just been doing some surfing on Hager stuff, it seems that rather annoyingly their AFDD MCB's are double width, whereas their AFDD RCBO's are single. So anyone with a split board that needs modifying is totally stuffed unless you happen to have a load of spare ways and an installer with the skills and spares kit to modify it around.
 
For what it's worth...... if this was me, I'd be giving a C3, because......

Is it imminently or potentially dangerous = No
Is it currently compliant = No
Can it / should it be corrected in the future = Yes
So I have got a second opinion off 4 other electricians now and sent them the report. They all unanimously, and without hesitation, said they would grade it C3. I followed this up with a call to the NIC EIC (national inspection council for electrical installations) and they said it should catagorically be a C3 even though the building is over 18 meters.

Attached is the quote the company sent me for the works which seems very high. I asked for the cheapest way possible to bring it to regulations
 

Attachments

  • AD14E9AF-B0F1-4237-996D-E21884AC6762.jpeg
    276 KB · Views: 82
So I have got a second opinion off 4 other electricians now and sent them the report. They all unanimously, and without hesitation, said they would grade it C3. I followed this up with a call to the NIC EIC (national inspection council for electrical installations) and they said it should catagorically be a C3 even though the building is over 18 meters.

Attached is the quote the company sent me for the works which seems very high. I asked for the cheapest way possible to bring it to regulations
Utter wrip-off nonsense, in my opinion.

I'd be tempted to go back to the inspecting company and ask them to put in writing the inspector's justification for a C2 coding when after a discussion with the NICEIC you've been advised that should only be a C3.... bet you get an amended report out of it.
 
Utter wrip-off nonsense, in my opinion.

I'd be tempted to go back to the inspecting company and ask them to put in writing the inspector's justification for a C2 coding when after a discussion with the NICEIC you've been advised that should only be a C3.... bet you get an amended report out of it.

We have looked up the building regs now as well and worked out they have misquoted them slightly. They have said british standard 421.1.7...no provision of AFDDs on circuits supplying sockets and applicances. The british standard only quotes "AC final circuits supplying socket-outlets...". They have added "appliances" on, which the british standard does not mention. We therefore think their quote of 5x AFDDs is excessive and calculate we think we only need 2. I explictly asked the quotation to be the minimum to bring it up to standard so am not happy about that. I have done exactly as you suggested and quoted what NIC told us to them to see what their response is
 
We have looked up the building regs now as well and worked out they have misquoted them slightly. They have said british standard 421.1.7...no provision of AFDDs on circuits supplying sockets and applicances. The british standard only quotes "AC final circuits supplying socket-outlets...". They have added "appliances" on, which the british standard does not mention. We therefore think their quote of 5x AFDDs is excessive and calculate we think we only need 2. I explictly asked the quotation to be the minimum to bring it up to standard so am not happy about that. I have done exactly as you suggested and quoted what NIC told us to them to see what their response is

Hello everyone, in case this helps anyone else: we have had the original certificate overturned and now have been issued a satisfactory certificate within an hour of calling them and sending an email to follow-up the call. We quoted what the NIC EIC about the issue being catagorically a C3 not a C2 issue, I called them up on the fact they have misquoted the British Standard to include appliances when it is sockets only and quoted us for 5x AFDD's when only 2x are required to bring it up to standard (I had specifically asked for them to quote me the minimum required to bring it to safe standard and they ignored that), I expressed deep disappointment the electrician told me everything was fine and passed in-person but then I received an unsatisfactory report late at night - so I had no chance to quiz him or ask questions, and finally I explained we had got a second opinion off 4 other electricians who all unanimously told us it should be a C3 rating.

Ultimately this company has missed out on some busines from us as we plan to get the advisories done (on just the sockets that actually require them as per the BS 421.1.7!) so that we are up to speed, everything is safe, and don't have the issue in the future. But we will do this by getting competing quotations and without the artificial 28 day deadline pressure and panic (else potential £30k fine) they put us under. If they had just been transparent and spoken to me about the various options we probably would have booked them there and then to do it, but instead sent the most expensive possible solution in an email despite my requests otherwise.
 
We have looked up the building regs now as well and worked out they have misquoted them slightly. They have said british standard 421.1.7...no provision of AFDDs on circuits supplying sockets and applicances. The british standard only quotes "AC final circuits supplying socket-outlets...". They have added "appliances" on, which the british standard does not mention. We therefore think their quote of 5x AFDDs is excessive and calculate we think we only need 2. I explictly asked the quotation to be the minimum to bring it up to standard so am not happy about that. I have done exactly as you suggested and quoted what NIC told us to them to see what their response is
I was just to about mention this "addition" of appliances to the wording of 421.1.7
This is misleading at best, fraudulent at worst.
 
I would however point out that there are 3 circuits that feed sockets, not 2. The fridge and freezer circuit and 2 sockets circuits.
Unless the fridge and freezer are hard wired.
 
I was just to about mention this "addition" of appliances to the wording of 421.1.7
This is misleading at best, fraudulent at worst.
Yes I am of the belief this company just has a blanket policy to do this to landlords in high rise buildings and send them the most expensive solution possible, as I explicitly asked them for (sorry) cheapest way to bring it to standard and even quoted some of the nice people in this forums suggestions and asked "please explore all avenues for a solution and come back to me with the most cost effective" and they simply just sent me the quotation for everything, even the C3 issue.

The survey was quite cheap so lesson learned. I had a lovely guy saved in my phone who came highly recommended on check a trade, but he wasn't available the day I needed to I panicked as needed to get it done and booked this big company who didn't have many reviews ("national surveyors"). The local electrician in my phone was £150 for the report and national surveyors was £89. I always like to go with local recommended tradespeople who you can actually have a conversation with and will take care of you start to finish and this is why (I am renovating a house elesewhere and all contractors have been local and its been great)
 
Attached is the quote the company sent me for the works which seems very high. I asked for the cheapest way possible to bring it to regulations

Quite unprofessional to quote for the fitting of Wylex protective devices in a Hager board. Either they're lax with paperwork or would have introduced an additional non-compliance to be picked up on subsequent EICRs.
 
Quite unprofessional to quote for the fitting of Wylex protective devices in a Hager board. Either they're lax with paperwork or would have introduced an additional non-compliance to be picked up on subsequent EICRs.
That was my first reaction. Then I spotted "new consumer unit" so wondered if they were intending to change the lot.
It's sad that people earn a living by misleading people, ripping people off, and mis-using legislation intended to simply ensure things are safe for tenants.
Equally, great the OP fought back and got this sorted. A nice change for one of these threads to end up with a good result.
 
Having just been doing some surfing on Hager stuff, it seems that rather annoyingly their AFDD MCB's are double width, whereas their AFDD RCBO's are single. So anyone with a split board that needs modifying is totally stuffed unless you happen to have a load of spare ways and an installer with the skills and spares kit to modify it around.
They have bought out single module AFDDs now:

 
They have bought out single module AFDDs now:

Its a dual RCD board, so putting in the AFDD/RCBO modules would really need another busbar segment so they are not off one of the RCDs.

Hager do an AFDD add-on for MCB, etc, that make double width if you needed arc-detection without residual current. I can't see many cases where that would be likely!
 
Its a dual RCD board, so putting in the AFDD/RCBO modules would really need another busbar segment so they are not off one of the RCDs.
Personally, I would fit them on the RCD anyway, unless the customer particularly wanted them off it (and was happy to pay for it). Not ideal, but 2 RCDs in series, both in the same location, not a problem IMO
 
Personally, I would fit them on the RCD anyway, unless the customer particularly wanted them off it (and was happy to pay for it). Not ideal, but 2 RCDs in series, both in the same location, not a problem IMO
Agreed, it is not dangerous, just not great "design" as you still have the risk of accumulated leakage tripping the RCD in spite of having coughed £120 or so per AFDD.

I don't know the Hager commercial boards well so don't know if you could just get a new section of busbar and extend the main switch L for the AFDD. As single-module they should fit after removing the MCBs, just the practicality of shuffling along and having the non-RCD bus to feed them.
 
Hijack; is there a test methodology for AFDD's now, or just its self test? Just curious.
I think the closest you will get are the Hager AFDD's that have bluetooth connectivity and using their app it is possible to download diagnostic information from the device and also the AFDD can also be updated to cope with newer appliances being connected or mains born noise
 
Fridge and freezer are hard wired
Are the fridge and freezer hard wired .some set ups have a switch above the counter that operates a socket behind the fridge or in an adjacent cupboard. Just to add I thought one of the reason for AFDDs was to detect faults in such appliances such as fridges and freezers. So by hard wiring them it they no longer require the AFDDs . As far as I see it a fridge hard wired in could have the same fault as one plugged in. Just saying
 
Every report you read on the US forums say the AFDD's are a real problem area and are eventually removed, don't know enough about them to comment personally, but they do seem to be a solution looking for a problem.
 

Reply to AFDD EICR - unsatisfactory report landlord in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
I am a landlord and my managing estate agent just recently organised an electrician to carry out EICR. Came back as unsatisfactory, no RCD...
Replies
27
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock