TL.DR version. AFDDs are a crap solution to a problem we don't have, use an RFC and forget about them.

In more detail..

From IEC62606-2103
"Residual Current Devices (RCDs) are recognised as efficient to reduce the risk of fire by detection of leakage current and arcing to ground as a consequence of tracking currents within an electrical installation. However, RCDs as fuses or circuit-breakers are not able to reduce the risk of electrical fire due to series or parallel arcing between live conductors.

During a series arc fault, there is no leakage to ground therefore RCDs cannot detect such a fault. Moreover, the impedance of the series arc fault reduces the load current, which will keep the current below the tripping threshold of the circuit-breaker and the fuse. In the case of a parallel arc between phase and neutral conductor, the current is only limited by the impedance of the installation. In the worst cases of sporadic arcs, the conventional circuit breakers were not designed for that purpose.
"

And the test procedure from IEC62606-2013..

"The insulation across both wires is to be slit 50 mm (or 2 inches) from one end to a depth to expose the conductors without severing any strands.
d) The slit in the insulation is to be wrapped with a double layer of electrical grade black PVC tape and overwrapped with a double layer of fiberglass tape.
e) The conductors are to be stripped at the end farthest from the slit approximately 12 mm (or 0,5 in) for connection to the test circuits. The cable specimen shall be then conditioned to create a carbonized conductive path across insulation between the two cable conductors:
f) The cable specimen is to be connected to a circuit providing 30 mA short circuit current and an open circuit voltage of at least 7 kV. The circuit is to be energized for approximately 10 s or until the smoking stops.
g) The cable specimen is to be connected to a circuit providing 300 mA short circuit at a voltage of at least 2 kV or sufficient to cause the current to flow. The circuit is to be energized for approximately one minute or until the smoking stops."


AFDDs are an attempt to reduce fires in timber buildings using relatively high-current radials, in North America where poor termination and/or breaks in conductors start fires. In the UK RFC's are inherently tolerant of single faults, a feature that makes them incompatible with AFDDs. Given the choice between an RFC and an AFDD it has to be the RFC, it's a cheaper and much more reliable way to reduce the risk of fire from a broken conductor.


You do know IEC62606 is a carbon copy of UL1699?

UL is in the IEC and so Eaton, I will find you the link.

The over voltage theory came about because they could not get in wall romex to arc unless it was carbonized by applying 8-15kv across it. Supposedly in the real world this would come from lightning strikes and multi kv surges jumping the gap in damaged insulation from over driven staples. This would eventually carbonize the path where 120 volts could arc across in high current and ignite the wood.

Here is that theory in depth:






Only two problems:

1) multi kv voltage spikes happening monthly would destroy any AFCI breaker and the home owners would notice when their electronics and MOVs become toasted regularly.

2) Never was pyrophoric carbonization ever considered or investigated as being a possible cause behind smoldering studs. Arcing was assumed immediately despite lab testing saying its not likely given just how many surges romex would have to take.


50601
 
Well looking at Cookie's avatar, he is an AMERICAN one of the World's Police Force, the special relationship and all that goes with it,

Had I known, I would have used an anonymous proxy. But that could get me banned. I've long learned international forums have a bit of an interest with what country a person resides in.

With that said I not only do not support what the US does, I DESPISE it.


But it should not matter in this conversation. Its not about politics but AFDDs. And if anything the fact they come from a country that is renowned for profit over all else should speak for itself.
 
And I'm assuming he's male. But now we all know, he's just an internet warrior.

If you want BS7671 to balloon to 3,500 pages and make any job cost so much muppets take over your respectable job turning the UK into a 3rd wold country of shocking knobs and hobs... great for you. But I don't think everyone would want that. Certainly not me.
 
A Troll, may be?????? only asking not accusing


And what would a background do? If I worked for a massive multi national company or code making body do you seriously believe I would hold these views? Posting them for all to see? They don't look for people who see the truth, they look for useful idiots and those who can progress the companies set goals both written and unwritten to which there are many btw.
 
I still don't see why you won't share your background. It's the first time I've ever seen this on a forum. You still haven't given a proper reason as far as I can see.
 
I still don't see why you won't share your background. It's the first time I've ever seen this on a forum. You still haven't given a proper reason as far as I can see.


Clearly you've never been on a US forum, because AFCI angst literally goes on for 5 dozen pages. Search AFCIs on Mike Holt's forum as an example.
 
Clearly you've never been on a US forum, because AFCI angst literally goes on for 5 dozen pages. Search "Mike Holt AFCIs"

You're just avoiding the issue again.

I never mentioned how long threads go for.
 
Go and a US forum and you will see plenty of not sharing credentials and people hold AFDD opinions far more extreme then mine.
Hi - opinions are like ears, everyone’s got one or two. It’s just human nature to have more respect for statements if there is some background knowledge of the person making them. If you don’t feel you can share, that’s fine :) .
I’m a big believer in proper design, installation and testing. I might be wrong, but I think this would remove the need for an AFDD, at least in UK (?).
 
Hi - opinions are like ears, everyone’s got one or two. It’s just human nature to have more respect for statements if there is some background knowledge of the person making them. If you don’t feel you can share, that’s fine :) .
I’m a big believer in proper design, installation and testing. I might be wrong, but I think this would remove the need for an AFDD, at least in UK (?).


But some opinions are based on fact others are based on fiction. I don't understand how my links (openly saying your breakers detect arcing) is not supporting evidence in of itself. I don't care who the messenger is, but rather what is he trying to say and what evidence he has.
 
But some opinions are based on fact others are based on fiction. I don't understand how my links (openly saying your breakers detect arcing) is not supporting evidence in of itself. I don't care who the messenger is, but rather what is he trying to say and what evidence he has.
Hi - yes, I agree, don’t shoot the messenger :) .
I am sorry to say that I’ve not looked at your links yet.
 
I'm a Yank spark, the reason I (and Cookie) are here is because we've been witness to an entire history of fraud in the US that is now spreading itself globally.

If you'd like more specifics, we can easily bore you for pages.

But the thing is, we are here because we need your help

Pursuant to this, you folks have a history of RCD's , Earth loop resistance , as well as other relevant theory.

Something that is far less a consideration in the states

This is a big reason why we've been duped

~S~
 
Hi - yes, I agree, don’t shoot the messenger :) .
I am sorry to say that I’ve not looked at your links yet.


The links are key. They say what I've been saying in black and white. I can post plenty more but I think there is enough to digest right now.

And Sisyphus is right, AFCIs are a nightmare in the US one that I hope does not spread past our boarders.
 
Electricians are above all practical people with a good understanding of theory, certainly in the UK. There has been much theory and academic referencing on AFDDs.

I suggest to Cookie and Sisyphus they now illustrate their criticisms of AFDDs by some examples - case studies - in the domestic, commercial, industrial settings - explaining why they did/did not perform correctly, and what sort of electrical events cause them to trip erroneously? Are there any 'fixes' for when they trip erroneously? How often does nuisance tripping occur? What could be done to improve the detection and threshold rules to reduce nuisance tripping?
 
Having perused this thread, linking out to some of the content to view or read I have found some valid points but also some biased almost on the conspiracy level hype to boot.

The introduction of AFDD's to the UK and the regulations that surround them make there implementation very much different to that of the US, it is very easy to demonstrate that an RCD can stop certain types of arc fault and make it look like a conclusive argument but as other have mentioned this totally ignores parallel and series faults which would not be detected by mcb's and or rcd's. This alone for me shows an advantage to using AFDD's in certain situations where the environment is such that an arc fault has a heightened risk of causing a fire, in fact the implementation of AFDD's into the BS7671 shows this by specifying these exact situations in the implementation guidelines.
I would argue the point that if this was all just a pointless exercise to make big bucks for certain groups where there were no actually net safety advantage then our regulations would have pushed them onto our market in a very different way.

AFDD's now are very different to those found decades ago, electronic monitoring of arc fault type means a significantly reduced occurrence of nuisance tripping which were the the bane of past generations, remembering here that arcs are naturally part of many electrical household device like vacuum motors so the device needs to distinguish between a natural arc and a fault arc.

I do find the links provided by our American member Cookie are weighted to expose specific and relevant points that support his own beliefs/concerns here but many relevant points that have been raised have not been addressed that counters that view in these links, I also get very skeptical when youtube videos of poorly demonstrated, set-up and measured experiments are part of the defense of position here.

Like I said and has been expressed earlier on, AFDD's cannot be replaced by the use of and RCD and MCB, yes!.. in certain demonstrated scenario's we would expect an rcd to function and negate the need for a AFDD but it is the other types of arc fault that only an AFDD would detect that make them a relevant introduction into the regulations, what should be the argument or discussion here is if the introduction of AFDD's will have an overall positive effect of reducing property damage and subsequently reducing injury and fatality caused by fires derived from an arc fault. Personally I think we already have installation practices and regulations that minimise this in domestic and it is only when we see poor workmanship and/or ignorance to the BS7671 that we have these situations, we already have a legal system that can act on such times, however when we creep into commercial and industrial I do see a genuine benefit in certain scenarios.

It will probably be a decade before we actually know whether they have been effective but I am not convinced on the counter argument and the header of this thread that AFDD's are a massive fraud .. this is a grossly sweeping statement and what I expect of hardcore conspiracy theorists, even making some relevant points and quite good discussion points does not justify the title of this thread, I would also be interested if we can get a response to the very relevant points raised that counter that claim and make AFDD's a viable solution to reduce property fires.

I don't think our American member is out to deliberately mislead us in anyway but I expect the use and implementation of AFDD in the US market is very different to that of how they are been introduced over here, I belief this has given a very skewered and skeptical view of the need for them when it comes to other countries, that and a limited knowledge of our regulations may be a large part of making such a sweeping bold claim that simply imho has not been shown or demonstrated.
 
Last edited:
We have no reason to purposely mislead you Darkwood.

What we do understand is , coropratism has drowned out the nay sayers here , you folks have a better grasp on the theory the we do, and perhaps your system allows for scrutiney

I'll try and hit on points asked....

First, know that AFDD's debuted in the late 90's here, and were mandated for a decade before they were confronted and upgraded to 'combination' AFDD's . What is meant by this is series/parallel mitigation.....7 manufacturers should have had callbacks ,or worse..... because that is what they marketed on originally.

This was a UL/CSPC/NEMA collaborative

I know of 3 class action suits stifled before they ever met the courtroom door, one being retore CSA.

They simply wrote the old version into code usage instead

To this day, they do not mitigate series arcs.

~S~
 
As to stats, we do know of one Chicago spark /firefighter who took the time to reveal them on NEC forums

The thing is , we are 50 odd fiefdoms in the consideration of electrical bureaucracy's adoption ,licensure ,inspection ,as well as the collection of fire forensics , a rather broad contingent of variables....

Anecdotally, having served on a FF brigade ,as well as being their token spark , revealed the validity of unfunded forensics juxtaposed to manufacturers claims as the perfect vehicle for the old statistics adage

~S~
 
Further.... UL1699, it seems to have holes one could launch a cow through in terms of variables.

To my understanding (which can be confronted) the chief operational component to all 'enhanced OCPD protection' is the time honored toroidal coil , needing all conductors to 'sense' irregardless of all electronica lumped onto it.

And so we've one manufacturer of AFDD's that not only differs, it does so blatantly and overtly marketing themselves as such


>>>>>

http://apps.geindustrial.com/publibrary/checkout/DEA-635?TNR=Brochures|DEA-635|PDF&filename=DEA-635.PDF

GE’s AFCI enables shared neutrals. Ordinarily you would not be able to have just one neutral coming back to the circuit breaker for the AFCI to function properly. GE’s AFCI has the ability to ignore the neutral. You can wire a multi-wire circuit or a shared neutral the same way you would wire a thermal magnetic breaker.

The above ^^^ has caused quite the ado among the US contingent of sparks

Yet here is a prime example of fundamental theory , something we hope you folks have a more definitive grasp of, as well as voice in

~S~
 
Electricians are above all practical people with a good understanding of theory, certainly in the UK. There has been much theory and academic referencing on AFDDs.

I suggest to Cookie and Sisyphus they now illustrate their criticisms of AFDDs by some examples - case studies - in the domestic, commercial, industrial settings - explaining why they did/did not perform correctly, and what sort of electrical events cause them to trip erroneously? Are there any 'fixes' for when they trip erroneously? How often does nuisance tripping occur? What could be done to improve the detection and threshold rules to reduce nuisance tripping?


And how do we go about creating these case studies? We don't have access to hundreds of thousands, research labs, their accreditation or trust. However just about any electrician in the field can tell you in great detail how they trip LED lights, treadmills, computer power supplies, garage door openers, vacuum cleaner, routers, TVs, stereos, refrigerators, microwaves, space heaters and a host of other devices. Along with how to mitigate tripping everywhere from dedicated circuits to strings of interference filters to extension cords to literally placing all AFCIs on one leg:




50621



What could be done to improve the detection and threshold rules to reduce nuisance tripping?


Why Improve what is a bad idea to begin with? Why try to find a measles cure when vaccines prevent the illness in the first place?

Its not about threshold (magnitude) but discrimination. Just about everything has a waveform, often indistinguishable from a dangerous arc. I think that is what is hard to grasp for many folks. You need levels of computing power and research simply not going to be found at $35 a pop.
 
I am not too au fait with how this has all transpired across the pond and on that point I can conclude there is possibly a lot of truth to what you both have said, the point I was trying to make is you seem to be projecting the issues experienced in America onto other very different economical and regulated systems like the UK and thus my comment on the thread title.
I have no doubt at all that big corporates lobby for favourable outcomes that financially benefits themselves and stifles competition and blocks government policy change, that happens everywhere (your own NRA as a classic example).
US regulations and practices for installation protection is very different from ours, AFDD's are been introduced to protect systems of higher risk from such faults where there tends to be a ready source of flammable material near and around electrical equipment i.e. joinery shops, chemical industry etc etc, this hasn't suddenly been thrust on us, it has been implemented after decades of investigations into the most common causes of fire in properties, our system is more transparent than it seems the US is, we can use freedom of information act to get information, studies, polls etc that are used in the lead up to regulatory changes and we do have a period to challenge them, the bodies that implement these changes do give notice years in advance which allows for challenges to be implemented if deemed necessary so I dare say our system is more transparent.
Is the UK system better?.. possible but it is far from perfect, we have our own crosses to bear and our forums are filled with very different repeated content which stems from certain industry bodies pushing regulatory requirements and also the failure to regulate other bodies that has all had an impact on our trade and the regulations that have subsequently been brought in but that's a whole different thread.
 
Last edited:
Having perused this thread, linking out to some of the content to view or read I have found some valid points but also some biased almost on the conspiracy level hype to boot.

The introduction of AFDD's to the UK and the regulations that surround them make there implementation very much different to that of the US, it is very easy to demonstrate that an RCD can stop certain types of arc fault and make it look like a conclusive argument but as other have mentioned this totally ignores parallel and series faults which would not be detected by mcb's and or rcd's.

You haven't read the links. They specifically say MCBs and RCDs mitigate parallel arcing. Specifically. Saying they don't is a giveaway you haven't understood what I have been saying all along.


Series faults- AFDDs do not detect them under under a few amps.

Further series faults can be detected by other means like heat detection.

Saying AFDDs must be used for series events is code governing technology which violates the basic principles and structure of the code.



This alone for me shows an advantage to using AFDD's in certain situations where the environment is such that an arc fault has a heightened risk of causing a fire, in fact the implementation of AFDD's into the BS7671 shows this by specifying these exact situations in the implementation guidelines.
I would argue the point that if this was all just a pointless exercise to make big bucks for certain groups where there were no actually net safety advantage then our regulations would have pushed them onto our market in a very different way.

All you have to do is get the regs to think they do something good.


AFDD's now are very different to those found decades ago, electronic monitoring of arc fault type means a significantly reduced occurrence of nuisance tripping which were the the bane of past generations, remembering here that arcs are naturally part of many electrical household device like vacuum motors so the device needs to distinguish between a natural arc and a fault arc.

Then why are trips still happening over here in the US?

I do find the links provided by our American member Cookie are weighted to expose specific and relevant points that support his own beliefs/concerns here but many relevant points that have been raised have not been addressed that counters that view in these links, I also get very skeptical when youtube videos of poorly demonstrated, set-up and measured experiments are part of the defense of position here.


The UL and Franklin links stand by themselves without the questionable you tube vids.

UL and Franklin which openly say MCBs prevent arcing.

UL and Franklin which are the official starting place of AFCIs.

Both of whom were taken very seriously by the industry and NFPA.

Despite Franklins untrolled experiments of lighting cardboard and blankets that had I done the same I would be been a laughing stock.



Like I said and has been expressed earlier on, AFDD's cannot be replaced by the use of and RCD and MCB, yes!.. in certain demonstrated scenario's we would expect an rcd to function and negate the need for a AFDD but it is the other types of arc fault that only an AFDD would detect that make them a relevant introduction into the regulations, what should be the argument or discussion here is if the introduction of AFDD's will have an overall positive effect of reducing property damage and subsequently reducing injury and fatality caused by fires derived from an arc fault. Personally I think we already have installation practices and regulations that minimise this in domestic and it is only when we see poor workmanship and/or ignorance to the BS7671 that we have these situations, we already have a legal system that can act on such times, however when we creep into commercial and industrial I do see a genuine benefit in certain scenarios.

It will probably be a decade before we actually know whether they have been effective but I am not convinced on the counter argument and the header of this thread that AFDD's are a massive fraud .. this is a grossly sweeping statement and what I expect of hardcore conspiracy theorists, even making some relevant points and quite good discussion points does not justify the title of this thread, I would also be interested if we can get a response to the very relevant points raised that counter that claim and make AFDD's a viable solution to reduce property fires.

What I think this boils down to is your inability to believe that humans make mistakes. That money motivates. That humans lie. That is the limiting factor in all this. Not the counter evidence or their claims.

Forget what bullies have done hiding behind conspiracy theories. I am not one of them.

On the other hand I and countless others in the states know the history and the fall out.



and a limited knowledge of our regulations may be a large part of making such a sweeping bold claim that simply imho has not been shown or demonstrated.


You do know UL extensively researched the UK system with great tenacity? The EU system? Doing loop impedance calcs for your and our systems more in depth then anyone has ever under taken here (ie not just tables but measuring the actual complex admittance, susceptance, conductance and elastance in a computer model). Building computer models of various homes and flats. Building actual US and UK power systems based on actual buildings? Testing European MCBs, RCDs and plugs, cords, twin and earth, ect in numbers. Subjecting hundreds of model circuits to short circuits, overloads, HV, thermal imaging, accelerated aging, oscilliography, ect, ect.

You do know that 15 plus years of obsessive research and emulation of the UK power system lead to the creation of AFCIs?

To say that any of this is based on limited knowledge of UK regs is very wrong. Because UL can tell you exactly how accurate or inaccurate your tables are 8 decimal places out.
 

Attachments

  • 1563279435984.png
    833.7 KB · Views: 7
I am not too au fait with how this has all transpired across the pond and on that point I can conclude there is possibly a lot of truth to what you both have said, the point I was trying to make is you seem to be projecting the issues experienced in America onto other very different economical and regulated systems like the UK and thus my comment on the thread title.
I have no doubt at all that big corporates lobby for favourable outcomes that financially benefits themselves and stifles competition and blocks government policy change, that happens everywhere (your own NRA as a classic example).
US regulations and practices for installation protection is very different from ours, AFDD's are been introduced to protect systems of higher risk from such faults where there tends to be a ready source of flammable material near and around electrical equipment i.e. joinery shops, chemical industry etc etc, this hasn't suddenly been thrust on us, it has been implemented after decades of investigations into the most common causes of fire in properties, our system is more transparent than it seems the US is, we can use freedom of information act to get information, studies, polls etc that are used in the lead up to regulatory changes and we do have a period to challenge them, the bodies that implement these changes do give notice years in advance which allows for challenges to be implemented if deemed necessary so I dare say our system is more transparent.
Is the UK system better?.. possible but it is far from perfect, we have our own crosses to bear and our forums are filled with very different repeated content which stems from certain industry bodies pushing regulatory requirements and also the failure to regulate other bodies that has all had an impact on our trade and the regulations that have subsequently been brought in but that's a whole different thread.


Your not aware of what happened here, but we are. Including wanting to replicate the UK system. And 12 years ago I would not only be saying the same but the efforts to make these global which is happening right now.
 
On balance I do believe that there is credibility in what Cookie is saying. And I respect his right to anonymity. From what he says AFDD is not the l
What I think this boils down to is your inability to believe that humans make mistakes. That money motivates. That humans lie. That is the limiting factor in all this. Not the counter evidence or their claims.

I don't think that's true. Anyway I haven't time to debate it now, as I'm trying to sell my 6 month old diesel car and the best offer I've had is a fiver.
 
On balance I do believe that there is credibility in what Cookie is saying. And I respect his right to anonymity. From what he says AFDD is not the l


I don't think that's true. Anyway I haven't time to debate it now, as I'm trying to sell my 6 month old diesel car and the best offer I've had is a fiver.


But why do you assume that?

At least 1/3 of the panel members in the NFPA CMPs are affiliated with manufacturers.
 
UL and Franklin which openly say MCBs prevent arcing.
Now that is a classic! To which I will reply...NO they don't. That is most definitely a false statement. Why do I say that? My experience has showed me again and again having seen the results of arcing on neutrals mostly, that cable and boxes have melted down including MCBs' due to arcing and the MCB just stood and watched. So who will I beleive? You or my lying eyes? As to overcurrent despite all the theory and guff etc. about OCPD and its thermal ability to shut off the supply again not necessarily. On a ring final circuit (32a) someone thought to pop a 10Kw dishwasher. Rather than the MCB operating it preferred to completely melt down without switching off. Bear in mind as to BS7671 when I started out as a trainee it was common to find the neutral fused as well as the line. This was sanctioned by earlier regs. This showed me that they do not know or think about all the things they should! Since then I always have a weather eye as to, does this actually make sense in the real world. Bottom line here, what is the fraud? What is it you actually want help with? Why do you think the AFCI is such a problem with tripping? We here have conjectured that AFDDs' would be tripping out when a fridge compressor switches in or a light switch is switched on it is very much a case of Quod Ed Demonstrandum.
You haven't read the links. They specifically say MCBs and RCDs mitigate parallel arcing. Specifically. Saying they don't is a giveaway you haven't understood what I have been saying all along.


But that is exactly what he did say! But look above they do NOT always by any means at all in real life whatever your links say because personally I have witnessed (and I dare say many others on here) MCBs' complete (sometimes) inability to react as theory says they should.
 
Let's say we have a L-N arc fault, RCD's will not detect such a fault as is the nature of there operation in detecting residual leakage to earth and thus an imbalance in current flow in the live wires.
MCB or RCBO and fuses will only operate if the arc fault meets their operating criteria found in their time/current curve so as to operate/trigger the device, it has however been shown that impedances measured in arc faults at our national voltage ratings are shown to diminish current flow in parallel faults thus increasing the likelihood of the device failing to detect the fault.

@Cookie - The youtube vid' posted demonstrating a arc fault and subsequent temperature values was to say the least a laughable video, the conditions were not controlled, the temperature measurement method was flawed and questionable and thus any data gathered was irrelevant, the fact you post stuff like this because it fits your position without scrutinising it and seeing the obvious flaws demonstrates you may have a form of cognitive dissonance in that you are happy to accept anything that supports your mindset with little to no scrutiny yet play the opposite game of auto dismissing any points raised that do not shore up your argument.

I do not know why you wrote the section about the UL as I am very aware of them but you have to accept that other national bodies and standards exist around the world and to assume that the UL standards somehow trump (pardon the pun) all the others is a disillusioned view to take, even when taking into account the history and size of this body, like you have found, it isn't always a good thing. I am also well aware the UL would love to become the worlds recognised safety symbol as would any of the main bodies like CE, regarding the UL achieving this then that can only be good for US business and trade given they would thus have leverage to manipulate world trade from within the standards they must conform to, what you will find though is the rest of the world is not so easy to just hand over this influential power so your claim that we are just going through the same motions that the US did 15/20 yrs ago are simply your unfounded opinion. We have our own trading and safety standards which also go through similar lab testing, computer analysis etc etc

The UK regulations are not governed by UL standards, in part there may be sections are areas that are lifted and repeated but there exists no direct influence hence the implementation of AFDD's in the UK BS 7671 is very different in approach and effect than that of your electrical standards.

Please remember you are the one coming onto a UK based forum telling us AFDD introduction into the BS7671 is fraudulent, this is based on your own experiences in the US, at no point have you posted anything that demonstrates this nor have you provided any irrefutable evidence, regardless of whether of not the UL has done intensive research and modelling into our own grid networks and installations is not in itself proof, it just demonstrates a research facility trying to ensure products made under UL standards could possible be meet the requirements of other nations following different codes... I totally fail to see how this is any kind of rebut to what I have said.

I ask you some simple questions with what I consider to be the correct answers ..firstly forget all that has occurred in the US and all the controversy you suggest AFDD's are having in the US and just think about my questions...


Do the AFDD provide a level of protection that is ill afforded by other devices or variations of devices ?...YES.
Would this protect property and subsequently save lives?.. YES.

Is the overall cost and implementation of using the devices warranted by the fires expected to be avoided?... remains to be seen but in Europe the biggest cause of property fires are electrically related, a device that can reduce this and has been demonstrated to should be worth reviewing.

Are there any other practical alternatives that afford the same level of detection of arc faults and protection from them?... NO

I noted you mentioned heat sensors/detection so I am all ears here on how you expect to monitor every part of an electrical installation including the integrals of faulting appliances with heat detection as an alternative and at what cost ... by the time your average heat detector has gone into alarm you already have a substantial problem, even smoke detectors are too slow in comparison to avoiding the fire altogether.
 
Last edited:
Forget what bullies have done hiding behind conspiracy theories. I am not one of them.

On the other hand I and countless others in the states know the history and the fall out.
The above statements are a mystery as to what you are talking about they make no sense and in no way clarify your actual point, which is??????? Forget what bullies have done??? I was nowhere near thinking anything like that I was just trying to get my head around what you are banging on about. You are saying we don't need AFDD, and you and myriad others find them a problem as they keep tripping So? Where is this going? You are saying just use an RCD without any conclusive evidence that it is fine and safe and what will I do in court say you told me so and here are a couple of studies. I need a lot more than that my friend. And believe me if I was convinced of your propositions I would actually take effective action.
 
Because its not about credentials. Its about the facts I've posted.
Ultimately you are spot on. The facts, if they are facts, are in no way diminished by method of delivery.

Trying to put someone on the spot to revel details about themselves is unnecessary, in my humblest of opinions.

I'm hoping some of the technical heavyweights turn up to add a little meat to this thread.
 
.....Where is this going? You are saying just use an RCD without any conclusive evidence that it is fine and safe and what will I do in court.....
" well milud, them went and changed the electrickery din't they, RCDs were perfectly safe in 2017 but 2018's electrickery is different you see so nows we needs they AFDDs so we is all safe from the new electrickery, i thinks" :mad::mad:
 
I'll double that if of any help?:cool:

Note to our American friends.

The above is an example of irony.

I know he's not really going to double the offer. Because he knows I'm not really trying to sell a diesel. We all know that we were conned (well some of us) by the government to switch to diesel engines. Which came about because idiots in government were conned by dubious science and corrupt manufactures. I don't really not believe your statements, but say I do to make myself look stupid which, hopefully, people don't believe. Its called irony, it's very subtle and something that Brits spot intuitively.

As for your campaign, good luck with that. We, on the hand, tend to shrug our shoulders, move on, and think ourselves lucky that we live in a country that allows us to say what I have.

I will not tell you again.
 
Now that is a classic! To which I will reply...NO they don't. That is most definitely a false statement. Why do I say that? My experience has showed me again and again having seen the results of arcing on neutrals mostly, that cable and boxes have melted down including MCBs' due to arcing and the MCB just stood and watched.

That to me sounds like a series arc fault, or more likely joule heating.

Franklin and UL allued to L-N and L-G.


So who will I beleive? You or my lying eyes? As to overcurrent despite all the theory and guff etc. about OCPD and its thermal ability to shut off the supply again not necessarily. On a ring final circuit (32a) someone thought to pop a 10Kw dishwasher. Rather than the MCB operating it preferred to completely melt down without switching off. Bear in mind as to BS7671 when I started out as a trainee it was common to find the neutral fused as well as the line. This was sanctioned by earlier regs. This showed me that they do not know or think about all the things they should! Since then I always have a weather eye as to, does this actually make sense in the real world. Bottom line here, what is the fraud? What is it you actually want help with? Why do you think the AFCI is such a problem with tripping? We here have conjectured that AFDDs' would be tripping out when a fridge compressor switches in or a light switch is switched on it is very much a case of Quod Ed Demonstrandum.


Sounds like a failed MCB. Or a loose connection at the MCB (series deal).

Fused neutrals? We had those those too 100 years ago and electricians still find them on rare occasions in century old homes. Half the time its a 2 wire 120 volt only service.


50629


50628



50630



But that is exactly what he did say! But look above they do NOT always by any means at all in real life whatever your links say because personally I have witnessed (and I dare say many others on here) MCBs' complete (sometimes) inability to react as theory says they should.

Failures, joule heating and old designs are not parellel arcing.
 
The above statements are a mystery as to what you are talking about they make no sense and in no way clarify your actual point, which is??????? Forget what bullies have done???

My point is I'm not a conspiracy theorist nor is my knowledge of AFDDs conjecture.

In the US (and I assume else where) "truthers" have given conspiracy theorists a bad reputation.

Case in point: mass shooting happens somewhere in the US. Nut bags claiming to know the "truth" come out of the wood work proclaiming no on died and its all crisis actors. Media somehow paid off by the government. They will call the family members of the victims and harass them to no end... I despise these people to end.

But sadly they've done the damage. In the states anyone thought to believe in conspiracies is now viewed as one of these bullies, or dumb enough to have taken their word.




I was nowhere near thinking anything like that I was just trying to get my head around what you are banging on about. You are saying we don't need AFDD, and you and myriad others find them a problem as they keep tripping So? Where is this going? You are saying just use an RCD without any conclusive evidence that it is fine and safe and what will I do in court say you told me so and here are a couple of studies. I need a lot more than that my friend. And believe me if I was convinced of your propositions I would actually take effective action.

The code should not mandate AFDDs. You don't need them.


Your breakers and RCDs detect parallel arcing already.

Series events can be mitigated through several other technologies. Code should not mandate technology. Otherwise its not impartial and in of itself shows bias.
 
So there you shifted from the statement

If you mean that in my original post I was referring only to parallel arcing (L-N; L-G) then I guess you could say that.

But- my statement still stands. Your system is already beginning to take care of series arcs:

Thermarestor® - (Thermal Monitoring) - https://thermarestor.co.uk/




to "openly prevent parallel arcing" consistency man consistency!

As in will not keep an arc going longer then a few cycles.

Skepticism results in me using simple words, simple concepts and blanket statements so people can "get it"
 
So there you shifted from the statement

to "openly prevent parallel arcing" consistency man consistency!


And not to muddy the waters but I feel the need to mention this now before someone asks latter:

UL has a very broad range (blanket) of what they call arcing. Traditionally arcing has revolved around Paschen's Law. However, because continuous arcing is impossible to sustain at 120 volt unless heavy carbonization is present UL had to come up with their own definition of 'a luminous discharge between electrodes...' meaning that even a sputtering short circuit fits their definition of arcing.

They needed to do this because arcing is not a concern at 120 volts the way it is at 230 volts.

However- short circuit or an actual arc- UL testing has shown that MCBs and RCDs can mitigate all parallel events.

................................................


In other words they knew actual arcing is possible at 230 volts nominal.

They and the CMPs for years knew arcing is possible at higher voltages hence why for decades prior 277/480 volt services of 1000amps or greater required and still require a GFP main breaker.

UL knew arcing at 120 volts is typically not possible.

So UL changed the definition (twisted the definition) to say arcing can take place at 120 volts.

And came up with the over driven carbonized path staple theory as a backup should the definition be called out.

UL proves the European system detects arcing at all voltages. UL then says this system needs to be implemented in the US. UL then puts on a show telling the CMP this system needs to be replicated in the US.

But because we are to dumb to be educated on loop impedance and UL pontificates perspective fault current is far lower at the service then it typically is- we must us an electronic breaker instead.

That is an over simplified version of it.


All the while UL, CPSC and CMPs are following the beat of Eaton and other manufacturers.
 
My understanding, is that his test method was not up to par.
Apparently he should have used a larger load or something.

Of course!

What people should be asking is why AFDDs stop at a few amps when series arcing and joule heating take place below that. Why sell a half empty fire extinguisher?
 

Reply to AFDDs are a massive fraud in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Page 337 cites UL testing, where arc resistance was found to be only 30 milliohms...
Replies
0
Views
757
Iv been given the scenario: 6 circuit earth fault loop impedance values were recorded. Each circuit has type B cb. referring to the maximum...
Replies
25
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top