Discuss After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
 
I guess your mean a s type (RCD) Residual Current Device in a tt system,otherwise there in no selectivity and little point in having rcbos,I have never had an rcbo fail only the rcds seem to fail for some strange reason
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
If the db isn’t remote from the cut out and tails are properly installed a main switch with dp rcbos is compliant adding an upfront rcd is going to reduce selectivity
 
If the db isn’t remote from the cut out and tails are properly installed a main switch with dp rcbos is compliant adding an upfront rcd is going to reduce selectivity
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
If the db isn’t remote from the cut out and are properly installed a main switch and dp rcbos is compliant
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
sp rcbos on a tt with a main switch would have no selectivity with a N to E fault.

I think the issue is making a statement saying Required or Needed means that there are no other options.
 
Last edited:
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
You just said it again “ dp rcbos are required”.

Dp rcbos are not a requirement they are an option.
 
I think you are rather mis-interpreting. I have only ever stated that where an upstream s type rcd is used in front of a db with rcbo's single pole rcbo's would not be compliant and therefore by default are required in that situation.I stand by that.
 
I think you are rather mis-interpreting. I have only ever stated that where an upstream s type rcd is used in front of a db with rcbo's single pole rcbo's would not be compliant and therefore by default are required in that situation.I stand by that.
Look at the definition of Required.

Your post @ 34 says sp rcbo with main switch would be compliant?
 
A main switch....not an rcd main switch. A db with a main switch and sp rcbo's would be compliant. It is not the way i would do it though.
Add a s type rcd main switch and the sp rcbo's are no longer compliant.
 

Reply to After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
877
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock