Hi All,

Having done my model for Amtech LV. I have noted that when Descriminating between two breakers the Pscc is taken at the load end of the circuit when analyazing discrimination between breakers.

Example being:-

The discrimination limit between upstream device Q1 and downstream device Q2 is 1.25kA. the fault current at Q2 is 10kA, the fault current at the load end of the circuit downstream of Q2 is 1kA. Amtech is telling me that I am achieving discrimination as Pscc is below 1.25kA. When I play around with circuit lengths, I managed to get a fault current of 1.5kA at the end of the circuit being supplied from Q2, only then did the program come with a warning for discrimination.

[FONT=Arial, Helvetica, sans-serif]Any ideas? I thought it is unusual that Pscc is taken at the load end of the of circuit. Shouldn't it be taken at the maximum (source of the circuit?) Are there different ways in interpreting BS Standards that I am not aware off? [/FONT]

Many Thanks
 

Reply to Amtech and Fault Current and Discrimination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
764
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock