hi ladies and gents

I have opened a ring final circuit to add 3 sockets. All was goin well till I powered it up and it keeps tripping. I have tested and IR comes back fine. continuity also fine, all test readings are fine. the circuit has 9 sockets and has a 32 type c rcbo. any other info needed please ask.

sorry for the short message but my keyboard is dying.

thank you
 
does it trip with nothing plugged in? if it requires a load to make it trip, you may have a N-E reversal at a socket.

edit: it would help if you told us your level of expertise.
 
hi ladies and gents

I have opened a ring final circuit to add 3 sockets. All was goin well till I powered it up and it keeps tripping. I have tested and IR comes back fine. continuity also fine, all test readings are fine. the circuit has 9 sockets and has a 32 type c rcbo. any other info needed please ask.

sorry for the short message but my keyboard is dying.

thank you

You must have wired it wrong, check all the new connections
 
check an old socket and the new ones.

the terminals might be in a different place.

you wont pick it up with end to end testing if you connected it up wrong
and this would cause it to trip when you plug something into a new socket
 
how?

if he has put both browns in N both blues in E and all the cpcs in L

it wont come up on end to end if there is nothing plugged into socket.

the figure of 8 R1+R2 only checks the resistance not if the cables are in the right terminal in the socket

I guess it depends on whether you do R1+R2 from the front of the socket (in which case you will spot an error) or the back of the socket (in which case, if you're going by wire colour, you won't).

Maybe this points towards why it's a good idea to do it from the front...

(Trainee :) )
 
How do you know this out of interest? Not exactly proper practice IMO. [emoji2]
ive tagged along with several firms in the past and been on building sites etc where they dont bother.

on a side note, have you guys seen demma installs, to say there a birds nest is an understatement

brand new bms installs with hundreds of cables tywrapped to ceiling grid etc with no support, i would feel embarrassed installing it but the clients dont mind it because they dont have to pay them for containment!!!!
 
The correct way to test a ring final circuit includes the end to end tests, the figure of right L to N and figure of eight L to E.
Both figure of eight tests should include readings taken at all points, or as many as realistically practical depending on whether it is IV or periodic testing.
 
does it trip with nothing plugged in? if it requires a load to make it trip, you may have a N-E reversal at a socket.

edit: it would help if you told us your level of expertise.

No no load applied. I have a socket tester that tells me reversals. But it won't stay on. I have checked all connections and they are correct and tight.

It it did stay on for about 5 hours today (friend put it on) then it tripped and won't go back on!!
 
I’ll give the OP the same advice I give all Electrical Trainee’s. Employ a qualified electrician to get your arse out of the fire.

The qualified electrician’s fees should come out of your own pocket (not the customers) just to remind you that you can’t learn this trade in a few weeks.

Hope that helps!
 
I’ll give the OP the same advice I give all Electrical Trainee’s. Employ a qualified electrician to get your arse out of the fire.

The qualified electrician’s fees should come out of your own pocket (not the customers) just to remind you that you can’t learn this trade in a few weeks.

Hope that helps!

That doesn't help no!
im ex army don't have the luxury of doing a full apprenticeship due to current commitments. After leaving I did a short course with the army loved it so much I want to do it for a living. So paying out my own pocket I'm studying the 2365 level 2 and 3. I have 17th edition, part P, solar PV design and installation, PAT testing (sitting test in a few days) and my NICEIC test coming up. So yes being experienced and qualified would be nice. But experience comes in time. But as I can't find someone to show me and help me gain the valuable experience. I'm trying on my own. So thank you for your input but advice and guidence is what I'm after not paying someone to do it for me.
 
I don't think the OP will be back, but if he does:

Are you a trainee or fully qualified? If you are a trainee how come you're doing this work? Daz
 
I don't think the OP will be back, but if he does:

Are you a trainee or fully qualified? If you are a trainee how come you're doing this work? Daz

Because his boss is maybe a Electrical Trainee and can't do it himself, just a thought
 
I don't think the OP will be back, but if he does:

Are you a trainee or fully qualified? If you are a trainee how come you're doing this work? Daz

He's just been reading this thread so fingers crossed he fill fill in the "gaps" and then maybe our guidance can be more productive!
 
I have been replying to people on here but apparently my internet don't want to work.

I am a trainee yes. Domestic installer but training to better myself (currently 2365 level 2 and 3)

all tests did come back as fine and a visual inspection of all sockets shows correct connections. Will start again tomorrow. Thank you to those who helped.
 
ok well lets move on from here, an r1/r2 will also prove correct polarity as well as contiunity , a 500v insulation test will show any problems with damage cables. So next what were your results.?
 
you said to him that he is talking rollocks about what he was saying. look at post 36

I know what i wrote..... and yes he is talking Rollocks.
I will ask again... what do you want me to elaborate on exactly or do you not understand how to do an R1 + R2 test and the reasons why we do it ????
 
Fine thanks mate. I'm struggling to see what Sparkie30's point is, the full series of tests in their correct order will identify any incorrect terminations as we all know. I think some are forgetting that the result of one test is a by product of another :)
 
Fine thanks mate. I'm struggling to see what Sparkie30's point is, the full series of tests in their correct order will identify any incorrect terminations as we all know. I think some are forgetting that the result of one test is a by product of another :)

I agree fully... also shanky is a bright lad and generally right but i think confused himself here. I also want to know what sparkie30 point is ??
 
I agree fully... also shanky is a bright lad and generally right but i think confused himself here. I also want to know what sparkie30 point is ??
confused? doing R1+R2 end to end tests at ccu wont show up if there in the wrong terminal in field with nothing plugged in

if i was doing r1+r2 in the field then of course it would show up but what most people use a quick R1+R2 for is to check continuity of the ring.
 
confused? doing R1+R2 end to end tests at ccu wont show up if there in the wrong terminal in field with nothing plugged in

if i was doing r1+r2 in the field then of course it would show up but what most people use a quick R1+R2 for is to check continuity of the ring.
Shanky the result you're on about is a result you get from the polarity test on an RCF. Now think about how that's done mate.
You're missing out a very important step.
 
my point is if you at socket wired neutrals on earth and earths on neutral. when doing tests on the board not socket. your tester will not tell you that you wired a socket wrong. from my understanding thats what shanky said.

when doing continuity, you checking the resistance of conductors and making sure connected inline
 
confused? doing R1+R2 end to end tests at ccu wont show up if there in the wrong terminal in field with nothing plugged in

if i was doing r1+r2 in the field then of course it would show up but what most people use a quick R1+R2 for is to check continuity of the ring.

Yes shanky confused..... have a think !!!
 
Yes shanky confused..... have a think !!!
feb32d97095cf2738831e323f544d24e.jpg


what im saying is if the right cores are together there just in the wrong terminals in the back of say a 2gang socket

then the fault would only apear when something is plugged in

because there wouldnt be a dead short between the cores or anything and your readings would be as expected
 
my point is if you at socket wired neutrals on earth and earths on neutral. when doing tests on the board not socket. your tester will not tell you that you wired a socket wrong. from my understanding thats what shanky said.

when doing continuity, you checking the resistance of conductors and making sure connected inline
How and why do you carry out a polarity test on a ring?
The tests you're describing are a very small part of the testing process and doing only these tests means that you have not tested the circuit properly.
 

Reply to Annoying simple circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
855
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
313
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
518
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock