Discuss Another "exporting PME post"... in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have a situation whereby a new build property has had a green electrical cabinet installed at its boundary, and a new 3ph PME supply installed.
There is a 4c 25mm SWA from here to the detached garage, which will house the plant room (3ph ground source heat pump, 3ph PV inverter), and then another 4c 25mm SWA from the garage to the house.
Incoming water is a new polypipe, and there is no gas/oil on site.

Is there anyway to use the PME, or will I need to TT each site??
 
Is 3 phase required in the house? Why not install 5c or run supplementary earth along side swa to futureproof any alterations? Is there any exposed structural steel work that is extraneous in house of garage?
 
Is 3 phase required in the house? Why not install 5c or run supplementary earth along side swa to futureproof any alterations? Is there any exposed structural steel work that is extraneous in house of garage?

Sounds like the cables are already installed.
As long as there are no extraneous parts requiring main bonding in either the garage or house then the PME earthing system can be used.
 
To my knowledge all pipework in the house will be plastic, but plant room will probably contain copper.
No exposed steels, all rsj's to be boxed in.

House is 3ph in order to to benefit from the 3ph solar PV, and keep it all balanced.
 
If main protective bonds are required then the armour is inadequate to support the bonding. It is assumed a switch fuse disconnector is to be used at the source of supply, the earthing conductor for this can be selected from Table 54.7 without calculation unless the DNO prescribes otherwise. From here the armour can be used as the cpc (assuming bonding is not required), you can verify the suitability of the armour to be used as a cpc using 543.1.3 and the adiabatic equation, it is not likely this will indicate the armour is not suitable. Remember if bonding is not an issue and a switch fuse connector is in place the armour is a cpc and not an earthing conductor.
 
"542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor." (Note quotation marks)
Irrespective of whether there are extraneous-conductive-parts or bonding conductors, the requirements are for the CSA of the main earthing conductor to be determined by use of Table 54.8, where the earthing conductor is other than copper, the CSA shall afford equivalent conductance. (Note lack of quotation marks)
 
On the earthing conductor bit, I've been struggling with this. Opening GN8, page 37, it reminded me "the earthing conductor of an electrical installation is the protective conductor that connects the means of earthing (DNO in this case) with the MET of the installation ... There is only one such conductor in each installation."

So my thoughts are : Assuming the cutout, service fuse and meter are in the garage, then the MET is likely there and the cable linking MET to cutout is the earthing conductor for the whole site. Since we know the DNO incoming is 25mm, the earthing conductor could be selected as 16mm, being the bigger of Tables 54.7 and 54.8, if I've understood correctly. Then the cable from garage to house needs to provide CPC and protective bonding conductor (if required). CPC could be selected from Table 54.7 to be the adiabatic equivalent of 16mm copper, and for this SWA armour is ok. The protective bonding conductor (if required) could be selected from Table 54.8 to be the conductive equivalent of 10mm copper, which the armour does not meet.

Please let me know if I've stuffed this :)
 
Yep I am with you on that. My notion above is that a switch fuse disconnector is installed then the armour does become a cpc, if not then I would view it as an extension of the earthing conductor. This is all assuming bonding is not required and then the armour only need be sized for its adequacy as a cpc in relation to the protective device at the switch fuse. If bonds are required this is irrelevant.
It is the 4 core 25.0 swa I am a bit confused with, I am assuming it is coming from the DNO source by way of said switch fuse.
 
"542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor." (Note quotation marks)
Irrespective of whether there are extraneous-conductive-parts or bonding conductors, the requirements are for the CSA of the main earthing conductor to be determined by use of Table 54.8, where the earthing conductor is other than copper, the CSA shall afford equivalent conductance. (Note lack of quotation marks)
I am not sure if you are being deliberately obtuse, again or whether you genuinely do not understand!
 
Yep I am with you on that. My notion above is that a switch fuse disconnector is installed then the armour does become a cpc, if not then I would view it as an extension of the earthing conductor. This is all assuming bonding is not required and then the armour only need be sized for its adequacy as a cpc in relation to the protective device at the switch fuse. If bonds are required this is irrelevant.
It is the 4 core 25.0 swa I am a bit confused with, I am assuming it is coming from the DNO source by way of said switch fuse.
The DNO supply comes into the green cabinet, and within this cabinet there is a 4w 3ph dist board.
The 4c 25mm SWA runs from here to the garage, to another 3ph dist board, then from here to the house.
There is a duct from cabinet to garage, so an additional bond could be pulled in, but as I say, the incoming water is plastic.
 
The DNO supply comes into the green cabinet, and within this cabinet there is a 4w 3ph dist board.
The 4c 25mm SWA runs from here to the garage, to another 3ph dist board, then from here to the house.
There is a duct from cabinet to garage, so an additional bond could be pulled in, but as I say, the incoming water is plastic.
Okay got you now.
 

Reply to Another "exporting PME post"... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
494
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
HI all, customers are building a small house and im coming off thier PME supply to the new build, 25mm 3 core SWA, small two bed house about...
Replies
10
Views
2K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Hi ok here we go. Friend has asked if can rewire his garage as he is turning it into a gym. I said ok no problem. He the put the spanner in. Ok...
Replies
50
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock