“The reason for condemning the supply to the oak building was because of the test reading it got, it was 371 ohms which made it non compliant"

We need to understand in layman's terms.
 
Do you have a report that you can share?
 
A bit of background would help,
have you asked for an EICR or some other additional electrical installation ?

if you have asked and paid for a report, you should get one.

if they have turned off or removed supply to that circuit against your wishes then they should have provided an electrical danger notice.
 
Which test result was 371 ohms.
 
Is it 371 ohm between conductors? (Insulation resistance)

As above. We need a lot more detail.
 
A bit of background would help,
have you asked for an EICR or some other additional electrical installation ?

if you have asked and paid for a report, you should get one.

if they have turned off or removed supply to that circuit against your wishes then they should have provided an electrical danger notice.
I asked for Electrical Test Reports for two recently installed Consumer Units. I paid £500 reduced from £900 but the Reports were not received despite many written and verbal requests. The Electrician has since refused to oproivide Reports say they would be Failure Certificates and we are worried and want to know what is wrong. The quote I put on the forum means nothing to us as home owners. We have no proof he is qualified but we must believe that he is. I wrote to the NICEIC and to Napit but neither have any records. I was not able to provide an address for him. I am asking an NICEIC Electriian to do the Test Reports and if they Fail we must know and understand the reasons so we can carry out any safety works needed, if any.
 
That’s as descriptive as “your cable’s f**ked”


Is it 371 ohm between conductors? (Insulation resistance)

As above. We need a lot more detail.
I am a home owner and not an electrician and I do not understand. I am commissioning a further Test by an NICEIC Registered Electrician.
 
There isn't a Failure Certificate they should issue an Electrical Installation Condition Report, this will either be satisfactory or unsatisfactory.
 
There isn't a Failure Certificate they should issue an Electrical Installation Condition Report, this will either be satisfactory or unsatisfactory.
I may be using the wrong terminology but the Electrician we commissioned knew exactly what we wanted. He simply wrote:

“The reason for condemning the supply to the oak building was because of the test reading it got, it was 371 ohms which made it non compliant"

We did not get an Electrical Installation Condition Report. I am sorry if I am not being very helpful.
 
I may be using the wrong terminology but the Electrician we commissioned knew exactly what we wanted. He simply wrote:

“The reason for condemning the supply to the oak building was because of the test reading it got, it was 371 ohms which made it non compliant"

We did not get an Electrical Installation Condition Report. I am sorry if I am not being very helpful.
No you are fine but this individuals statement is vague it could mean a few things.
 
No you are fine but this individuals statement is vague it could mean a few things.
Thank you and I agree. My wife and I simply want to do anything to make our wiring safe, if it is not. I challenged him but I do not have the technical skills. I suggested that no Wholesaler or Trader or Retailer would sell a non compliant armoured cable and I am blanked. I thought it may be unlawful but I am not in my comfort zone not being an electrician. It is also hard to believe an experienced and qualified electrician would use a non-compliant cable.
 
It is not likely to be non compliant cable but a fault which has developed.
 
  • Like
Reactions: DPG
It is not likely to be non compliant cable but a fault which has developed.
Thank you for taking the time on a Sunday evening to assist me. If it is necessary I will instruct the replacement of this armoured cable although it will be a big job. Our safety is paramount of course.
 
It is not likely to be non compliant cable but a fault which has developed.
Or something was left connected during the test, or it could just be a downright lie to get more money under false pretences from the OP.
You will have to excuse my synical thinking but there are a lot of people out there claiming to be qualified who have not got a clue
 
Thank you for taking the time on a Sunday evening to assist me. If it is necessary I will instruct the replacement of this armoured cable although it will be a big job. Our safety is paramount of course.
Cable may not need replacing just wait for the second electrician. I suspect the reading they have stated is a high earth fault loop impedance (Zs) due to a breakdown of conductor continuity, this is an assumption though. If this is the case it may be possible to correct this.
 
Or something was left connected during the test, or it could just be a downright lie to get more money under false pretences from the OP.
You will have to excuse my synical thinking but there are a lot of people out there claiming to be qualified who have not got a clue
Thank you again Ung. He was introduced as a teacher (Electrics) and I always believed this and still do. Is there a way I can find out his qualifications? Please do not trouble to reply so late in the day but perhaps tomorrow if you do not mind. May I ask if you are Surrey based?
 
Thank you again Ung. He was introduced as a teacher (Electrics) and I always believed this and still do. Is there a way I can find out his qualifications? Please do not trouble to reply so late in the day but perhaps tomorrow if you do not mind. May I ask if you are Surrey based?
Don't worry about the time and day people will respond at all hours.
 
Thank you again Ung. He was introduced as a teacher (Electrics) and I always believed this and still do.
There is a saying that those that can't do it, teach although I do know a few good lads that went into teaching because they got fed up of crawling round sites in all the muck
Is there a way I can find out his qualifications?
Unfortunately not
Please do not trouble to reply so late in the day but perhaps tomorrow if you do not mind.
This is relaxation time beer in one hand one finger typing with the other
May I ask if you are Surrey based?
Unfortunately not I live just off J24 of the M6 and the furthest south I get these days with work is Shropshire
 
Don't worry about the time and day people will respond at all hours.

There is a saying that those that can't do it, teach although I do know a few good lads that went into teaching because they got fed up of crawling round sites in all the muck

Unfortunately not

This is relaxation time beer in one hand one finger typing with the other

Unfortunately not I live just off J24 of the M6 and the furthest south I get these days with work is Shropshire
I also have a beer in hand. You have helped me a lot. I hope I can now ask reasonably intelligent questions about this armoured cable and the alleged reading. What if I find it is not true! I am trying to give this man the benefit of my doubts but I am struggling.
 
  • Like
Reactions: DPG
I also have a beer in hand. You have helped me a lot. I hope I can now ask reasonably intelligent questions about this armoured cable and the alleged reading. What if I find it is not true! I am trying to give this man the benefit of my doubts but I am struggling.
Just to try and get some perspective on this prior to the testing was this cable in service and operating normally if it was with the resistance figure quoted I'm thinking a decimal point may have been dropped or the MFT was setup incorrectly and gave a red cross in the display so was considered a fail by the tester
Approximately how long is this armoured cable and what is the overall diameter so we can try and identify the conductor size
 
The details of the cable are sometimes moulded into the black plastic covering… ie 2c25
 
  • Like
Reactions: UNG
Just to try and get some perspective on this prior to the testing was this cable in service and operating normally if it was with the resistance figure quoted I'm thinking a decimal point may have been dropped or the MFT was setup incorrectly and gave a red cross in the display so was considered a fail by the tester
Approximately how long is this armoured cable and what is the overall diameter so we can try and identify the conductor size
I have calipers and will measure in the morning. I would guess about 15 metres end to end but I can tell you tomorrow. It has been working fine but since it was condemned it has been turned off. I will upload some photos tomorrow which may help.
 
Cable may not need replacing just wait for the second electrician. I suspect the reading they have stated is a high earth fault loop impedance (Zs) due to a breakdown of conductor continuity, this is an assumption though. If this is the case it may be possible to correct this.
This is very helpful. I wonder if I can show these postings to my new Electrician. He is NICEIC Registered and he has been highly recommended. He is booked up in the early term but he will assist. The generous responses have been amazing and I am very grateful. I hope this will have a good and safe outcome.
 
If he knows his stuff he will fathom it out without us but we would like to know the outcome.
 
I have calipers and will measure in the morning. I would guess about 15 metres end to end but I can tell you tomorrow. It has been working fine but since it was condemned it has been turned off. I will upload some photos tomorrow which may help.
I think this would suggest that the guy who condemned it got it wrong somewhere
 
I think this would suggest that the guy who condemned it got it wrong somewhere
I would put money they are referring to Zs.
 
  • Agree
Reactions: UNG
If he knows his stuff he will fathom it out without us but we would like to know the outcome.
Good Morning Westward 10 - I wish to thank you and others you so helpfully gave up their time yesterday to respond. I will measure the armoured cable length this morning and try to identify the cable at the Oak Building Consumer end of the run (with it switched off having been made aware of the danger). I will take digital pictures I hope I can post. Of course I will advise on the outcome.
 
With a decimal point missing in the figure quoted is my thinking
This is a duplicated posting by me this morning Ung: Good Morning - It is a far more serious issue this morning as I have examined the Consumer Unit this morning and located the main armoured cable. It is more like 20 metres end to end. I discovered by lying down and look up with a torch that there is an earth cable no more than 2 inches in length cut off and in mid air. The live and neutral go to the main fuse. No wonder he advised of a risk of death. The obvious question this poses is if this earth cable is earthed both at this end and the other end (it may be) then will the Test Reading give a safe result? The Electrician recommended running a new armoured cable end to end. This would have been a huge high cost job but if this ultimately must be done to make it safe this is what we will instruct. I have not checked the other end and I stress again I am not an electrician but a 74 year old very worried home owner.

It is extremely hard to read the writing on the cable as the Power is off and I could only use a torch. It is 12 mm cable and it may read as follows:

FIECTRIP CABLE?
600/1000V
Coraka or similar?

Does this help?
 
You really need the opinion of the second electrician as this may be possible to rectify.
 
Here is a picture of the Consumer Unit in the outbuilding. The condemned armoured cable is on the right. The live and neutral go to the 63A Fuse pictured left. The top of the cable cannot be seen but to my horror I saw a short length of earth wire (no more than 2 inches) not clamped in an Earth Terminal but hanging loose in mid air. Could this explain the high ohm reading reported. No other explanation was offered. I was not advised of this unclamped earth wire. There are many empty terminals and the earth cable could easily be clamped. As I am not an electrician I am taking no risks. I hope this assists the many kind electricians who have tried to help me. I am waiting for a visit from a recommended NICEIC Electrician.


IMG_5005.jpg
 
We would love to hear the outcome of this,
I am wondering if the outbuilding is on its own TT supply and has its own earth rod.
I am further thinking that the 371 ohms is because the rod is no longer providing a good earth.

A good electrician should be able to explain what the issue is and come up with a solution to fix it.
I suspect that the distribution board in the picture may well need replacing.
the bus bar at the bottom looks heavily corroded and the 63A RCD on the left looks like it has heat damage on its upper right hand side.
 
A rod (TT) is a possible with that rather large conductor at the earth bar.
 
the bus bar at the bottom looks heavily corroded
Looks like it's tinned to me. That would be a first.
No SWA gland or earth connection to the SWA, and a big earth cable that's either a bond (to what?) or to a rod. Has to be TT, surely?
 
I also suspect a TT / Divorced earth situation, however I'm finding this picture confusing because... Red/Blue conductors would normally indicate an old cols 3c cable yet I see no yellow, and we've two brown lives in the box (B10 and B16) yet only one blue neutral??? We also seem to have three circuit cpc's into the bus bar for four circuit??
 
We would love to hear the outcome of this,
I am wondering if the outbuilding is on its own TT supply and has its own earth rod.
I am further thinking that the 371 ohms is because the rod is no longer providing a good earth.

A good electrician should be able to explain what the issue is and come up with a solution to fix it.
I suspect that the distribution board in the picture may well need replacing.
the bus bar at the bottom looks heavily corroded and the 63A RCD on the left looks like it has heat damage on its upper right hand side.
The Consumer Unit is not old and looks like new and there is no corrosion and no heat damage. I really appreciate the kind responses I am getting and possibly only from experienced electricians. I am an elderly home owner and not an electrician and I am trying to understand but this is difficult as I do not follow much of the technical advice. I was told the armoured cable was non compliant and the only reason given was the alleged reading of 371 ohms which means nothing to me. I was told it was dangerous so the reply is turned off. By visual examination I discovered, to my horror, that the earth wire coming from the armoured cable is cut short and in mid air. It is not connected to any one of many earth terminals. I simply wondered if the earth wire is connected if this was likely to produce a safe reading? The electrician was recommending the replacement of the armoured cable. This would be a huge job over a distance of about 20 metres running underground below a concrete floor and a concrete slab adjacent to the outbuilding. It is an awkward sloping site and the cost will be very high but if it is true that it must be replaced to make it safe this is what we will do. If wiring to cut earth cable into an earth terminal makes it safe this will take minutes and minimal cost. I have an NICEIC Registered Electrician visiting in the next week. I will advise on the outcome.
 
If he knows his stuff he will fathom it out without us but we would like to know the outcome.
Does this help? The top of the armoured cable is behind the top plate so cannot be seen. The arth cable coming from the armoured cable is cut and can be seen in this picture. As I have stressed several times I am not an Electrician so I struggle with the technical responses so kindly given. I simply wonder if this is why the Electrician said the armoured cable was not compliant and should be replaced which would be at huge cost. I am hoping that once this earth cable is secured in one of many free earth clamps it will then be safe and a safe reading will be produced? Unfortunately the reported unsafe reading of 371 ohms means nothing to me. Questions have been raised about the condition of the consumer unit. It is metal clad and modern and to the untrained eye looks in new condition with no heat marks on any of the fuses as suggested. I hope this clarifies and helps. The good news is that are NICEIC Registered Electrician hopes to visit within a week and I can then report the outcome. Fingers crossed.



1666659634037.png
 
Do you have a picture of the cable a bit further up and / or a bit of a wider angle so we can see a bit more of how the armoured is installed
 
Good Morning Ung - There is no power on in the building following the advice the armoured cable is non-compliant and the serious risks. I used a torch last time which was not ideal. I may be able to use a light on an extension lead from our house and if I can then I ought to be able to get a better picture. I hope to send one later. Thank you for your continuing interest.
 
  • Like
Reactions: DPG
I also suspect a TT / Divorced earth situation, however I'm finding this picture confusing because... Red/Blue conductors would normally indicate an old cols 3c cable yet I see no yellow, and we've two brown lives in the box (B10 and B16) yet only one blue neutral??? We also seem to have three circuit cpc's into the bus bar for four circuit??
I agree it looks like a separate TT system. The missing yellow conductor is likely to be the conductor that has been cut back coming from the swa, and left disconnected (the "earth" that James is concerned about). Difficult to see but the missing blue could be terminated in the same terminal as the one shown, but hidden from view in the picture. There appear to be 5 cpc's a pair that appear to be part of a ring or possibly 2 radials also sharing the same breaker in one terminal, one terminated on its own and 2 that share another terminal.

Either way it needs some more investigation and improvement, so will be nice to see what the electrician who's going to take a look has to say about it.
 
I think it's fair to say that something is wrong with this installation that needs investigation and sorting, but there's nothing that we've seen in the thread to suggest that the cable needs replacing.
 
I think it's fair to say that something is wrong with this installation that needs investigation and sorting, but there's nothing that we've seen in the thread to suggest that the cable needs replacing.
I PULLED DOWN THE ARMOURED CABLE TO TAKE THESE PICTURES. I HOPE THIS HELPS ALL THE KIND PEOPLE WHO HAVE BEEN TRYING TO HELP ME. Our electrician will be attending in the coming days. The electrician who condemned this cable hoped to replace it and it would be a major job at very high cost. I am hoping our NICEIC Registered Electrician will clamp this loose earth wire and be able to report a safe reading. The other armoured cables got to an external motor, an automatic underground pump and to external lighting. There is only the one incoming supply cable as pictured. This may help those of you who have been trying to help me.Screenshot 2022-10-25 at 13.13.25.png
 
Last edited by a moderator:
There is a few issues here. The cable is not correctly glanded hence the armour is not likely to be effectively earthed. If the cable is readily accessible this can be rectified assuming other tests come back fine. If the electrician decides to maintain the TT system, which we are assuming to be in place then the cable will require correct installation to ensure the armour is earthed and that it is isolated from the TT earth. It probably isn't insurmountable.
 
That is probably not an earth cable.
it may well be an unused yellow cable.
 
I think it's fair to say that we know there are some issues with how it's been installed - and it's not a great leap to also think that an inexperienced 'inspector' may not have realised what they were looking at. Someone more experienced should be able to resolve this mess fairly simply, I suspect.
 
There is a few issues here. The cable is not correctly glanded hence the armour is not likely to be effectively earthed. If the cable is readily accessible this can be rectified assuming other tests come back fine. If the electrician decides to maintain the TT system, which we are assuming to be in place then the cable will require correct installation to ensure the armour is earthed and that it is isolated from the TT earth. It probably isn't insurmountable.
I promised to report the outcome. The new electrician was not NICEIC regitstered as I thought but he is NAPPIT Registered and was strongly recommended. Those who responded did not have the benefit og a physical inspection but the replies were for the most part very impressive and extremely helpful. There was nothing wrong with the armoured cable and no reading of 371 ohms was taken. I was not able to comment upon this alleged reading as I have no experience and I am not an Electrician. The recommendation was to install an external Earth Rod externally and close to the Consumer Unit. The recoomendation was to install 2 threated earth rods and each was 1.2 metres in length so they went nearly 2.4 metres into the ground. This may have been much deeper than absultely necessary but I was happy with the suggestion. The work required drilling a hole through a concrete slab path before hammering the rods deep into the ground. The first was hammered most of the way in and then the second was connected with the threaded joining piece then that was hammered into the ground. A wood block was used to protect the top of the second earth road. Finally an Earth Road Inspection Pit to comply with regulations. On completion of the work a Test Reading was taken and it produced a figure of 24.5 ohms. I was invited to watch the work being cvarried out. It took less than 1 hour and I am hugely relieved having been advised to replace an alleged defective armoured cable. I wish to thank the many who gave up theur valuable time freely and willingly in an effort to assist. There was some inspired thinking. The new electrician has been brilliant. His work is to a very high standard and we can feel safe.
 
I think it's fair to say that something is wrong with this installation that needs investigation and sorting, but there's nothing that we've seen in the thread to suggest that the cable needs replacing.
I promised to report the outcome. The new electrician was not NICEIC regitstered as I thought but he is NAPPIT Registered and was strongly recommended. Those who responded did not have the benefit og a physical inspection but the replies were for the most part very impressive and extremely helpful. There was nothing wrong with the armoured cable and no reading of 371 ohms was taken. I was not able to comment upon this alleged reading as I have no experience and I am not an Electrician. The recommendation was to install an external Earth Rod externally and close to the Consumer Unit. The recoomendation was to install 2 threated earth rods and each was 1.2 metres in length so they went nearly 2.4 metres into the ground. This may have been much deeper than absultely necessary but I was happy with the suggestion. The work required drilling a hole through a concrete slab path before hammering the rods deep into the ground. The first was hammered most of the way in and then the second was connected with the threaded joining piece then that was hammered into the ground. A wood block was used to protect the top of the second earth road. Finally an Earth Road Inspection Pit to comply with regulations. On completion of the work a Test Reading was taken and it produced a figure of 24.5 ohms. I was invited to watch the work being cvarried out. It took less than 1 hour and I am hugely relieved having been advised to replace an alleged defective armoured cable. I wish to thank the many who gave up theur valuable time freely and willingly in an effort to assist. There was some inspired thinking. The new electrician has been brilliant. His work is to a very high standard and we can feel safe.
 
I think it's fair to say that we know there are some issues with how it's been installed - and it's not a great leap to also think that an inexperienced 'inspector' may not have realised what they were looking at. Someone more experienced should be able to resolve this mess fairly simply, I suspect.
I promised to report the outcome. The new electrician was not NICEIC regitstered as I thought but he is NAPPIT Registered and was strongly recommended. Those who responded did not have the benefit og a physical inspection but the replies were for the most part very impressive and extremely helpful. There was nothing wrong with the armoured cable and no reading of 371 ohms was taken. I was not able to comment upon this alleged reading as I have no experience and I am not an Electrician. The recommendation was to install an external Earth Rod externally and close to the Consumer Unit. The recoomendation was to install 2 threated earth rods and each was 1.2 metres in length so they went nearly 2.4 metres into the ground. This may have been much deeper than absultely necessary but I was happy with the suggestion. The work required drilling a hole through a concrete slab path before hammering the rods deep into the ground. The first was hammered most of the way in and then the second was connected with the threaded joining piece then that was hammered into the ground. A wood block was used to protect the top of the second earth road. Finally an Earth Road Inspection Pit to comply with regulations. On completion of the work a Test Reading was taken and it produced a figure of 24.5 ohms. I was invited to watch the work being cvarried out. It took less than 1 hour and I am hugely relieved having been advised to replace an alleged defective armoured cable. I wish to thank the many who gave up theur valuable time freely and willingly in an effort to assist. There was some inspired thinking. The new electrician has been brilliant. His work is to a very high standard and we can feel safe.
 
That is probably not an earth cable.
it may well be an unused yellow cable.
I promised to report the outcome. The new electrician was not NICEIC regitstered as I thought but he is NAPPIT Registered and was strongly recommended. Those who responded did not have the benefit og a physical inspection but the replies were for the most part very impressive and extremely helpful. There was nothing wrong with the armoured cable and no reading of 371 ohms was taken. I was not able to comment upon this alleged reading as I have no experience and I am not an Electrician. The recommendation was to install an external Earth Rod externally and close to the Consumer Unit. The recoomendation was to install 2 threated earth rods and each was 1.2 metres in length so they went nearly 2.4 metres into the ground. This may have been much deeper than absultely necessary but I was happy with the suggestion. The work required drilling a hole through a concrete slab path before hammering the rods deep into the ground. The first was hammered most of the way in and then the second was connected with the threaded joining piece then that was hammered into the ground. A wood block was used to protect the top of the second earth road. Finally an Earth Road Inspection Pit to comply with regulations. On completion of the work a Test Reading was taken and it produced a figure of 24.5 ohms. I was invited to watch the work being cvarried out. It took less than 1 hour and I am hugely relieved having been advised to replace an alleged defective armoured cable. I wish to thank the many who gave up theur valuable time freely and willingly in an effort to assist. There was some inspired thinking. The new electrician has been brilliant. His work is to a very high standard and we can feel safe.
 

Reply to Armoured Cable Question. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
881
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
A
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3...
Replies
4
Views
500
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
743
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
356

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock