I have a compressor to be hard wired into a zone 1 container. The container has a 3 phase + E supply but the compressor requires a 3 phase, N & E. This is not something I have experienced before within an ATEX installation and when researching there is a few discussions on TN-S, IT and TT grounding where neutral and earth are bonded together. Can anyone pass on any advise when it comes to this situation?
 
You cannot just combine the Neutral and Earth from the compressor and connect to the container earth, this will send the return current from any single phase load down the earth wire.
It's somewhat unusual for a compressor to need a neutral, what kind is it and what is the neutral used for? If it's just to run a 240-24V transformer for control voltage, then you could likely modify the compressor to use a 400V transformer. Keep in mind though, any modification to equipment in a ATEX zone will likely have additional regulations.
 

Reply to ATEX Neutral connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
741
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
682
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock