Hi guys having a brain fade moment.

Any reason why I can't use C type RCBO's instaed of B?
Doing a CU change at a Nursing home and been quoted for C type, currently they're B type.

Board is 3 phase but all breakers are single phase.


Thanks in advance.
Steve.
 
as long as the Zs is low enough to meet disconnection times. the max. Zs for C type is 1/2 that for a B type of the same rating.
 
so the RCD side of the RCBO is used for fault protection. assuming a 30mA RCBO, then your max. Zs is 1667. it's fine.
 
No, they are more susceptible to tripping under inrush/ start up current, nothing to do with sensitivity, in most domestic cases B type should be used. And anywhere that c type is used great attention should be placed on measured ZS value. Unless as has been said, you are employing a RCD, then it matters less
 
B type = domestic / standard circuits
C type = light commercial, inductive loads, inductive lighting such as loads of flouresents/ mods, etc
D type= heavy commercial/ industrial such as bigger motors/ commercial welding equipment
MCCB = are used in initial distribution and really big loads !!

Anything bigger and your into the realm of HV and ACB's etc and that's the speciality of maniacs like Tony!!
 

Reply to B or C type breakers? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
845
I have seen recent changes that require (most) EV chargers and solar systems to be fitted with a type B RCCD. I work with power semiconductors...
Replies
9
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Been looking at what type RCD should be fitted for small single phase individual UPS. Looked at Hager rcd selection guide under type B has 3...
Replies
3
Views
2K
I have a customer who want's me to fit a 3Kw Patio heaterto a garage. - I believe this requires a Type C breaker. There is limited space in the...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock