Hi Guys,
We have an installation we are about to carry out some extras on.
One of which is a small 3 phase DB adjacent to the main switch fuse in the remote DNO's building next to the transformer to install power to 3 caravan hook up points. (Max 20a per phase)
Some background info,
The supply is TN, 800amp Schneider ACB as incoming over current set to 550amps.
Ze from the switch fuse is 0.02
The switch fuse is a 630amp with 500A fuses fitted.
As everything is sealed and no busbar chamber is present for alterations I was thinking of installing tails 25mm ho7 insulated and sheathed singles from the load side of the switch fuse (to ensure we still have one point of isolation) through existing galv trunking to new DB which will be attached to it also.
In the DB install a 63a CB as incomer.
This obviously relies on back fusing as with a busbar system, but have never really done this without a chamber. I know the principal is the same but just wanted some thoughts.
Thanks in advance, Rich.
Sent from my iPhone using Tapatalk
We have an installation we are about to carry out some extras on.
One of which is a small 3 phase DB adjacent to the main switch fuse in the remote DNO's building next to the transformer to install power to 3 caravan hook up points. (Max 20a per phase)
Some background info,
The supply is TN, 800amp Schneider ACB as incoming over current set to 550amps.
Ze from the switch fuse is 0.02
The switch fuse is a 630amp with 500A fuses fitted.
As everything is sealed and no busbar chamber is present for alterations I was thinking of installing tails 25mm ho7 insulated and sheathed singles from the load side of the switch fuse (to ensure we still have one point of isolation) through existing galv trunking to new DB which will be attached to it also.
In the DB install a 63a CB as incomer.
This obviously relies on back fusing as with a busbar system, but have never really done this without a chamber. I know the principal is the same but just wanted some thoughts.
Thanks in advance, Rich.