Hi folks,

I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about the quality of the install:
  • I wasn't given any documentation, so no "part P" documentation.
  • Around three metres of new meter tails were added - running from the electricity meter to a new consumer unit which feeds the inverter. I think meter tails are double-insulated, so probably no issue there.
  • Those new meter tails are supported by cable ties - attaching them to a gas pipe which conveniently runs in the same direction.
So, am I worrying needlessly, or should I be concerned.

Thanks for your thoughts,

Nick
 
You have every right to be concerned. Under no circumstances should cables be tied to a gas service pipe. Have you contacted the company for certification?
 
  • Like
Reactions: DPG
You have every right to be concerned. Under no circumstances should cables be tied to a gas service pipe. Have you contacted the company for certification?
Thank you for confirming that. So far, I have written to them asking for clarification on what should happen with regard to Part P.

No response as yet, but it is the weekend.

Thanks again!
 
OK, things have moved on. I have also noticed that the meter tails that were installed in the meter cabinet have exposed inner insulation on several of the tails. I complained about that too. I have now been visited by a different pair of engineers. They made little comment, but fixed the issue with the exposed inner insulation. They also fixed the invertor properly to the wall - apparently a screw was missing. They also stated that there was no issue with the tails being clipped to a gas pipe, because the tails actually don't need to be supported at all.

I have also received a "Building Regulations Certificate of Compliance" which I presume is the long-awaited Part P. It just says "8002 - Install one or more new circuits". In my mind, I am comparing that with or recent kitchen extension for which we also got a very long document, a "Minor Electrical Installation Works Certificate" defining each circuit that was added, along with all the testing details.

Thoughst very welcome.

Thanks,

Nick
 

Reply to Battery and Inverter installation in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, So I purchased a Novopal 2000w/4000w(Peak) Pure Sine Wave Inverter DC 12V to 110V/120V. I purchased this so I can hook it up directly to...
Replies
5
Views
718
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
550
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
183
Hi. I've recently passed an EESS course with LCL snd just done my first inverter and battery install with parts supplied by the customer. My...
Replies
0
Views
1K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
739

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock