Discuss Best way to redirect a cable in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
186
Hi Gorgeous people.
Hope you are all well and surviving!

Just curious to others views on redircting an oven cable which has to move (so it will not be over the hob) but with no access to the above floor where it comes down from (which is a tiled bathroom).
Ideally the new switch wants to go on the left hand side near to the window wall. The question is, How would you do it trying to keep to zones, not hiding an extending connection in the wall etc?
Worth a note: on the other side of the wall is a utility room.

The only viable option I see is to lay a new cable under the floor and up. Which is a bigger job and may be problematic as the kitchen is an extension with only inches below it (not sure there's a straight way through).

Anyone done similar recently with good results?

InkedIMG_20200818_174715_LI.jpg
 

Attachments

  • IMG_20200818_174715.jpg
    99.1 KB · Views: 7
Do connection plates hidden behind appliances form zones?

Don't want to go off topic, but it's a question I've wondered about before. Common sense says no as they're hidden, but I don't know the answer to this.
 
Dig out the cable and pull it back to the ceiling through a hole, depending on which way the joist run cut holes (or not) to get through to the pipe box next to the window.
Either M-F inside the pipe box or in the ceiling if too short or box with blank fitted into the side, then down to the position.
Unless anything else is going there the switch might as well be in the side of the pipe box.


Cooker switch.PNG
 
As above cut a small hole in the ceiling , pull cable up.
if it was originally installed left to right as we look at the photo then just redirect it.
if it comes from the right then you will need to join it to a new bit of cabor via a MF free junction box
 
Do connection plates hidden behind appliances form zones?

Don't want to go off topic, but it's a question I've wondered about before. Common sense says no as they're hidden, but I don't know the answer to this.
I would so no. certainly if they can not be seen as the purpose of a zone is so you know where a cable might be at. If you don't know where the zone is then it's, well, not a zone...
 
Throw a blanking plate on the existing point (to give you the zone start) chase horizontal from the plate into corner, chase up corner zone (if you're feeding from the corner) or up the vertical zone formed by that blanking plate then place your socket in its new position along the horizontal zone from the plate and wire in 6243YH.

522.6.x is the general area that should be able to clarify this.

I'm sure that sounds right?
 
Throw a blanking plate on the existing point (to give you the zone start) chase horizontal from the plate into corner, chase up corner zone (if you're feeding from the corner) or up the vertical zone formed by that blanking plate then place your socket in its new position along the horizontal zone from the plate and wire in 6243YH.

522.6.x is the general area that should be able to clarify this.

I'm sure that sounds right?

Technically correct, but in reality you would avoid doing it like that.
The majority of people know that cables run vertically above or below accessories, the other zones are generally known only to electricians, so it's best to stick to vertical above/below accessories as far as possible.

Also a random blank plate in the kitchen wall will rarely go down well with the customer.
 

Reply to Best way to redirect a cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
262
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
927
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
678

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock