I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's now a dedicated boiler circuit. I'm doing an EICR.
I've found a number of faults;
1. No grommet in Consumer unit knock out, used for gas bonding (It's a recessed consumer unit)
2. Stranded cable does not have ferrules
3. Unfused Boiler switch
4. 16A MCB (2.5mm T&E)
5. Gas not bonded, bonding taken to central heating pipe only

Most of these are black and white very poor work. I've had to fix all of these so the EICR is a pass, but I have a dilemma.
#4, the MCB is way too big for a boiler. I now have a switched fuse with 3A fuse, so the boiler is now protected. It's a 2.5mm T&E cable so the 16A MCB is protecting the cable. Nothing is unsafe. If it were a new circuit, I'm sure he would have purchased a 6A MCB, but as it's not he's just used existing 16A. I'm going to need to do 16 EICR's following these guys. I'm sure this will be a theme. Is there a reg I can quote for wrong sized MCB, or is this just poor workmanship ?
 
1. No grommet in Consumer unit knock out, used for gas bonding (It's a recessed consumer unit)
Are you particularly worried about a bonding conductor touching the frame of a metal consumer unit? Do you feel that is potentially dangerous?

Simpler to add a fused spur (as you did) than mess around changing an MCB for the boiler.
I don't lose sleep about simple fixes, I do them and move on. It's usually quicker than filling out the observations section!
 
While I sympathise with the OP, I would tend to agree with @Rockingit. Anyone involved in periodic inspection and testing of existing installations should be very familiar with the type of installation that they're inspecting and testing.
Of course, no one person can be expected to know everything. But it boils down to the difference between knowledge and experience. Such experience is often picked up on the job whilst working alongside more experienced colleagues.
What though if a person doesn't have the benefit of being able to work with such a mentor?
I suppose the next best thing is this forum...
 
Are you particularly worried about a bonding conductor touching the frame of a metal consumer unit? Do you feel that is potentially dangerous?

Simpler to add a fused spur (as you did) than mess around changing an MCB for the boiler.
I don't lose sleep about simple fixes, I do them and move on. It's usually quicker than filling out the observations section!
My concern was protection against fire, the consumer unit is now open to the cavity. Any internal fire within the consumer unit could now travel freely in the cavity. A blind grommet would have easily resolved this.
 
Is there a reg I can quote for wrong sized MCB, or is this just poor workmanship ?

It's not the wrong size MCB and it's not poor workmanship.

16A 2.5mm radial has been the generally accepted standard supply for any small appliance such as a boiler for a long time.

Using a smaller MCB would be unusual and would be unlikely to give any selectivity with the 3A fuse for the boiler.
 
In all honesty, I don't know. What is the technical difference ?

Coarse stranded conductors do not need ferrules, fine stranded conductors do need ferrules or other suitable treatment at the end.

It is important to remember that the regulations do not require the use of ferrules, they require fine stranded cables to be suitably treated at their terminations. This can be achieved by using ferrules but this is not the only way.
 
My concern was protection against fire, the consumer unit is now open to the cavity. Any internal fire within the consumer unit could now travel freely in the cavity. A blind grommet would have easily resolved this.
A rubber blind grommet wont stop any sort of fire, and regardless this is outside the scope of an EICR.

You are pulling up things that relate to workmanship (gas bond excluded) and adherence to BS7671. An EICR is solely to give an engineering view on whether an installation is safe for continued use.
 
Explain a bit more - cable for what, terminated where and how?
Its a 1mm cable from FCU to boiler. 526.9.1 requires suitable terminals. I'm now curious on the definition of fine wire & very fine wire. I'd say 1mm would come under this regulation. Any multiwire cable below 2.5mm I put a feral on. But I'm not aware of the physical difference.
 
A rubber blind grommet wont stop any sort of fire, and regardless this is outside the scope of an EICR.

You are pulling up things that relate to workmanship (gas bond excluded) and adherence to BS7671. An EICR is solely to give an engineering view on whether an installation is safe for continued use.
For clarity, I am referring to 'Wylex Fire Retardant Membrane Cable Entry'
 
It's not the wrong size MCB and it's not poor workmanship.

16A 2.5mm radial has been the generally accepted standard supply for any small appliance such as a boiler for a long time.

Using a smaller MCB would be unusual and would be unlikely to give any selectivity with the 3A fuse for the boiler.
I'd not thought about, Selectivity, this is a good point. Saving myself doing the maths, what size MCB do you put on boiler circuit to achieve selectivity?
 
Coarse stranded conductors do not need ferrules, fine stranded conductors do need ferrules or other suitable treatment at the end.

It is important to remember that the regulations do not require the use of ferrules, they require fine stranded cables to be suitably treated at their terminations. This can be achieved by using ferrules but this is not the only way.
I agree with your comments, but what is fine wire and very fine wire ?
 

Reply to Boiler circuit 16A MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
761
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
854
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
660
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
332
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock